Airease RPGE13 will not crank up for heating for the first time this season. LED indicator light is blinking a fast steady blink which is supposed to indicate normal operation. I am a handyman by trade and at a friends house trying to help them out. Any tricks of the trade would be appreciated
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
11/21/2017
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,712
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

One moment please..Note it takes time to type and add links so please be patient. Also the site will send you a phone call offer, that is not me.

Ask Your Own HVAC Question

Sounds like maybe a thermostat issue, is the thermostat battery powered? If so replace the batteries and try it. If not when you switch the thermostat to FAN ON does the fan run?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
It will be a few minutes til I can check I will be back with you in a few minutes

No problem

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Ok, we were purging the gas system per the instructions on the panel. So I had to wait before turning it back on.
I turned it back on by the fuse panel with the gas system switch off,the system started up with the fan on and the sound I usually associate with gas running on any heater unit. When I turned the switch to on the whole unit stopped everything,no fan no running gas sound. I came to the thermostat and played with the settings to make sure heat was supposed to be currently on, nothing happened. I switched the fan to run now,nothing happened. We are dealing with a nest thermostat,so we now have it taken off the wall and are charging it to make sure it is charged.
So I guess any other ideas for when we try it again in about 30 mins would be awesome
Customer reply replied 8 months ago
Oh and now the LED is blinking a 2 pattern and I can’t make out the code explanation on the panel because the sticker is deteriorating

Shut the power off to the unit for about 20 secs and turn it back on and try it again

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Ok the light is blinking fast steady again,but the fan still won’t come on and nothing else does either.Ok the unit just attempted to cut on,it started sounding like it was going to kick in it revved up for about 5 seconds and did not ignite and then it revved down ,when it did the light actually began blinking even faster so I guess it is blinking at the slow steady blink actually
Customer reply replied 8 months ago
It has tried a second and a third time but kicks off after 5 seconds or so when it doesn’t ignite

CLICK HERE Also make sure that tube is not cracked.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
We got it going, it was a wiring problem at the thermostat. The C wire was a light blue that connected to a yellow and then came from the unit to the thermostat and whoever installed it had it hooked to y1 instead of C..that got the heat properly working and no more Nest codes but it only registers the heat it doesn’t register the cool now which is what it was using of course thru the summer. So they’re going to have a tech come out I guess to finish it up. Thank you for your help

OK no problem, weird issue have a Happy Thanksgiving!

All I ask is please select the 5 STAR rating at the top of your page before leaving otherwise I receive ZERO credit for assisting you. Thanks and you can come back anytime for free followup questions.

HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,712
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified
HVAC Guru and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,712
18,712 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My HVAC system stopped working yesterday. Here are the
Hi! My HVAC system stopped working yesterday. Here are the components: White Rodgers Thermostat 1F81-51 White Rodgers Control Module 50A51-495 Trane XL 80 The screen on the thermostat went blank. I to… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an American Std UY120R9V5V . The zone controller is
I have an American Std UY120R9V5V . The zone controller is calling for heat, but there is no ignition or blower activity. The vent fan runs continuously which is not normal. It was running fine yester… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Trane XB80 gas furnace / air conditioner that will
I have a Trane XB80 gas furnace / air conditioner that will not light sometimes. It has a White Rodgers circuit board 50A55-571 with a blinking red light. Usually, when I turn off the thermostat for a… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
Hello Mr. HVAC Technician, We have a GHR26 Lennox Elite Series,
Hello Mr. HVAC Technician, We have a GHR26 Lennox Elite Series, Model CHR26Q3-75-8. The 2 lights are blinking normally. When I remove the door panels and depress the door sensor switch, the only thing… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
Hello, Last month I had a new Trane HVAC system installed
Hello, Last month I had a new Trane HVAC system installed at my home. This was a complete replacement of the AC, coil, and furnace. The furnace is a down draft XR95, the AC is an EXR 16. The AC works … read more
R G
R G
44 satisfied customers
I HAVE A LENNOX 80UHG FURNACE. IT WILL NOT COME ON AT ALL.
I HAVE A LENNOX 80UHG FURNACE. IT WILL NOT COME ON AT ALL. CODE LIGHTS BLINK AT THE SAME TIME SLOW. WHEN THERE IS A DEMAND FOR HEAT THE LIGHTS BLINK FAST AT THE SAME TIME. AFTER A FEW MIN. THE LEFT LI… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a question concerning a goodman furnace - GMS80905CNBD. The
I have a question concerning a goodman furnace - GMS80905CNBD. The draft blower comes on but no gas flows. Looking at the pressure switch, the voltage at the terminals is 1.16 volts when the blower is… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My P474-1100RF theromstat isnt communicating with the receiver.
My P474-1100RF theromstat isnt communicating with the receiver. Unlike my first P474 that died, the thermostat looks ok and the buttons work, but it doesnt control the HVAC unit. During the winter, I … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
What is the reason for red blinking light inside the furnace?
What does the red blinking light mean inside the furnace? Can be seen from the small peep hole on lower furnace panel? There was a gas outage in our area. Gas service has been restored and furnace see… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
The furnace is working but I can see a flashing red light and
The furnace is working but I can see a flashing red light and a steady green light through the small window in the front of the furnace. What does the flashing red light mean?… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
So Ive installed a new thermostat and am running throught
So I've installed a new thermostat and am running throught the test in the instruction. Said to crank the heat up to 90 and wait two minutes. Did, but cool air is blowing out. Looking through peephole… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a Payne PG9MAB furnace. I smell an electrical burning
I have a Payne PG9MAB furnace. I smell an 'electrical burning' smell which prompted me to check the furnace. I removed the front panel and see the red LED status light is solid red - should it be soli… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
have a gks9, red light is on (not blinking), furnace doesnt
have a gks9, red light is on (not blinking), furnace doesn't start . The thermostat is an honeywell (3 wires), fan is working when if force the fan on, .... fast answer is appreciated ... It's pretty … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Lennox 80MGF 4/5-120A-1 furnace. Same symptoms as
I have a Lennox 80MGF 4/5-120A-1 furnace. Same symptoms as asked back 300 days ago by a different customer. Just need a little help with diagnosis. I'm able to troubleshoot with you. I have a Lennox M… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Fan runs, orange glow, relay clicks but no gas ignition, red
Fan runs, orange glow, relay clicks but no gas ignition, red led is blinking, is the problem the ignitor or gas valve? Model of unit is Trane X880. Resistance of ignitor is around 34 ohms.… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a trane xr90 and a honeywell minizone. No heat, but
I have a trane xr90 and a honeywell minizone. No heat, but the fan runs. Minizone shows no calls for heat, though all zones' thermostats are set high enough to call for heat. Furnace blinks steady red… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have a RUUD Super Quiet 80 Two-Stage. Presently operating
Have a RUUD Super Quiet 80 Two-Stage. Presently operating on heat cycle. When looking through blower compartment window, I see the 4 LED's lit up in this order from left to right: yellow/steady - gree… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
one the bottom half of our furnace (a Trane high efficiency
one the bottom half of our furnace (a Trane high efficiency two stage XL80) there is a clear circle.....there is now a constant blinking red light here in this circle. what does this mean? we recently… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x