I wired my profusion 5000 direct to a 30 double breaker. Red…

Customer Question
I wired my profusion...

I wired my profusion 5000 direct to a 30 double breaker. Red to one and black to other. White is to the ground bar. In the heater I ran black to L1, red to L2 and white to E, per the manual. I do not get a ***** *****ght when I turn knob to the right. Any suggestions

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

New unit, just installed

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

No filters and built in thermostat

Contractor's Assistant: Do you plan on doing the work yourself?

It is done

Submitted: 5 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
11/23/2017
HVAC Technician: David Bowden, General Contractor replied 5 months ago
David Bowden
David Bowden, General Contractor
Category: HVAC
Satisfied Customers: 768
Experience: Owner at Floridaco
Verified

I​t sounds like the wiring is connected properly per the manual, however it does say to turn the thermostat know all the way clockwise to the high setting where the Yellow Power Indicator light will turn yellow, (perhaps it needs to start warming up before turning yellow)? These are very straight forward heaters and if you do not have a yellow indicator light, it is either not getting voltage across it or the bulb may be bad. Other than that it sounds like everything else was done correctly.

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 5 months ago

Greetings… Just following up to see if you were still needing some help answering your question?

Thanks,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 4 months ago

I was reviewing my open questions list and noticed this one has not been answered or replied to. Did you still need help with it or should it go back to customer service for proper processing?

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 4 months ago

Greetings… Just following up to see if you were still needing some help answering your question? If this information was helpful you can close out this question simply by completing the rating questionnaire when prompted, however…

If you are still having problems that my response and recommendations were unable to resolve, just let me know and I will continue looking for another possible solution, however I do ask that you please do not complete the rating until I have had a chance to do some further research.

One of the goals here at Just Answer, is to provide each customer with the best experience possible and for the experts to earn a 5 Star Rating based on their responses, recommendations, and professionalism, when answering questions. If I have achieved that goal for this question, please take a few moments to rate my service and select the 5 Stars before logging out.

It has been my pleasure providing an answer for you, however if additional service is needed, please use the reply box to let me know and I will respond back once I have the requested information.

Enjoy the rest of your day,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 3 months ago

I am not sure if you have been receiving my follow up messages regarding this question however, if you would be so kind as to please respond and let me know if the information I provided initially was helpful or if you still require some assistance, I would sincerely ***** ***** that way I can either continue helping you or forward this to customer support for further processing.

Thank you very much,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 3 months ago

Hello, I was reviewing my open questions and noticed this one has not been replied too, however I did respond with an answer back on November 23, 2017 and therefore I am wondering if that has resolved the problem you were experiencing. I would greatly appreciate a reply email, so I can complete this open question, or just let me know if you need further assistance, and I can continue to look for another solution.

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 2 months ago

Hello... As part of our continuous follow up procedures, every open question requires it to be closed out once it has gone past a reasonable time, and that the expert has provided an answer that should have helped resolve your question. This can be done simply by completing the 5 Star Rating once it appears. If you still require assistance or have additional questions, you can let the expert know by replying to this posting that you still need their advice and recommendations.

Thank you,

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 1 month ago

Your assistance is needed... A​s of today this question is over 90 days old and based on the nature of the problem along with the recommendation that were provided, I would like for us to close out this question, however to do that it requires a rating by you as explained below.

Please note that the rating is only based on the experts attempt to resolve the problem. If you feel a credit or refund is applicable, please contact customer service directly as the experts are not authorized to handle these matters.

One of the goals here at Just Answer, is to provide each customer with the best experience possible and for the experts to earn a 5 Star Rating based on their responses, recommendations, and professionalism, when answering questions. If I have achieved that goal for this question, please take a few moments to rate my service and select the 5 Stars before logging out.

​Thank you very much for your assistance with this, I sincerely ***** *****

Dave

Ask Your Own HVAC Question
HVAC Technician: David Bowden, General Contractor replied 25 days ago

Greetings...

I was reviewing my open questions and noticed this one has not been rated yet. If you could take a couple of moments and complete the 5 Star Rating which will close out the question I would appreciate it.

Thanks,

Dave

Ask Your Own HVAC Question
Was this answer helpful?
Ask David Bowden Your Own Question
David Bowden
David Bowden
David Bowden, General Contractor
Category: HVAC
Satisfied Customers: 768
768 Satisfied Customers
Experience: Owner at Floridaco

David Bowden is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Rheem model 13Ajn24A01 outside condenser. Last
I have a Rheem model 13Ajn24A01 outside condenser. Last night I noticed the thermostat room temperate was 74 and the thermostat was set on Cool 72. I removed filter on inside furnace unit and saw fros… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm wandering about some way to prevent the air condition
I'm wandering about some way to prevent the air condition from running water inside the room while turning it on for the first time in summer season. Because last year there was complete mess with a lot of water run just into the room which was caused by a spider which desided to make a nest in some of the pipes. Is it possible to avoid my last summer's situation for sure without calling a HVAC engineeer to check all pipes or whatever that calls? … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
1,210 satisfied customers
I have a question on a Munchkin boiler. A few weeks, I get
a few weeks, I get either an f05 or f06 fault code … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I am trying to find out if the new outside air unit is
I am trying to find out if the new outside air unit is compatible with the old inside unit. I am having issues now and one repairman says they are and one repair man says they aren't. I do have the mo… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
We have s basic Honeywell system. The thermostat is set at
We have s basic Honeywell system. The thermostat is set at 66 and the heating system keeps running even if I turn it off. It's now 73 in here . The system had cool/ off/ heat/ em heat . The Dan has au… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,712 satisfied customers
I have a jennair jfi2089aep12 I was fine this morning. I cam
i have a jennair jfi2089aep12 I was fine this morning. I cam home and the control board in front is blank and I don't hear the rerrigerator running … read more
Webb-Guy
Webb-Guy
Maitenance Supervisor
Associate Degree
2,804 satisfied customers
I have a Bathroom exhaust fan upstairs that vents out to the
I have a Bathroom exhaust fan upstairs that vents out to the roof and every couple months it stops working. Can anybody help me with this?… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,712 satisfied customers
The hood fan is in auto mode and I can't turn it off! Just
The hood fan is in auto mode and I can't turn it off! … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,712 satisfied customers
Nordyne furnace failed to ignite. Igniter did not glowbut
nordyne furnace failed to ignite. Igniter did not glowbut there is current. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Pl have Lennox hs25-311. Have Lennox hs25-311. Need to know
Have Lennox hs25-311. Need to know where the two blue wires from the hi pressure switch aware connected. One goes to the right side of contactor switch. Where does the other connect. Time delay? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have water standing around my outdoor water well. What to
I have water standing around my outdoor water well. What to do … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Unit is a Carrier Infinity.wires to thermostat have been
Unit is a Carrier Infinity.wires to thermostat have been disconnected while doing work. When feeding wires next to a line of conduit they sparked and now I have error code 170 … read more
Bill
Bill
Service Mgr
83 satisfied customers
I have a Cm907 honeywell heater thermostat wall unit. The
Hi, I have a Cm907 honeywell heater thermostat wall unit. The LCD display is scrambled, even after resetting the unit and replacing the batteries. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,712 satisfied customers
I have a Bathroom exhaust fan upstairs that vents out to the
second opinion] I have a Bathroom exhaust fan upstairs that vents out to the roof and every couple months it stops working. Can anybody help me with this?… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
My Armstrong Furnance shut down last Dec. the service man
My Armstrong Furnance shut down last Dec. the service man came and after a long serch told me all was now well within an hour I had to call back he then said I should turn off the humidfier it ran ok … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,712 satisfied customers
Why does my unit hiss? I've cleaned the blades and it's even
Why does my unit hiss? I've cleaned the blades and it's even louder now … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,712 satisfied customers
I have a 2 year old Trane AC which has just started to leak
I have a 2 year old Trane AC which has just started to leak water from the coils into the air box below. The unit is on the second floor. When the unit was replaced they opted to remove the filter on … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My water heater is not heating. It is an AO Model GPVH. The
My water heater is not heating. It is an AO Smith Model GPVH. The Intelli-Vent controller shows a green light next to Warm (far left) and yellow light on C (far right). … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x