Americian standard freedom 80 single stage natural gas

Americian standard freedom 80...

Americian standard freedom 80 single stage natural gas furnace won't light

Contractor's Assistant: Did you double-check the thermostat? And what about the pilot light?

Don;t think this furnace has a piolet light it has a glow plug put in a new circit board a year ago problem is back again

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Service person put board in. furnace starting blowing cold air, shut furnace off at the main switch turned it back on worked for 1 day now won't start

Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
11/22/2017
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,712
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question

Will it not even start heat sequence, meaning the indcuer fan does not come on at all?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
fan starts - glow plugs come on - -few seconds a click and glow plugs go out with no ingition

This is likely a thermal rollout issue. There are high limit safety thermostats that are around the burner housing area that can trip open if they fail or the unit is overheating. Some of these have reset buttons on them that you can manually press down to reset while others do not. The ones that do not either are one time limits or are limits that are suppose to manually reset when cooled down. Now that does not always happen when they go bad so you will have to check them for continuity with an ohm meter across the two leads going to them. If you do not pwn a ohm meter you can physically bypass each rollout to make sure it is good by connecting the two wires to each rollout sensor together to see if the unit will then operate. Now once you have found the bad one you can change it out or reset it and then you should check your furnace filter for blockages and make sure you main furnace blower is running to speed. These two things can cause a unit to overheat and trip one of these rollout sensors. Mosts units have 3 of these devices and here is a link to what they can look like on your unit.

CLICK HERE

CLICK HERE

CLICK HERE

All I ask is please select the 5 STAR rating at the top of your page before leaving otherwise I receive ZERO credit for assisting you. Thanks and you can come back anytime for free followup questions.

HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,712
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified
HVAC Guru and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,712
18,712 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
AMERICAN STANDARD FURNACE FREEDOM 80 SOMETIMES IT LITES AND
AMERICAN STANDARD FURNACE FREEDOM 80 SOMETIMES IT LITES AND OTHER TIMES IT DOESNT AND THE FAN KEEPS BLOWING COLD AIR I SHUT IT OFF AND RESET IT THE IGNITER GLOWS AND THE GAS VLVE CLICKS BUT NO FIRE UN… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a american standard freedom 80 single stage furnace
hi my name is ***** ***** have a american standard freedom 80 single stage furnace about a 2003 vintage . the fan comes on the burner lights up ,the fan goes off the burner goes off .this can happen 2… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an American Standard Freedom 80 single stage furnace.
I have an American Standard Freedom 80 single stage furnace. Suddenly started blowing cold air. I tested the hot surface igniter. It was bad. I replaced it with a silicone nitride universal igniter. I… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
there. I have an American Standard Freedom 80 Single Stage
there. I have an American Standard Freedom 80 Single Stage that has been lighting intermittently. I cleaned the burners and it worked well two weeks. When this happens it won't light at all and goes t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My American standard freedom 80 two stage furnace has a red light that
My American standard freedom 80 two stage furnace has a red light that I'd blinking 3 times what do I do about a pressure switch error… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi, I have an American Standard Freedom 90 Single Stage that
Hi, I have an American Standard Freedom 90 Single Stage that has been cycling no heat with 4 flashes code. I have checked and tapped the two primary problems. The only fix seems to be wiggling the mai… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an American Standard Freedom 90 Furnace and it is blowing,
I have an American Standard Freedom 90 Furnace and it is blowing, but not giving off any heat - the indicator light blinks 9 times which states - indicates ''Check Ignitor'' more information on line s… read more
Heath.M
Heath.M
Refrigeration Mechanic
Vocational, Technical or Trade School
223 satisfied customers
Greetings. American standard freedom 80, just replaced filter,
Greetings. American standard freedom 80, just replaced filter, single red light blinking, no heat. Ideas?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hello, I have an american standard freedom 80. It will go
Hello, I have an american standard freedom 80. It will go through the start up cycle but not light. the inducer motor runs, the glow plug lights up, but never lights. I am getting a pressure valve err… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Have a American Standard Freedom 80 2 stage furnace-5 years
Have a American Standard Freedom 80 2 stage furnace-5 years old. The furnace will ignite and get up to temperature, then shut off. However, after awhile the furnace starts to make loud clicking sounds… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
My American standard freedom 80 single stage furnace started
My American standard freedom 80 single stage furnace started acting up. The furnace will ignite the gas and start burning but then shuts its self off quickly in around 5 seconds and then repeats itsel… read more
joeydelia
joeydelia
HVAC-R Tech
High School or GED
81 satisfied customers
I have a American Standard Freedom 80 furnace installed 8 years
I have a American Standard Freedom 80 furnace installed 8 years ago and sometimes it doesn't kick in to heat the house. I have had to go down shut the main power off...give it a minute and turn it bac… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My american standard freedom 80 single stage furnace is not
My american standard freedom 80 single stage furnace is not functioning. I went down to investigate and found a pool of water at the base of the furnace that had spilled over from the wash tub. The fl… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
We have two American Standard Freedom 80 Single Stage about
We have two American Standard Freedom 80 Single Stage about three years old. One burner did not start up on the first day we wanted some heat. Called for service and was told the glow bar was bad and … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have an American Standard Furnace Freedom 90 single stage
I have an American Standard Furnace Freedom 90 single stage that is operating but blowing cold air. When I go down to the furnace room I see three red blinking lights. This happened once when we had a… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
hi i have an american standard heater single stage freedom
hi i have an american standard heater single stage freedom 80 and it is sending a trouble light . the light flashes 4 times which through some research i have found that to be a error fault of open hi… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
We have a American Standard Freedom 80 gas furance about 5
We have a American Standard Freedom 80 gas furance about 5 years old. This morming it would not go on. How can I check the pilot and/or restart or relite the pilot?… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Hello I have a American Standard Freedom 80 Comfort R furnace.
Hello: I have a American Standard Freedom 80 Comfort R furnace. Model is AUD100R9V5K4. Wall thermostat is Braeburn Model 3000 Non-Programmable Single-Stage Heat/Cool Thermostat. All installed about a … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.