I am having trouble. The flint glows and then click.....the gas does not light. We replaced the upshot burner tubes. Everything worked when I turned it on and now...it just clicks. No fire
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
11/22/2017
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,209
Experience: Furnace, A/C and heat pump specialist.
Verified

If furnace is not coming on or does not stay on , there should be an error light flashing on the control board in blower compartment to indicate what has failed. If you can locate this and tell me the pattern of the flash, that will point us in the right direction for troubleshooting.

Also let me know if you have a multi meter for troubleshooting.WE will go from here.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
No lights on blower

Can you give me the complete model number on the furnace?

The number on outside of furnace is just a series.

Actual model will be on a label on inside furnace panel just above burners.Remove panel to burner compartment and look inside. The model number will help me give accurate assistance for your specific unit.

Below is a link to a generic video showing where to find label with model number:

https://www.youtube.com/watch?v=KZfyeZOFdpU

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Ugph-07eauer
Customer reply replied 8 months ago
Blower works
Customer reply replied 8 months ago
I see an orange light an 2 green light bulbs but they aren't lit or blinking

If the green power is not lit, blower nor anything else will come on.That indicates we have power to board. Hold door switch in

Ask Your Own HVAC Question

Have to step away for a few but will e back shortly

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Got ot....green lights 2 are lit. No orange light. They are not blinking

OK now call for heat and see how far furnace goes.If it fails to light the ok light should start flashing

Ask Your Own HVAC Question
Customer reply replied 8 months ago
it worked like it did earliwr.....but it will go off and not work in a bit....and orange light is on. When it doesn't work, the blower sounds, flint turns orange and there is a clock with no fire so the flint goes off. It does it again...no fire and the blower will blow....but no heat

Orange light is the flame light.It will only be on when burners are on.Watch it and when it goes off or fails to light see if the ok light blinks a code. Also check the wires to gas valve and make sure connections are clean and tight.Are you on LP or natural gas?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Natural
Customer reply replied 8 months ago
Ok. Cut off. Blowing excess. Orange light went off

OK gas pressure should not be changing with natural. As soon as hear click after igniter lights check for 24vac at valve.If we have 24v but gas does not come out you may have a failing valve

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Is there a tool for that?

Multi meter .Yyou can get an inexpensive one at Walmart for about 15 bucks if you would like to troubleshoot and I would be happy to guide you.

http://www.walmart.com/ip/Innova-3300-Equus-3300-Hands-free-Digital-Multimeter/14644665

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Thank you do much. How can I contact you tomorrow?

Just come to the website and go to MY QUESTIONS.That will bring you here.Type a comment and I will be notified

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Thank you so much!

Thank you.

airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,209
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,209
9,209 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
We have a Trane XE 80 furnance. Recently started having some
We have a Trane XE 80 furnance.Recently started having some problems. First had to replace the blower and capacitor that went out. Next replace the flame sensor.. All seemed to be working fine until t… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
AMERICAN STANDARD FURNACE FREEDOM 80 SOMETIMES IT LITES AND
AMERICAN STANDARD FURNACE FREEDOM 80 SOMETIMES IT LITES AND OTHER TIMES IT DOESNT AND THE FAN KEEPS BLOWING COLD AIR I SHUT IT OFF AND RESET IT THE IGNITER GLOWS AND THE GAS VLVE CLICKS BUT NO FIRE UN… read more
airheatman
airheatman
HVAC Technician
6 years college
9,209 satisfied customers
I have a Carier Weatermaker 9200. It is giving me an error
I have a Carier Weatermaker 9200. It is giving me an error code 34. Induction fan starts, starter glows, gas valve clicks, but does not fire at all. Other times, fires and works normally. Other times … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
The burner is not lighting. The pilot light goes own, but the
The burner is not lighting. The pilot light goes own, but the burner does not fire up. the pilot light goes off and then the furnace is stuck in its cycle. then the fan continues to blow cold air and … read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have a 1997 American standard 90 residential furnace. Last
I have a 1997 American standard 90 residential furnace. Last night, While checking the gas line, I turned it off during a running cycle. Once powered off, it would not power back on. The inhibition sw… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
goodman 70K 95% 2 stage furnace i installed was running perfect
goodman 70K 95% 2 stage furnace i installed was running perfect now will not fire... flashing no codes… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have trane de060a936k2. on the diagnostic light it says thermal
I have trane de060a936k2. on the diagnostic light it says thermal protection device open. I have no heat but fan turns on. No burner.… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
I have a G50 that is not working right. At first all 3 burners
I have a G50 that is not working right. At first all 3 burners would light, the the combustion air blower kicked in, but the blower didn't kick on. After a few minutes running like that the burner wou… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Hi. I have a York Diamond 80 furnace. The ignitor (glowing
Hi. I have a York Diamond 80 furnace. The ignitor (glowing metal piece) lights up and the gas valve clicks but the gas/burner doesn't fire up unless I gently shake the plastic housing (with all the wi… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I have a Trane VX 80 furnace. Today it just started this problem.
I have a Trane VX 80 furnace. Today it just started this problem. I set the thermostat to turn on the furnace. The furnace begins its start cycle and the small fan turns on. There is then a noticeable… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Carrier Furnace - Model Number 58PAV090 - 16 will not light
Carrier Furnace - Model Number 58PAV090 - 16 will not light up. I've read through many similar issues that others have posted here and tried most of the suggested fixes with no luck. Heater seemed to … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Nordyne M1MB 056A BW furnance. It quit working on
I have a Nordyne M1MB 056A BW furnance. It quit working on me last night, sometime between 1 am and 7:30. The red light was blinking 4 times, which means "Lockout due to failed ignition". I turned the… read more
TimVZ26
TimVZ26
Service Foreman
Vocational, Technical or Trade Scho
157 satisfied customers
I have a Goodman model c2e24b-2a. The heat doesnt work.
I have a Goodman model c2e24b-2a. The heat doesn't work. I know we have gas because the stove works. The fan will come on so I know we have power. It doesn't blow warm air. Please help.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I HAVE A GOODMAN 70,000 BTU 80% FURNACE, ABOUT 4 YEARS OLD.
I HAVE A GOODMAN 70,000 BTU 80% FURNACE, ABOUT 4 YEARS OLD. INTERMITTANT PROBLEM HAS NOW BECOME CONSTANT. FURNACE GOES INTO LOCK OUT AFTER TRYING TO FIRE 3X. WHEN CALLS FOR HEAT, INDUCER FAN STARTS, I… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
good morning i have a model gmt045-3b the igniter glows but
good morning i have a model gmt045-3b the igniter glows but wont light.when i blow into the gas tubes it fires and runs there are no lights flashing , thanks jim… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I recently tried to turn on the furnace and the igniter glowed
I recently tried to turn on the furnace and the igniter glowed but the burners did not ignite and the green light started blinking..it worked fine this summer in air conditioner mode...is there a rese… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
WE HAVE A TRANE XL80 AND IT QIT WORKING LAST NITE. THE IGNITOR
WE HAVE A TRANE XL80 AND IT QIT WORKING LAST NITE. THE IGNITOR MAKES NOISE BUT IT DOESN'T FIRE UP THE FURNACE.IS THERE A WAY TO MANUALLY GET THE PILOTS WORKING? XXXXX XXXXX… read more
Robert
Robert
Associate Degree
161 satisfied customers
My Rheem Criterion II died last night. I did the troubleshooting
My Rheem Criterion II died last night. I did the troubleshooting steps, but no luck. Now it's 7 degrees in Denver. Help!… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x