I have a Utica Boiler, DV125A, Temp gauge on side says its…

Customer Question
Hello, I have a...

Hello, I have a Utica Boiler, DV125A, Temp gauge on side says its hitting 180 degrees. But output never exceeds 165, trying to determine why

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Not sure, we purchased the house with the existing boiler in it, just trying to determine why DHW takes so long

Contractor's Assistant: Do you plan on doing the work yourself?

Have been, with help of family. Already changed out the DHW take, replaced the pumps, put in a new TekMar 402. Just working our way thru

Contractor's Assistant: Anything else we should know to help you best?

Hard to say, I don 't know what I don't know. I am a computer guy doing a heating system.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

No filters installed that I am aware of.

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 7 months ago
Attached some photo's. Don't know if they help or not. Shows boiler gauge at 180, and boiler supply which is read at the top, 4 inches prior to the pressure / expansion tank. Almost a 30 degree difference, cannot help wonder if that is factoring into DHW taking longer. Plus I believe I may have a bad air vent I just noticed on the SMART 50 indirect hot water tank, possible I have trapped air which would lengthen the time, however if I don't have near 180 exiting the boiler , that would not help.
IMG_1503.JPGIMG_1503.JPGIMG_1510.JPGIMG_1510.JPGIMG_1504.JPGIMG_1504.JPGIMG_1506.JPGIMG_1506.JPGIMG_1505.JPGIMG_1505.JPG53309693478__A21C0C2C-CC...JPG5330969...JPG53309694240__6030A86C-23...JPG5330969...JPG53309695863__8F32D34F-67...JPG5330969...JPG53309698523__C17E4E05-BA...JPG5330969...JPG53309726498__3E626ECD-A9...JPG5330972...JPG
Answered in 11 hours by:
11/23/2017
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,383
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

Based on what you've said so far this sounds like an issue of the boiler not being able to keep up with system demand. If the burner doesn't shut off that is a confirmation. Unless you have a very big boiler (looks like you don't) DHW recovery might not be as fast as you like. The system water temp won't approach the target temp until the tank temp is near tank limit setting. With the tekmar outdoor reset system temp for heating will be lower if outdoor temp isn't that cold. If you have the DHW wired and programmed for priority (looks like you have) the target temp will be your max limit setting. Air in the line is very unusual on an indirect that is at the same level as the boiler (assuming boiler is the low point in the system). Even if you did have some air in the line your Spirovent should eliminate it. This has nothing to do with boiler temp and likely has little effect on DHW recovery.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Rick, I have no DHW. I have a Viessmann Vitodens boiler and
Hi Rick, I have no DHW. I have a Viessmann Vitodens boiler and a Heat-Flo indirect 60 gallon hot water tank. They are controlled by a Tekmar 370, set to DHW priority. I have three radiant heat zones a… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
I have an oil fired boiler and the pressure relief valve is
I have an oil fired boiler and the pressure relief valve is dripping a lot , this valve was replaced less then a year ago for the same issue and the pressure tank was also replace. the pressure gauge … read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
Wiring 2 ganged SR504's to a tekmar 260. The tekmar 260 is
the tekmar 260 is new the sr504's are 20 years installed with 7 zones and dhw priority … read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
I have an old HE-5 Weil-McLain Cast Iron Boiler for my
I have an old HE-5 Weil-McLain Cast Iron Boiler for my natural gas DHW and 3 zone baseboard heating system with a single Taco 007 speed circulator pump and 3 zone valves. I have been reviewing NG Boil… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
Is it possible that a Rodgers valve stops closing the limit
Is it possible that a White Rodgers valve stops closing the limit contacts when it gets too hot? I'm troubleshooting an indirect water heater problem where the Tekmar doesn't initiate a call for heat.… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
Rick, I need to verify the wiring to a Rodgers zone valve
Rick, I need to verify the wiring to a White Rodgers zone valve used to heat DHW. Attached is the current wiring. Is this correct? The transformer seems to have been burned out and don't know if the w… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
I have a gas boiler - munchkin - that is short firing. It's
I have a gas boiler - munchkin - that is short firing. It's causing our indirect hot water heater and radiant heating to be very inconsistent temperature wise. An expert I already spoke with believes … read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
Have a Burnham SP4-NI gas fired boiler with a indirect water
Have a Burnham SP4-NI gas fired boiler with a indirect water heater . DHW pump is calling, boiler will not fire Has electronic igniter, inducer motor on boiler… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
I have a Weil McLain gas-fired boiler controlled by a Tekmar
I have a Weil McLain gas-fired boiler controlled by a Tekmar 371, including a DHW loop. The house gets cold when the outside temp drops and especially when the wind blows - seems like the system can't… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a triangle tube challenger cc125 combi boiler 124K btus
I have a triangle tube challenger cc125 combi boiler 124K btus and only have sufficient water flow to run one shower at 2 gpm. If you turn another faucet on the pressure drops. My tech suggested addin… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
WATER IN BOILER SYSTEM TURNS TO STEAM AND POPS OFF RELIEF WHILE
WATER IN BOILER SYSTEM TURNS TO STEAM AND POPS OFF RELIEF WHILE TEMP GAUGE SHOWS ONLY 170 DEGREES AND BURNER IS SET TO TURN OFF AT 160… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
I have a gb142 buderas hot water system not providing hot water;
I have a gb142 buderas hot water system not providing hot water; the unit reads h7 p13; the gauge going into the system reads 18 psi, temp of 145 degrees. The circulating pump is on (I can plug/unplug… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
Hello: I have a 12 yr old Crown 119 BDS LC boiler with a Honeywell
Hello: I have a 12 yr old Crown 119 BDS LC boiler with a Honeywell basic control with a high, low and 15/20 controller; connected to a forced fan vent and an indirect megastor water heater and 2 hydro… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
Weil Mclain GV-6 series 2 boiler is short cycling. Approx two
Weil Mclain GV-6 series 2 boiler is short cycling. Approx two minute rotation. If gauge is correct output temp is 140f at 15psi. System is not maintaining temperature in house at single digit outside … read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
I have just installed a Harmon wood/coal boiler and tyed it
I have just installed a Harmon wood/coal boiler and tyed it into my exhisting gas fired boiler. The installation instructions from Harmon were followed and we even added an extra expansion tank to the… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
I have a Lennox furnace in a hot water heating system. The
I have a Lennox furnace in a hot water heating system. The bladder type expansion tank is installed besides the furnace. There is banging in the piping. There is also a cracking noise but this I belie… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
Weil mclane oil boiler I have a pail under the pressure relief
Weil mclane oil boiler I have a pail under the pressure relief valve and have to empty it daily. The valve does not release due to pressure but allows water to pass by it. I replaced the pressure reli… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
I am about to select a new heat/hot water system for my home
I am about to select a new heat/hot water system for my home (oil to natural gas conversion). One quote is for a separate, direct AO Smith Hot water heater and a Buderus GB142/23 boiler. The other quo… read more
Rick
Rick
HVAC Supervisor
24,383 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x