I have a lennox airhandler cbx32mv-048-230-6-07 I have no…

I have a lennox airhandler...
I have a lennox airhandler cbx32mv-048-230-6-07 I have no heat and this unit has heat strips. I have had techs out here and they have changed the 3 relays and today the mother board. lasts week the man changed my thermostat and I need to know if it is wired correctly from thermostat to mother board. the thermostat is wired like this and I can send u photos of both. the = thermostata has a red wire rh and a jumper to rc, g=green ,y=yellow and c=black,b=blue wire and w=white. now the unit on the mother board has the following w3=white and g=green,y2=blue wires, y=yellown c=common are black but no red wire ? the red wire goes to a cut off switch for water in pan overflow.
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
11/23/2017
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,206
Experience: Furnace, A/C and heat pump specialist.
Verified

Canot see letters on motherboard well enough to tell. Back up and get wires and terminals clearly

Ask Your Own HVAC Question
Customer reply replied 7 months ago
give me a min

Take your time

Ask Your Own HVAC Question

Also give me model on thermostat

Ask Your Own HVAC Question

OK now I see some issues here with wiring. Is your outdoor unit a heat pump?If you are not sure give me model on outdoor

Ask Your Own HVAC Question
Customer reply replied 7 months ago
thermostat has PRO on front

Is your outdoor unit a heat pump?If you are not sure give me model on outdoor

Ask Your Own HVAC Question
Customer reply replied 7 months ago
maybe it is pro with a 1 in center of o, my outdoor is not a heat pump
Customer reply replied 7 months ago
I have heat strips
Customer reply replied 7 months ago
this is a 4ton lennox

OK there are several of the PRO1 tstats do you see a label maybe on inside of front cover with a T905 T805.T725 or anything?https://www.pro1iaq.com/products/thermostats

Ask Your Own HVAC Question
Customer reply replied 7 months ago
t701a

You have a blue wire that appears to go to outdoor.Can you give me model on outdoor please?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
hold
Customer reply replied 7 months ago
xc16s048-230=04

OK.Want to make sure to give you accurate info

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I can call u if need be

Excellent.You have a two stage ac .

However this thermostat does not offer two stage cool.

You will need a thermostat with both Y1 and Y2.

Phone call is an extra fee if you want phone call as I will be dedicating my time soley to you.

Now we should be able to get you some heat temporarily but ultimately you are going to need a 2 stage cool thermostat

Ask Your Own HVAC Question
Customer reply replied 7 months ago
ok so the thermostat is incorrectly wired

Yes that blue should be going to a Y2 terminal to bring on second stage ac. The B on thermostat you have initiates a reversing valve for a heat pump

Ask Your Own HVAC Question

Do you want to get some heat working for now using this thermostat?

Ask Your Own HVAC Question

Excellent. Disconnect the blue wire at thermostat and tape it off,shove back in wall for now (You will need it later)

Ask Your Own HVAC Question
Customer reply replied 7 months ago
ok then I should have heat
Customer reply replied 7 months ago
let me go brb

Not yet we are not done.

Next tell me about the red from thermostat.I see it is red at thermostat but black at motherboard.

Is the red going to a float switch in drain and then coming to board as black?

Ask Your Own HVAC Question

On back of thermostat make sure fan switch is set to Electric

Ask Your Own HVAC Question
Customer reply replied 7 months ago
fan switch is set on electric and I have heat and I informed those knuckle heads that it cold be thermostat not wired correctly.

They will need to bring you a to stage cool thermostat and wire it same as we just did except add the blue wire to Y2.

If you have further questions, please let me know.

Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.

To rate answer, please select one of the stars on the page.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
what stat brand I need are does it matter need make sure 2 stage and how does it hook up using blue wire
Customer reply replied 7 months ago
you mention y1 and y2

I personally prefer Honeywell brand. Really does not matter as long as it is says 2 stage cool.

You currently only have a single Y

The thermostat you need for 2 stage cool will have a Y1 and a Y2.

Everything will wire as it is except the blue we stuck in wall will connect to Y2

Ask Your Own HVAC Question
Customer reply replied 7 months ago
after I call them Monday and trust me I am not a happy camper. costs me a lot of money and tech should have knew

Absolutely.Installer should have know this

Ask Your Own HVAC Question
Customer reply replied 7 months ago
thanks you so much

Feel free to save and share our conversation

Ask Your Own HVAC Question
Customer reply replied 7 months ago
thank you so much.

Please remember to rate answer before you go as that is how I am compensated for my time and if you need further, just come back for up to 30 days at no additional cost.Thanks again

airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,206
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,206
9,206 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a lennox 4 ton unit CBX32MV-048-230-6-07 electric
I have a lennox 4 ton unit CBX32MV-048-230-6-07 electric heat not a heat pump has elec strips for heat. my question is is my thermosat wired correctly. rh red wire with a red jumper to rc, g ==green, … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Need to hook up a thermostat to an 8 wire system. The thermostat
Need to hook up a thermostat to an 8 wire system. The thermostat has only 7 terminals. Heater system has terminals labeled.... C , Y, R, E, W1, W2, W3, G, My THERMOSTAT Terminals are ..... G, Y, W, RH… read more
hvacexpertjoe
hvacexpertjoe
Electronics Technician
Vocational, Technical or Trade Scho
183 satisfied customers
We are installing a new thermostat for the furnace. A Honeywell
We are installing a new thermostat for the furnace. A Honeywell Model # ***** We put in a new wire and it is a bit different from the old. The old wires were White, Green, Red, Blue with the blue wire… read more
warmneighbor
warmneighbor
owner
Vocational, Technical or Trade Scho
9 satisfied customers
I have a dual compressor American Standard Heritage 16 Heat
I have a dual compressor American Standard Heritage 16 Heat pump that was built in 99'and is suppose to be 3h/2c system. It currently has no thermostat,tech twisted 4 wires together until he could fin… read more
lordofbtus
lordofbtus
pres
Vocational, Technical or Trade Scho
26 satisfied customers
I have a 3 year old Lennox signature series system. I have
I have a 3 year old Lennox signature series system. I have a new 3M-50 thermostat to replace a Honeywell TH8000 thermostat. Some of the terminals don't match up. The Honeywell is wired as follows: RC … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,038 satisfied customers
I have an old Lennox thermostat with the mercury bulbs the
I have an old Lennox thermostat with the mercury bulbs the wiring code on it is ,y with a orange or yellow wire, X with a green wire, L with a white wire, R with a black wire, A with a purple wire, V … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,348 satisfied customers
I just bought a ADMH110 Series. I am replacing a totaline energy
I just bought a ADMH110 Series. I am replacing a totaline energy star. For the wiring on the totaline the wire connectings are as follows, R- red, G-green, Y1- blue, W2- no wire, W1- white( also has a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier Performance Series TP-PHP Thermostat wired
I have a Carrier Performance Series TP-PHP Thermostat wired as follows: Wire Color - Terminal Blue - OAT Brown - SRTN Red - Rh White - W/W1 Green - G Yellow - Y/Y2 Black - C Orange - O/W2/B I want to … read more
servtech50
servtech50
HVAC/R service tech
296 satisfied customers
I have a Trane XB80 with a 50A55-486 control. I replaced the
I have a Trane XB80 with a 50A55-486 control. I replaced the old Honeywell T8401C thermostat with a new Filtrete 3M50 programmable thermostat but cannot get it to work.The connections for the old ther… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I am replacing a Trane thermostat (XT302B) with a 3M Filtrete
I am replacing a Trane thermostat (XT302B) with a 3M Filtrete (3M-50). The Trane is connected (R-Red) (B-Blue) W1(White) W2(Black) (Y1-Yellow) (G-Green). The new thermostat has: C - B - O - W - W2 - Y… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Hello, Looking for a little help to install a new thermostat.
Hello, Looking for a little help to install a new thermostat. I've been trying to read as much as I could on this but I'm still a bit confused. I currently have a Totaline thermostat (P374-1100) and I… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I purchased a LUX TX9000TS thermostat for my single stage heat
I purchased a LUX TX9000TS thermostat for my single stage heat pump. When I unhooked hte old thermostat I had wires G (Green), B (Blue), R (Red), Y (Yellow), W (White), X2 (Black) and O(Orange) all ho… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,038 satisfied customers
I am converting from a Weathertron thermostat to a Hunter model
I am converting from a Weathertron thermostat to a Hunter model 44860. The Weathertro was wired as follows: X2- Black O - Orange G - Green Y - Yellow W - White R - Red B - Blue the Brown wire was not … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Yes, this is another Lennox Thermostat wiring question. Im
Yes, this is another Lennox Thermostat wiring question. I'm replacing a Lennox 51H3401, 6 wire, with a Honeywell 7500. The old Lennox wiring is C,G, Y2, Y1, W1, RH, RC. There is a connection for all o… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have Rheem rbhc 24, I want to install a new thermostat, my
I have Rheem rbhc 24, I want to install a new thermostat, my wires on old thermostat as follows: W- white wire RH- Black jumper wire from RC B- no wire RC-Red wire, with black jumper to RH O- no wire … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,348 satisfied customers
I have a 1981 coleman envon heat pump and am trying to replace
I have a 1981 coleman envon heat pump and am trying to replace the thermostat but the wiring is not in alignment. The wiring at the board is as follows: TI motherboard / AC Unit / Thermostat wiring co… read more
Mr. Jeff Pearson
Mr. Jeff Pearson
Refrigeration Systems
Associate Degree
155 satisfied customers
Hello Presently I have a heat pump furnace and Im trying
Hello XXXXX have a heat pump furnace and I'm trying to change a "Water Furnace" thermostat with a Honeywell RTH8500. Presently the Water Furnace has this configuration R Y/Y2 G C W/W1 O/W2 Y1 L The Ho… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Carrier TSTATCCNAC01-C Thermostat Im trying to replace
I have a Carrier TSTATCCNAC01-C Thermostat I'm trying to replace with a Hunter 44110 programable thermostat. There are 8 wire coming out of the wall (Red, Yellow, Green, Blue, Brown, White, Orange, an… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x