I have a Carrier Model 58MVP 120 blinking error code. 13.

I have a Carrier...

I have a Carrier Model 58MVP 120 blinking error code

Contractor's Assistant: How old is the appliance? Have you gotten error messages before?

13

Contractor's Assistant: Do you plan on doing the work yourself?

About 14 years

Contractor's Assistant: Anything else we should know to help you best?

Yes

Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
11/23/2017
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,920
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified

Hello,

My name is Billy.

When 13 code is present...is the main blower running?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Furnace runs for about 5 minutes then shuts burners off and fan continues. The filter is clean but I’ve removed it.

And does this system also have an ac coil or just furnace only?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
it has an AC coil. I’ve blown out the burners with an air compressor and a significant amount of dust came out. I just had my basement finished and am sure it was drywall dust. I removed the front of the furnace and the AC exchanger looked ok but was cold to the touch. This was about 4 minutes after a heat cycle.

this is related to internal temp. While the burners may have been dirty they do not affect the limit sensor.

I ask about the ac coil because it can become plugged and mimic a plugged filter. Also a dense filter made to catch very fine microns also mimics a plugged filter...Right now you have an imbalance of air to the heat output.

I would recommend cleaning the ac coil....especially if drywalling has been done as that goes through a filter

Ask Your Own HVAC Question
Customer reply replied 3 months ago
Ok, how?
Am I getting charged for every question or was this a one time charge?

you are not charged multiple times...there is just the one charge.

Have you opened the ac coil yet? Every installation is different...cased coil, uncased, horiz etc...I would need pics to tell.

Even if it involves opening sheet metal, the goal is to get to and clean the side of the coil that air blows against

Ask Your Own HVAC Question
Customer reply replied 3 months ago
The coils look like a big ‘N’. Looking into the furnace from the control panel. How do I send you a picture?

There should be an "attach files" link or icon

Ask Your Own HVAC Question
Customer reply replied 3 months ago
I’m using my iPhone and don’t see an attach icon.

ok does the box around the ac coil match the furnace or is the coil inside silver sheet metal?

Ask Your Own HVAC Question
Customer reply replied 3 months ago
It doesn’t match. It’s in silver sheet metal.

Then the usual way is to cut open the duct with an access hole to get to bottom of coil...Then just putting a metal patch over it like an inspection door.

In tight installs I have seen the ac coil need to be removed...They do have some sprays at the home improvement stores called evaporator coil cleaner. This is just sprayed on and soaks in and breaks down the dirt.

Here is a no rinse version

Billy

BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,920
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Verified
BillyHvac and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 2 months ago
Hi Billy,
I've used three bottles of cleaner on the internal evaporator coils. I've set up a small fan to blow very lightly on the burner box and this kept the furnace running through the nights. It never achieves the set temperature. If I remove the fan, the furnace runs for about an hour and then faults out (error code 13, sometimes 33). Any other thoughts?

Would you be willing to speed up the blower by switching a couple wires on the circuit board for me?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Yep. Just tell me what to do.
I should tell you this is a 4-zone system. 4 thermostats with 4 different ducts with dampeners controlled by a board. Pretty common in this area, just wanted to make sure you knew.
Customer reply replied 2 months ago
The blower is a dual speed.

That does change things....the zoned systems run hotter because the furnace is running full and only a portion of the duct is open. But there should be a barometric damper connecting the return to supply to "dump" extra air back through the system.

On the circuit board...follow the wires from the blower motor..there will be a black wire likely on COOL terminal....and then a red, blue, yellow....One of those will be on HEAT and the other 2 on PARK.

Can you tell me first which color is on HEAT

Ask Your Own HVAC Question

do you have pics of circuit board in bottom section?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Where the wires attach? I'll get one.

ok I see you have multi system...can you give me full model number so I can pull schematic?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Product: 58MVP120-F-18120
Model: 58MVP120-20

Thank you...this will be a dip switch selection..see page 34 and try to get familiar with the cfm table (cubic feet minute).

We want the dip switches to be set for highest cfm on this unit

Ask Your Own HVAC Question

see page 29 for dip switch placement on board click here

Ask Your Own HVAC Question
Customer reply replied 2 months ago
This unit has been running for 13 years with the settings as is. Should I really be changing things? I'm not familiar with dip switches.

Well there are 2 ways to look at it...

1 - it was never configured properly and has actually been running like this all along but finally wore out the limit switch.

2 - it was configured properly and something has happened recently to start tripping the limit.

Number 2 would be things like the dirty coil, too dense filter, zone barometric damper stuck.

With this particular system I would only change settings if you are trying to eliminate items as suspect.

A zone system basically shuts off portions of the duct depending on demand...lets say only 1 zone calls.....all duct is closed off except the one zone which leads to excessive heat circulating through furnace.

I am betting if all zones are open the unit does not trip....it is likely when only 1 or 2 are open.

Can you see if there is "crossover" that connects the return to the supply duct? I do not see it in pics

Ask Your Own HVAC Question
Customer reply replied 2 months ago
O.K. I understand your analysis.
The only return I see is the humidifier 8 inch duct that runs from the return to the humidifier in the duct supply.
Customer reply replied 2 months ago
I'll snap another picture.

Thank you!

I am drawing a rudimentary sketch...just a moment.

Ask Your Own HVAC Question

Ok, like you said it has been this way 13 years...but I am betting it has gradually worn out the limit because I do not see a barometric bypass.

See HERE

Picture the unit trying to pump air...but only a portion of duct is open. This cause back pressure and heat in the furnace.

The damper I talk about is supposed to relieve the pressure by recirculating through the return....it is a "runoff" of sorts.

I see no crossover for your system which means from the beginning it has ran under pressure. The humidifier helps some by default...but is not substantial enough.

Zoned systems are great for individual comfort, but are harder on equipment due to choking off ducts. Now this is not a fix out of no where....but just an observation that this could have simply led to wearing the limit switch out....coupled with the basement project it just hastened the switch demise.

The switches are pretty affordable...I would put a new limit in to see if things return to normal..

Example of part here

Ask Your Own HVAC Question

Is this natural gas or propane?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
It's natural gas.Is it ok to run the furnace with the secondary fan cooling the burner box? Am I bypassing any safety switches by doing this?

What do you mean by secondary fan?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
I've set a small fan at low speed in front of the furnace. This keeps the burner box limit cooler.

Understood..that is fine.

The only thing you can NOT do is bypass the switch we are referring to.

This must be in place...whether out of calibration or not...

The odor concerns me as that is a sign of bad gas pressure or or other contaminate...does it smell acrid at exhaust?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
It doesn't smell like rotten eggs at all, more like exhaust, just lots of it.Would this switch I just bought explain why the house never gets to temperature, even with the secondary fan?

Correct....every time the switch gets to a set temp (or triggers a worn out switch)...it turns off the gas valve....blower continues...cools...gas valve on...repeat...

The fact you are hitting 13 code means it faulted 3 times in one cycle.

That means instead of kicking on and running to set point, it turned the gas off 3 times.

It could run this way a long time tripping only once or twice a cycle before you would know it. It locks out at code 13.....but trips 3 times at code 33...and keeps restarting itself.

So whatever has been happening...you have no idea how many times it has tripped just once or twice per cycle..

First step would be to change the switch.

If the unit continues to cycle I would call for a pressure/exchanger check.

Ask Your Own HVAC Question
Customer reply replied 2 months ago
Ok. I'll get the switch on Dec 1st.
Customer reply replied 2 months ago
Hi Billy, I installed the new switch and it seemed to run fine for about an hour (maybe it was wishful thinking). I noticed the flame seemed significantly larger and the smell was gone from outside. However, I got an error code 13 again and everything is the same. The bad smell is outside again and I need to run a secondary fan blowing onto the burner box to keep the furnace running. Any other ideas? I'm getting frustrated...What should the resistance be across the limit switch I just replaced? Maybe I got a defective one??

First a simple test....

But you must watch the burners (flame ) closely.

Star furnace...watch ignition....now you will have a minute of flame before circulation blower kicks on...watch the flame carefully....when the blower kicks on....do yellow tips appear or the flame wavers/dances a bit?...this is in correlation to the blower starting...

Ask Your Own HVAC Question
Customer reply replied 2 months ago
I just saw something very interesting.
I watched a couple cycles.
The first cycle:
Igniter lights, flame kicks on. Blue flame orange tips. Fan kicks on. Flame stays the same. Strong odor outside the house (exhaust smells bad).
Second cycle:
Igniter lights. small burst of flame in burner box. Doesn't ignite.
Third cycle, immediately follows second cycle:
Igniter lights, flame ignites, very large flame. Flame extends from valve, through burner tube. Big orange flame. No smell outside. At cycle end, it got scary. The flame went out but a blue flame danced around the burner box like extra gas being burned off. Flame 'popped' and went out. Error code 33.
What the hell was that???

You have either a gas supply issue or bad exchanger.

This would require putting a gas pressure gage on the gas valve (there is a allen head screw on valve leaving side)

Natural gas should be 3.5 " water column

Ask Your Own HVAC Question

Gas supply issue = gas to unit or gas valve istelf

Ask Your Own HVAC Question
Customer reply replied 2 months ago
No issues to other gas appliances in the house. So that means it's either the valve or the exchanger. How do I check the exchanger? If the exchanger is bad, can I replace it and where would I get it?

How old is the furnace?

Ask Your Own HVAC Question
Customer reply replied 2 months ago
13 years

Then I would call a Carrier dealer. The heat exchanger is under warranty. There would be labor cost..but the exchanger is covered.

You are at the point where it is not something "basic" and actually even sounds dangerous.

I would have a Carrier dealer check the exchanger.

Ask Your Own HVAC Question
Customer reply replied 2 months ago
OK. Thanks, I'll call first tomorrow.
Was this answer helpful?
Ask BillyHvac Your Own Question
BillyHvac
BillyHvac
BillyHvac, Journeyman HVAC Tech
Category: HVAC
Satisfied Customers: 22,920
22,920 Satisfied Customers
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics

BillyHvac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
The high temp wire that is wrapped around the heat exchanger
the high temp wire that is wrapped around the heat exchanger is showing no continuity, I get A2 error code … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Does Honeywell still sell he265a humidifier? if not what is
Does Honeywell still sell he265a humidifier ? if not what is the number of the replacement model number ? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My heat exchangers do not function any where near the rated
My heat exchangers do not function any where near the rated BTU output. They were installed three years ago by a professional electrician. The units operate, but you can only tell by putting your hand… read more
F. Naz
F. Naz
CA Finalist & Completed B.com
277 satisfied customers
Installed HM700A1000 steam humidifier and it works great
Installed HM700A1000 steam humidifier and it works great except that the AC runs when the humidifier runs and was told I needed a an SPDT relay and I'm not exactly sure how to hook this thing up. I wa… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
We have a true steam humidifier HM512 and it will always
Hi, We have a true steam humidifier HM512 and it will always stop humidifing and the service light blinks ten times. What fault is it showing? … read more
MattR757
MattR757
HVAC Contractor / Owner
Associate Degree
14 satisfied customers
I've recently installed a HM700A1000 steam humidifier and
I've recently installed a HM700A1000 steam humidifier and everything is working fine except that it's not shutting off. It has the yellow LED constantly on which indicates the water level is to high w… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I'm installing a HM700A1000 steam humidifier and the steam
I'm installing a HM700A1000 steam humidifier and the steam distributor has 2 condensate legs. One comes out horizontal directly underneath or in line with the steam hose and the other comes out vertic… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
I have a Honeywell hwm-330 humidifier. Is there a manual
I have a Honeywell hwm-330 humidifier. Is there a manual available? … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
428 satisfied customers
The flashing light on control says humidifier is running but
The green flashing light on control says humidifier is running but is not the screen that says the amount of humidity is blank … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
How can I adjust the water flow on the humidifier? The
how can I adjust the water flow on the humidifier? The saddle valve will not shut off and I replaced it twice. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
My Carrier Furnace Model CNPVP4324ATAACAA says humidifier
My Carrier Furnace Model CNPVP4324ATAACAA says humidifier pad needs to be changed. Is that something easy to do? … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
A quick question on a humidifier: The humidifier goes on at
A quick question on a humidifier: The humidifier goes on at 20 {manual on} but does not shut off when the flame goes off (cool). Where can I find manuals for these humidifiers and what is the problem?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
58MVP080 model got the heat exchanger issue. I have tech
Hi Pearl,58MVP080 model got the heat exchanger issue … read more
BillyHvac
BillyHvac
Journeyman HVAC Tech
22,920 satisfied customers
Need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. #
need a heat exchanger for model GIN 80bu-1000 14B-3A; ser. # 1607K 03798 … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Is it unsafe to have a cracked heat exchange on your
Is it unsafe to have a cracked heat exchange on your furnace? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My carrier evaporator keeps on blowing the 3 amp fuses. I
my carrier evaporator keeps on blowing the 3 amp fuses. I already replaced the capacitor, contactor and lastly the transformer. You think that I have wires sticking together? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
I need a heat exchanger kit for a weil-mclain ultra 105, no
i need a heat exchanger kit for a weil-mclain ultra 105 … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,938 satisfied customers
When were stainless steel heat exchangers required for
When were stainless steel heat exchangers required for residential usage and/or what HVAC company was the first to provide them. And are they as effective as touted.… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x