Hi i have a...

Hi i have a american standerd freedom 80 down draft furance that keeps short cycles all ready replaced flam sencer with new one along with the thermostat if left off for a hour or so furnance will run normal for about 3. 5 mons then will star to short cycle agin

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

Not the thermostat

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

A good answer would be great my ac is located below the furance and the nlower is on top of the furance

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
11/21/2017
HVAC Technician: airheatman, HVAC Technician replied 8 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,200
Experience: Furnace, A/C and heat pump specialist.
Verified

Can you give me the complete model number on the furnace?

The number on outside of furnace is just a series.

Actual model will be on a label on inside furnace panel just above burners.Remove panel to burner compartment and look inside. The model number will help me give accurate assistance for your specific unit.

Below is a link to a generic video showing where to find label with model number:

https://www.youtube.com/watch?v=KZfyeZOFdpU

If furnace is not coming on or does not stay on , there should be an error light flashing on the control board in blower compartment to indicate what has failed. If you can locate this and tell me the pattern of the flash, that will point us in the right direction for troubleshooting.

Also let me know if you have a multi meter for troubleshooting.WE will go from here.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I donot have the model no at the moment the furance will call for motmal heat after 3to 4 times it will go into lovk out 2blinks then a pause if i reset it it will go back for normal call for heat if i leve it off for 15 30 mins the burners will light and stay on for 3 5 min then shouts of.
Customer reply replied 8 months ago
No
Customer reply replied 8 months ago
Are you still there
Customer reply replied 8 months ago
When the furance goes off after 3...4 times 2nlinks then pause indicates lockout
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

You should get an error code the very first time before the lockut code.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
There is no error code befor lock out just the normal code for calling for heat
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Locate the limit switches and try bypassing them one at a time and see if maybe one of them is opening.Just bypass long enough for when it would be shutting off.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Ya had a guy out yesterday and he ck those and they were working. If the ac coil was dirty would that cause a over heating prob in the furrance and make it dhout down
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Absolutely.The limit will cut it out until chamber cools down,If he checked it with furnace cold they would be closed.We need to check when it is off and should be on

Ask Your Own HVAC Question
Customer reply replied 8 months ago
K ill have to ck later tonight when i get home ill try and remove the door for the ac coils and clean them up and see what hsppehs
HVAC Technician: airheatman, HVAC Technician replied 8 months ago

Let me know what you find.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
What are the symptoms of a bad heat exchanger
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

Bad heat exchanger can cause limit to trip.Signs would be if you get headaches and family seems to constantly have cold symptons .You will also often have change in flame characteristics when blower comes on.An old school way of testing heat exchanger is to allow blower to start and toss in a tablespoon of table salt.Watch flame and if turns all orange that is a sure sign heat exchanger is allowing household air into the heat chamber.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Will a bad heat exchanger cause the flame to go out and not telight till it has cooled down
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

It can yes

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

If bad enough it can actually cause the flame to blow away from the flame sensor also

Ask Your Own HVAC Question
Customer reply replied 7 months ago
See my furance will light and turn on a few min with the blower running mormal then flame out and will.not reignite for sometime
Customer reply replied 7 months ago
If heat exchangers are bad is it worth replacing them or what to do
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

If issue turns out to be a bad heat exchanger,it is wise to just replace unit as cost will outweigh benefits.For just a few hundred bucks more, you get all new warranties on all parts

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,200
9,200 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have American Standard Freedom 80 Comfort-R System, 5 Days
Have American Standard Freedom 80 Comfort-R System … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I have an Amer. Standard Freedom 80. The fan keeps starting
Hi, I have an Amer. Standard Freedom 80. The fan keeps starting about every 20 seconds and stops after 3 seconds. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have an american standard freedom 90 furnace, no heat, the
I have an american standard freedom 90 furnace, no heat, the red light on the controller just flashes "normal' no call for heat". The small inducer blower runs and the big blower runs, but no signal t… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,348 satisfied customers
I have an American Standard Freedom 80 w/AC. When I run the
I have an American Standard Freedom 80 w/AC. When I run the AC, or just the fan, it runs for around 2 minutes and then shuts off. The outside AC Condenser keeps running but the fan shuts off. I'm thin… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
I have an American Standard Freedom 90 Single Stage furnace...about
I have an American Standard Freedom 90 Single Stage furnace...about 7 years old. I have had few problems, and nothing wrong yesterday. Last night the outside temps dropped to -9 in Illinois. I woke up… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,348 satisfied customers
My AC unit is not coming on. AC: Amana Hi Efficiency 12,
My AC unit is not coming on. AC: Amana Hi Efficiency 12, model #RCC42A2B Furnace: American Standard Freedom 80 Two Stage --The control board in the furnace shows as normal (slow blinking red). --The b… read more
caleb
caleb
63 satisfied customers
Hello. I live in Denver, where humidity is not an issue,
Hello. I live in Denver, where humidity is not an issue, lack of it is. Our Lennox 5 ton compressor went out. It and our furnace are 14 years old. Thus, we are contemplating changing out the system to… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,348 satisfied customers
Hi,My heating/cooling system is about 15 years old. Its
Hi, My heating/cooling system is about 15 years old. Its made by American. My heating system was working fine, but my thermostat for some reason would not turn on my ac unit. So, I decide to replace m… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
My Daughter has a bryant electric furnance. She had people
My Daughter has a bryant electric furnance. She had people come out to see why it was not heating the way it should. They said the temperature is coming out at 100 degrees F. Is this normal or should … read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Trane XL 90 two stage furance with a Honeywell FocusPro
I have a Trane XL 90 two stage furance with a Honeywell FocusPro TH500 thermostat. The Honeywell keeps the house right on the degree setting but on real cold weather the furnance fan can turn on and o… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox merit series furnance, the induction blower
I have a Lennox merit series furnance, the induction blower kicks in and then shuts off with the indicator lights as follows: Left = off, right= slow flashing. I dont' see any of the burner on? Is my … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,348 satisfied customers
Blinking RED light on American Standard Freedom 80 Comfort R furnace
I have an American Standard Freedom 80 Comfort R furnace. Red light is blinking on the front. I know this is something simple... Can't find ANY manuals or trouble-shooting guides online. Can anyone he… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My 6-year old Rudd AC is acting funny. Works great for a while,
My 6-year old Rudd AC is acting funny. Works great for a while, then stops working. Outside cooling fan runs for a few seconds, then stops for a few minutes, then tries to start again. After shutting … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,348 satisfied customers
I have American Standard Freedom 80 multi stage gas furnace
I have American Standard Freedom 80 multi stage gas furnace with White Rogers 1F91W-71 thermostat. Occasionally, (about once per week) after a morning startup the fan remains running when furnace stop… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Replaced a thermostate (twice) both prreviously work for a
Replaced a thermostate (twice) both prreviously work for a short time, half a day. New replacement gives only fan, shorting w-r does not seem to turn on furnace, only fan, only blows cold air. Shortin… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
The burner on my furnace was going on for a short period then
The burner on my furnace was going on for a short period then off. The fan ran continually and the temp. was 80 degrees coming out of the closest vent. after about three days it was back to normal. Th… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i have a bryant heat an a rheem a/c the furance is showing
i have a bryant heat an a rheem a/c the furance is showing a code 2 red flashes fallowed by 4 red slow flashes so code 24 i replace the 3amp fuse that was blown it fired up an ran for about 3 min it s… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
How do change a multi-speed fan to the low operating mode
How do change a multi-speed fan to the low operating mode? Also, I have a 50,000 btu furnance supplying a 2,200 sq ft basement. The thermostat is set on 71 and the unit continues to cycle very quickly… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.