I have a temp-star nugj125dg03 furnace that’s showing 8

Customer Question
flashes and not attempting to...
I have a temp-star nugj125dg03 furnace that’s showing 8 flashes and not attempting to start when thermostat asking for heat. If I shut off the power to the furnace and turn it back on it starts up and runs the normal cycle until the house reaches set temp and shuts it down. Then repeats same problem. Any help you can give me will be greatly appreciated. I can’t find any literature on this 1988 furnace.
Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 9 minutes by:
11/23/2017
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,348
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Russ here. How are the filters on system. Russ

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Brand new furnace filter
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago

Look on furnace and see the error codes. Is 8 error code short tom gas valve. Russ

Ask Your Own HVAC Question
Customer reply replied 7 months ago
8 flashes is low voltage input
Customer reply replied 7 months ago
S8610U Honeywell ignition control
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago

Temperate uses the Honeywell Smart valve. Sometimes the wires get loose. There are molex plugs on the gas valve. Make sure they are tight . Push them in snuggly. Retry furnace and let me know. Russ

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Furnace has been working fine ever since I shut it off and on this morning. I’ve been waking up to a 60* house every morning here in Wisconsin and it’s not even cold out yet lol. I’ll have to let you know if that helped. I shut off the power and wiggled/ firmly pushes the wires going to the valve. I’ll have to let you know if that works, next time it doesn’t start again I’ll message you. Thank you
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago

You are welcome just let me know. Russ

Ask Your Own HVAC Question
Customer reply replied 7 months ago
tonight getting 8 flashes and not even shutting of an on will make it run.
Customer reply replied 7 months ago
Ok wiggling on wires to valve worked I’ll have to clean them and tightening the connector tomorrow and check. Thanks
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago

Good work. Let me know in the morning. Russ

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Morning update, 65* thermostat set to 71* and it says heating on thermostat. Low voltage flashes still.
HVAC Technician: gotoman for ac, HVAC Technician replied 7 months ago

If you still have the flash code you will need to replace gas valve. It is heart of the furnace and the Smart valve controls everything for furnace to light. Replace valve and you will have no more problems. The Smart Valve can be cranky by working and throwing intermittent faults. Russ

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask gotoman for ac Your Own Question
gotoman for ac
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,348
5,348 Satisfied Customers
Experience: 51 years of experience install design and repair of all makes and models of AC

gotoman for ac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Having problems. AC works fine, but heat comes on, heats up
Having problems. AC works fine, but heat comes on, heats up to set temp, turns off and then will not come back on until power cycled at the thermostat or at the furnace. Either way brings heat until t… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
I have an old tempstar furnace that has a fan/limit switch.
I have an old tempstar furnace that has a fan/limit switch. When heat is called for, the burners ignite, the fan comes on at the proper temperature, and the burners will run for about 5 minutes until … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have problems w/ a Coleman DGAA 70 gas furnace. Runs fine
I have problems w/ a Coleman DGAA 70 gas furnace. Runs fine for about 3~4 cycles then I get a green flashing light. Reset switch and runs fine for another 3~4 cycles. Help… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Hi, we can't get our heat to turn on. We have a Honeywell thermostat.
Hi, we can't get our heat to turn on. We have a Honeywell thermostat. We set the fan to auto and switched the switch to heat but nothing is coming out.… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I'm staying at my son and daughter-in-laws' house in Manhattan
I'm staying at my son and daughter-in-laws' house in Manhattan Beach California. They have a new Carrier furnace that was installed in February of this year. The furnace has been operating erratically… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a coleman furnace Model DGAA090BDTA, serial # *********
I have a coleman furnace Model DGAA090BDTA, serial # ********* In the mornings when hear is called for it may cycle 4 to 5 times before igniting. what is the problem?… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have a trane xb90 that will not work. The thermostat clicks
I have a trane xb90 that will not work. The thermostat clicks but nothing happens at the furnace. Breakers have all been checked.… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have a Honeywell programmable thermostat. In the morning
I have a Honeywell programmable thermostat. In the morning when the temp is programmed to change the setting from 62 to 68 the furnace comes on but then aborts at about 66 degrees. I have to turn the … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Consolidated Industries furnace MBA080NH3R. Furnace would not
Consolidated Industries furnace MBA080NH3R. Furnace would not start. Found draft inducer motor locked-up (bearings) and over heating. Replaced draft inducer assy. Furnace now runs through normal ignit… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a ugph-12earjr and the burner will not light. I replaced
I have a ugph-12earjr and the burner will not light. I replaced the igniter but it still does not light. If I turn off the furnace then turn it back on, it begins the start up cycle. I wait for the ga… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hello, Last month I had a new Trane HVAC system installed
Hello, Last month I had a new Trane HVAC system installed at my home. This was a complete replacement of the AC, coil, and furnace. The furnace is a down draft XR95, the AC is an EXR 16. The AC works … read more
R G
R G
44 satisfied customers
Ruud UGRA-12NRAJS. Will not start. If I open the lower panel
Ruud UGRA-12NRAJS. Will not start. If I open the lower panel and close it (cycle the door switch) both the power and OK LED light and the inducer blower runs. After about 30 seconds, the inducer blowe… read more
gotoman for ac
gotoman for ac
HVAC Technician
5,348 satisfied customers
We have a Honeywell TH8320U-1008 thermostat about 5 years old.
We have a Honeywell TH8320U-1008 thermostat about 5 years old. When we set the temp for heating the furnace turns off before it reaches the desired temperature. For example, if the inside temp is 65 a… read more
gotoman for ac
gotoman for ac
HVAC Technician
5,348 satisfied customers
Hi; Got a Thermo Pride oil fired OL5-85 RDA low boy hot air
Hi; Got a Thermo Pride oil fired OL5-85 RDA low boy hot air furnace with direct drive multispeed fan motor and hooked up for AC, came home from work Fri. and found blower motor running on high spd. an… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
After night time setback, my furnace goes on and runs for a
After night time setback, my furnace goes on and runs for a short time and then goes out. The code light flashes red 9 times continuosly for about 15 minutes and then the furnace ignites and runs for … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello, I have a Trane XL80 that appears to be running fine.
Hello, I have a Trane XL80 that appears to be running fine. When it reaches the desired temperature set by a programmable thermostat it shuts down as it's supposed to. The problem somes when the tempe… read more
gotoman for ac
gotoman for ac
HVAC Technician
5,348 satisfied customers
my white rodgers digital thermostat shuts off my furnace prematurely
my white rodgers digital thermostat shuts off my furnace prematurely when i come home after work and set the temp from 62 deg. to 72 deg. it reaches about 69 and i have to move the thermostat from hea… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Heil Furnace Model 8MPT or 8MPV flame kicks on for 6-8 seconds
Heil Furnace Model 8MPT or 8MPV flame kicks on for 6-8 seconds and goes out. Tries to relight and does the same thing. Diagnostic light flashes 6 times telling me there was a "failure to ignite or fla… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x