Customer Question
I have a simple...

I have a simple Trane HVAC with 5kW heating element that I just replaced. The coil was burned thru so I replaced with a universal 5kW heating coil. The problem I have is when thermostat set to AUTO and turned up above ambient room temp., the fan will not come on. When I select the thermostat ON fan switch, the heater comes on. I'm guessing some relay is not coming on. What do you think>?

Contractor's Assistant: Are you an HVAC professional?

No.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes. I have certain 'skills' that makes this easy for me.

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
11/22/2017
HVAC Technician: airheatman, HVAC Technician replied 10 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,529
Experience: Furnace, A/C and heat pump specialist.
Verified

Sounds like a relay maybe a sequencer.What is model on air handler and do you have a multi meter for troubleshooting?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Just one row of coils. I have a meter. Model is a Trane Model 2HM06500506A.
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Let me see if I have a wiring diagram

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Not finding this as a Trane model.

Do you see a wiring diagram on unit that you can send a picture of?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
I just noted that I put the heating coil panel in backward against airflow (they have an arrow on it for airflow direction). I don't think that it would change anything when I flip it over. Why would they make the installation ambidextrous??? Don't answer that. LOL.
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Element needs to be at least a certain distance from blower so it deosnt cause high limit to shut it off. Is it working now?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Checking on wire diagram. Noted that the last heating coil was installed the same as I replaced it. So that won't affect anything. Pretty ambidextrous looking heating coil panel.
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

OK I have not been able to find anything by model 2HM06500506A

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Problem. No schematics or diagrams. Also, forget I said Trane. It is a York model by Borg & Warner.
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Do I have number right?

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

OK looks like that may be model on the heat kit.If so do you see a model on the air handler?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Well, looks like that is the Model No of the heating part.
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

See a label on actual air handler?

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Anything like FANB/FALB, FBRC/FBFC, FYRC/FYFC ?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Model No. G+HCQ24AA. "+" may be 2 or B.
Customer reply replied 10 months ago
But that may be for AC part. Other than that, there are not other model numbers listed anywhere.
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Still not finding anything.Can you attach a pic of the wiring including heat kit? Usually there is a wire from sequencer that energizes blower

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Where can I send pics?
Customer reply replied 10 months ago
How can I send pics??
Customer reply replied 10 months ago
Here are pics
CD12ACCB-A295-4B2F-A7B5...jpegCD12AC...jpeg01E56C81-F4C2-4F82-933A...jpeg01E56C...jpeg71EF4D31-5246-408E-9169...jpeg71EF4D...jpeg4684BA38-E684-40B1-A193...jpeg4684BA...jpeg
Customer reply replied 10 months ago
That’s the wire to the sequencer.
Customer reply replied 10 months ago
Hello
Customer reply replied 10 months ago
Bought new sequencer while still able. Thanksgiving prep now delaying me installing. I’ll get back to you when I get it installed.
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

I understand.Issue is most likely the sequencer or that little peanut relay.Let me know and we will go from here.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Thanks so much! Will do.
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Talk soon

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a T8001C Thermostat and when I set it to heat the
I have a T8001C Thermostat and when I set it to heat the blower comes on immediately, stays on for a few minutes, then shuts off. I cannot tell if the gas is also being turned on, but I know it should… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Replace one coil for BAY96X1415 assembly. American
Replace one coil for BAY96X1415 assembly. American Standard/Trane. is there a part number for that. … read more
airheatman
airheatman
HVAC Technician
9,529 satisfied customers
The furnance will not blow hot air. The coils heat up inside
The furnance will not blow hot air. The coils heat up inside the unit, but does not blow out the hot air. Also, turned on the furnace with thermostat, but only way to turn off is to turn off the break… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,978 satisfied customers
I just installed a trane ac split system with a remote. It
I just installed a trane ac split system with a remote. It cools down the room great. I have it in cool mode (not auto), and I can display the set temp on the remote but not the ambient room temp. Whe… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My blower on my Train air handler does not kick in when on Auto. See this link
My blower on my Train air handler does not kick in when on Auto. See this link for more information. http://terrylove.com/forums/index.php?threads/heating-blower-wont-start-on-auto.60475/… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,024 satisfied customers
We have a Trane unit from 2007, model numbers 2WCX3030A1000A There
We have a Trane unit from 2007, model numbers 2WCX3030A1000A There is a timing issue with the air flow fan. Sometimes it want turn on when the thermostat engages. The heat pump motor and out side fan … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a furnace that I think it miswired... it's a 20kw furnace
I have a furnace that I think it miswired... it's a 20kw furnace with 2 breakers. I can't find a schematic (the front panel was replaced at some point). The only model number I can find is MCE42F20D2F… read more
airheatman
airheatman
HVAC Technician
9,529 satisfied customers
My furnace works in fan mode but not Auto, It shuts itself
My furnace works in fan mode but not Auto, It shuts itself off in Auto. I guess it comes on after say 30 mins once turned off or when temp goes below 69F. Is the problem with heat sensor or do i have … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
i have an intertherm system (i keep seeing intertherm and nordyne
i have an intertherm system (i keep seeing intertherm and nordyne interchanged)model u-32 serial ********** earlier, my wife said she smelled something coming from the air conditioner. it smelled like… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
My room temperature can not get up to 70 degrees F, with the
My room temperature can not get up to 70 degrees F, with the Trane XR11 system. This system was installed in 2005, and I moved in in 2012. I have not touched the system. The outside unit seems working… read more
airheatman
airheatman
HVAC Technician
9,529 satisfied customers
I have a three element unit that the third element heater has
I have a three element unit that the third element heater has never been connected. I need to know from which color wire from thermmostat do I get the 24volt to operate the sequencer to energize this … read more
V12Tech
V12Tech
252 satisfied customers
My Wesco electric furnace is hot even when its off. We noticed
My Wesco electric furnace is hot even when it's off. We noticed warm air coming into the house through the return. Switched off the breakers. What's going on?… read more
joeydelia
joeydelia
HVAC-R Tech
High School or GED
81 satisfied customers
My honeywell chronotherm III seems not to be working correctly.
My honeywell chronotherm III seems not to be working correctly. I don't think the fan is coming on at all in the AUTO setting. I can turn it on so it runs all the time, but if it is not in that positi… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Sanibel, Florida I just programmed 2 RTH7600D thermostats
Sanibel, Florida: I just programmed 2 RTH7600D thermostats for use in a small shop with 3 package HVAC units (A/C + electric heat, not heat pump). Present exterior temp: 55F. Interior temp: 60F. Progr… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a trane system can not read the wiring diagram because
I have a trane system can not read the wiring diagram because of the system is old. model #twe060p13fa0 only one stage of the heating is working top coil not the bottom All the heating part have been … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Janitrol A61-20 Rev C electric furnace. 3 or the
I have a Janitrol A61-20 Rev C electric furnace. 3 or the 4 heating elements have burned out so I am going to replace the entire heat package. Where can I find the heat package and what KW rating do I… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have two Trane Weathertron XE 1200 HVAC systems (electric)
I have two Trane Weathertron XE 1200 HVAC systems (electric) - one to heat/cool upstairs, one to heat/cool downstairs. Both units were made in '95 and installed a year later. Upstairs works fine. Down… read more
tom goellner
tom goellner
owner
Vocational, Technical or Trade Scho
1,115 satisfied customers
I have an Amana BMA Multi Position Airhandler with a EDK07A
I have an Amana BMA Multi Position Airhandler with a EDK07A Electric Heating Kit. The heat went out in it today, and I am looking for simple things to check. I have verified that the thermostat and co… read more
Michael Reush
Michael Reush
Master Technician
High School or GED
2 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x