HVAC

Have HVAC questions? Ask an HVAC Expert for answers

Ask an Expert,
Get an Answer ASAP!

Yellow purge light on and off and one zone not heating.

Customer Question
Yellow purge light on...

Yellow purge light on and off and one zone not heating

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Change the filters?

Contractor's Assistant: Do you plan on doing the work yourself?

If it is very simple

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 28 minutes by:
11/23/2017
HVAC Technician: Phil, Mechanical Engineer replied 7 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello,

I need to know what type of equipment this is, a forced air heating and cooling system with an air handler (furnace/ blower) or a hot hot water heating system with a boiler or water heater involved.

Take a close up, exceedingly well focused photo of the wiring diagrams attached to the equipment and I will mark them up with trouble shooting instructions. Use the 'add files' link next to your send button to get the photo(s) to me.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed , after you rate this answer:

Select the 'finish and rate your expert link' near the top of your page and click on it.

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally.. and with over 8,000 questions answered here since 2009, with a 98.5% satisfaction rating.

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my answer so far positively.. . and I will deliver that training and coaching to you All on the same dime so to speak.

That said, I cannot guarantee that you will not do something unsafe, or cause damages. You take that risk.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer, if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a unit in my attic and the heat does not seem to be
I have a unit in my attic and the heat does not seem to be working. When I went up there, there is a panel (HZ311 and it appears to be turning on and off intermittently and there is a purge light that… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
It's freezing. Heat won't turn on. 3rd zoning board that has
It's freezing. Heat won't turn on. 3rd zoning board that has gone out... heat light blinking red … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
The fan won't turn on. All zone lights are on the panel but
The fan won't turn on. All zone lights are green on the panel but the purge light is orange … read more
type2technician
type2technician
253 satisfied customers
I am having an issue with my hvac system, and I am trying to
I am having an issue with my hvac system, and I am trying to do research on it. I have a gas furnace in the attic with two zones of heat, 1st and 2nd floor. The other morning when we woke up it was 79… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 5 zone in-floor water-based radiant heating system.
I have a 5 zone in-floor water-based radiant heating system. One zone has always had trouble heating. The thermostat is OK. The furnace is trying to pump into the zone, but the output line is luke war… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
The yellow purge light is flashing on my honeywell zone
The yellow purge light is flashing on my honeywell zone unit. Heat seems to be going to zones fine. Furnace does seem to be cycling quite bit more than normal. Also there is a high pitched wheezing no… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
My purge light is on? How can I get the heat on? I turned
I turned the thermostats up and they don't move. The filter is new. … read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
Trying to figure out what a yellow purge light on my HZ311
Customer: trying to figure out what a yellow purge light on my HZ311 means im having trouble with wifi therms resetting … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
Zone two has quit sending cool air, it is a very slight breeze
Zone two has quit sending cool air, it is a very slight breeze coming out of vents. I changed or cleaned the filters and it worked better for about 4 weeks now it is doing it again. On the side of the… read more
Brian
Brian
Plumbing & Heating Engineer
131 satisfied customers
my heat stop wrking on the first floor of my house. i have
my heat stop wrking on the first floor of my house. i have base board heating and the second floor works great. my circular pump is hot on both ends of the pipes coming out of it. i replaced the therm… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Bryant unit outside, trion unit inside. Honeywell total zone
Bryant unit outside, trion unit inside. Honeywell total zone emergency light staying lit. No heat in any zone , outside unit not coming on.… read more
joeydelia
joeydelia
HVAC-R Tech
High School or GED
81 satisfied customers
The yellow purge light is flashing on my honeywell zoning system.
The yellow purge light is flashing on my honeywell zoning system. Can I reset it by pushing the boot button ?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Im not getting heat to one of my zones on my hot water baseboard
I'm not getting heat to one of my zones on my hot water baseboard heat. I could not get it to heat by turning up my thermostat. I checked the zone valve and by the stuff I had read I switched it to th… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
one of the zones shows thermostat as yellow and zone value
one of the zones shows thermostat as yellow and zone value as red. We have A Taco ZVC406EXP. One of the bedrooms is 53 degrees but every other room is working. What's wrong with it? WHERE YOU AT? NO A… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have Lennox Merit Series 13hPX unit. Panel lights indicate
Have Lennox Merit Series 13hPX unit. Panel lights indicate "purge zone 1 2 3". System not working. HELP!… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
I have a dunkirk quantum 90/200 boiler that will not ignite.
I have a dunkirk quantum 90/200 boiler that will not ignite. I have tried restarting several times but cyles off after 3 start attempts and is flashing red light.… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Open limit device error on my furnace with no heat upstairs
Have gas furnace with Honeywell MiniZone controller. No heat or flow is getting to upstairs. Red light is showing on controller for Zone 1 (upstairs) and system, green light for Zone 2 (downstairs). T… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
i have a dunkirk furnace with three zones the first two work
i have a dunkirk furnace with three zones the first two work fine the third upstairs does not heat at all i changed the relay but same thing i tied the thermostat wires together nothing. the pipe gets… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.