I have trane xb furnace. I'm not getting any trouble code lights on. No light at all. I have checked for power to the circuit board and I have 122 to the board.

Contractor's Assistant: Did you check the furnace's filters?

Just replaced the furnace filter and the high limit switch

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Unit looks clean, but nothing else I can see

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
11/24/2017
HVAC Technician: gotoman for ac, HVAC Technician replied 8 months ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,358
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Check power between R and C/B on furnace board to see if you have 24 volts. If not check the fuse on the board. It is a 3 or 5 amp auto type fuse. Russ

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Not getting any voltage there and there is no fuse on the board. Already called a tech to come by and look at it.
HVAC Technician: gotoman for ac, HVAC Technician replied 8 months ago

Ok. If no fuse inline sounds like bad transformer. Let me know please. Russ

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Transformer and board where bad.
HVAC Technician: gotoman for ac, HVAC Technician replied 8 months ago

Must have had a power surge to get board and transformer. Hope the tech installed a fuse on transformer. Russ Glad you are back online.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Trane XE80 furnace not igniting. 4 blinking lights. 24V
Trane XE80 furnace not igniting. 4 blinking lights. 24V across high limit connections. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Trane Xb that an “ open limit switch “ failure code
Hi I have a Trane Xb that i'm Getting an “ open limit switch “ failure code on. When I turn off power to the furnace it resets and goes through the ignition sequence, the combustion blower comes on an… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a amana air command 95 furnace, i have 4 blinking red
I have a amana air command 95 furnace, i have 4 blinking red lights, both blowers are running, but no heat or flame, code says open high limit switch, problem is i not sure where it is, need help … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a trane xl80, and have the error code "open high
not too old. I had ignitor errors before and replaced the ignitor … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My furnace blower comes on before anything. It stays on even
My furnace blower comes on before anything. It stays on even though it's not firing. The vent fan doesn't even try to run. It doesn't go through any cycles. Even if I turn the power off, unplug the t … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I'm trying to reset my KeepRite DC90. In high winds there is
I'm trying to reset my KeepRite DC90. In high winds there is some safety mechanism that kills it. No power to thermostat. I have rest it but it was a long time ago. I have a photo… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Trane Gas Furnace that stopped working. The problem
I have a Trane Gas Furnace that stopped working. The problem is it won't light. The code on the control board indicates its the high limit sensor, but have checked it and it's good. The igniter is goo… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have an Armstrong Ultra 90 furnace 16 years old. The main
I have an Armstrong Ultra 90 furnace 16 years old. The main fan will blow all the time. The blower does not turn on and the furnace will not ignite. It does this even with the thermostat disconnected.… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have a trane xb furnace 2006. It wont fire the heat just
I have a trane xb furnace 2006. It won't fire the heat just runs the fan. Red lighting blinks 4 times… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Trane XE 90 blower runs constantly with a 5 flash code
I have a Trane XE 90 the blower stays on all the time with a 5 flash code the blower comes on with the thermostat wires removed.… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Trane XR80 giving a code of high limit open (4 flashes). I
Trane XR80 giving a code of high limit open (4 flashes). I have continuity across all limits and from plug to plug. I jumpered each safety in turn, yet I could not get the fault to clear. Unplugged ha… read more
gotoman for ac
gotoman for ac
HVAC Technician
5,358 satisfied customers
HVAC Question Trane Model XE 70 with a White Rogers Model
HVAC Question: Trane Model XE 70 with a White Rogers Model 50E47-060 Ignition Control Board. Opened front panel and found board with a continuous blinking red light. Unplugged power and plugged back i… read more
Shane D
Shane D
HVAC Service Manager
32 satisfied customers
I have trane de060a936k2. on the diagnostic light it says thermal
I have trane de060a936k2. on the diagnostic light it says thermal protection device open. I have no heat but fan turns on. No burner.… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
Our Trane Furnace was working fine until we turned up the gas
Our Trane Furnace was working fine until we turned up the gas in our gas fireplace for a second last night. We had a strong gas oder and had to air out the house. Then the furnace quit putting out hea… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Rheem Imperial High Efficiency gas furnace. The pilot
I have a Rheem Imperial High Efficiency gas furnace. The pilot light glows, but the furnace does not ignite?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Trane XB 90 Gas furnace. I have cleaned all the drainage
I have a Trane XB 90 Gas furnace. I have cleaned all the drainage hoses, replaced the filter and have installed a new thermostat. The furnace starts its cycle as the fan blows. It starts and stops sev… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I am looking for some information on just what might be causing
I am looking for some information on just what might be causing this code to show up on my furnace. I have a armstrong air ultra v tech 80 furnace. it keeps throwing a code 4 ( open limit switch or li… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
fg6ra 096c 12b fRIGIDAIRE FURNACE SHORT CYCLES. GAS HEAT TURNS
fg6ra 096c 12b fRIGIDAIRE FURNACE SHORT CYCLES. GAS HEAT TURNS OFF AS SOON AS THE MAIN FAN STARTS. ERROR CODE IS 4 RED LIGHTS BLINKING ONE PER SECOND AND TEN 4 SECONDS OF NO RED LIGHT. fILTER WAS VERY… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x