Our digital thermostat went blank. We have a model

Customer Question
Hi! Our digital thermostat...

Hi! Our digital thermostat went blank. We have a model CU5830-C175 Payne furnace. Code 33. I replaced a very dirty filter, manually hit the reset and the furnace worked, fan and flame. Goes through a cycle then again the thermostat goes blank.

Contractor's Assistant: Have you tried power cycling the appliance -- unplugging it and leaving it off for a few hours?

I have turned off the breaker for a minute or so.

Contractor's Assistant: Do you plan on doing the work yourself?

I will try! I have a smarter friend that might help me later in the day if necessary.

Contractor's Assistant: Anything else we should know to help you best?

I have electric space heaters ;-)

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
11/21/2017
HVAC Technician: airheatman, HVAC Technician replied 7 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,182
Experience: Furnace, A/C and heat pump specialist.
Verified

Can you give me the complete model number on the furnace?

The number on outside of furnace is just a series.

Actual model will be on a label on inside furnace panel just above burners.Remove panel to burner compartment and look inside. The model number will help me give accurate assistance for your specific unit.

Below is a link to a generic video showing where to find label with model number:

https://www.youtube.com/watch?v=KZfyeZOFdpU

If furnace is not coming on or does not stay on , there should be an error light flashing on the control board in blower compartment to indicate what has failed. If you can locate this and tell me the pattern of the flash, that will point us in the right direction for troubleshooting.

Also let me know if you have a multi meter for troubleshooting.WE will go from here.

Ask Your Own HVAC Question
Customer reply replied 7 months ago
I do not have a multi meter. Model No.PG9MAA036080. light flashes 33 Limit circuit fault.
HVAC Technician: airheatman, HVAC Technician replied 7 months ago

Thanks. Now right now, do we have display and thermostat calling for heat?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have carrier furnace model CK5BXA048021AAAA that is not
I have carrier furnace model CK5BXA048021AAAA that is not heating up. … read more
airheatman
airheatman
HVAC Technician
9,182 satisfied customers
Plus 90i flashing a 33 fault code. blower seems to be
Bryant plus 90i flashing a 33 fault code. blower seems to be running at a low speed. thermostat has no power … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an error code 33 on my 90i plus. I think that means I
I have an error code 33 on my bryant 90i plus. I think that means I need to clean the filter - which I did and they were very dirty. However the error code 33 is still flashing and I'm reading that I … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
my furnace keeps shutting off. I press the reset button, it
my furnace keeps shutting off. I press the reset button, it comes on then reaches the set temp goes off, then wont come back on until I hit the reset button again.… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I woke up this morning and my Bryant thermostat###-##-####00001
I woke up this morning and my Bryant thermostat###-##-####00001 screen is blank and cold air is blowing from the vents.… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have a payne furnace PG9MAA. All of a sudden, there was
I have a payne furnace PG9MAA. All of a sudden, there was just cold air coming out of my vent and the fan would run constantly in auto and not turn off. I tried powering down the furnace and powering … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier furnace model cu5830-c175, serial no 6098f01123.
I have a Carrier furnace model cu5830-c175, serial no 6098f01123. The blower is running, however, it's blowing cold air. The red LED light is blinking 3 quick times, then 3 slow times. Any ideas?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Payne furnace model CU5830-C175. The blower is working,
I have a Payne furnace model CU5830-C175. The blower is working, but is blowing cold air. The LED indicator was flashing code ‘13'. I pulled the filter, and now have a solid indicator light. Should I … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
im dealing with a payne two stage heater series 100. model
i'm dealing with a payne two stage heater series 100. model pg9mxa. went to increase temp while stat was in heating mode but not running. blower fan came on with no heat and hasn't shut off without ha… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Payne PG8JAA furnace. The blower stays on. Ive read
I have a Payne PG8JAA furnace. The blower stays on. I've read that I may have to manually reset the control switch. But I can't find it. I have taken the access panels off. I see a circuit board, but … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a payne furnace is give me a code 33 mod pg8maa024070
I have a payne furnace is give me a code 33 mod pg8maa024070 ser 4506a18928, when the furnace just turned on with power it go straight to the code 33 the inducer fan did not come on at all just the bl… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
My BRYANT 310AAV/JAV Is not giving out heat fan is continuously
My BRYANT 310AAV/JAV Is not giving out heat fan is continuously running just changed filters code changed from 13 to 33 after i took panel off now what can I do to get the heat back.… read more
airheatman
airheatman
HVAC Technician
9,182 satisfied customers
Hello, I have Lennox CX34-31A-6F Heater. A month ago, my thermostat
Hello, I have Lennox CX34-31A-6F Heater. A month ago, my thermostat digital display controlling the heater went blank. I bought a new thermostat and installed it. The heater has switched on, but is bl… read more
jason3kgt
jason3kgt
Technician/salesman
3 years at University
19 satisfied customers
I have a Payne downflow furnace, model PG8DAA. The blower runs
I have a Payne downflow furnace, model PG8DAA. The blower runs continously. I have code 33 flashing. I have cleaned the filters, cleaned the flame sensor, reset the manual reset limit switches. I am u… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Coldest night of the year and my Payne gas furnace (no pilot
Coldest night of the year and my Payne gas furnace (no pilot light kind) is blowing cold air only. Did the recycle thing. When power applied, blower comes on immediately, but no burners that I can tel… read more
Shane D
Shane D
HVAC Service Manager
32 satisfied customers
heating system is shutting off before it reaches set temp
my heating system is shutting off before it reaches its set temperature? Also the temperature is going up much slower than normal. The code shows 3 shorts and 3 longs. I had the same problem last year… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
We have a Bryant central gas furnace that is virtually brand
We have a Bryant central gas furnace that is virtually brand new but has never worked right since we moved into our house. It will come on for a while but then shut itself down and then it will not re… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
i have a payne pg8uaa upflow furnace. i noticed i was getting
i have a payne pg8uaa upflow furnace. i noticed i was getting cold air. the fan runs nonstop but doesnt light. i am getting code 33, but if i turn thermostat up i get 13 briefly.. i am lost! i checked… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x