I have a weil mclain boiler CGA gold that won't fire up. The gas valve does not open. Measured voltage there I get about 1 volt. Checked the pressure switch and resistance across switch goes to 0 when functioning, Fusable link has resistance of 0.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

This is the first I turned the system on this season

Contractor's Assistant: Do you plan on doing the work yourself?

If possible I have some technical ability

Contractor's Assistant: Anything else we should know to help you best?

I already replaced the valve so I can rule that out

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
11/21/2017
HVAC Technician: Webb-Guy, HVAC Mechanic replied 7 months ago
Webb-Guy
Webb-Guy, HVAC Mechanic
Category: HVAC
Satisfied Customers: 3,306
Experience: maitenance tech at casto
Verified

Hello, and welcome to JustAnswer. My name is ***** ***** I will be the one to assist you. Sorry to hear that you are having this trouble.

On the CGA there are only about 3 things that will make the gas valve not open.

The first is if the motorized flue damper malfunctions...This is pretty common on those things. If it doesn't wind all the way open, it won't make the end switch.. That will hold the gas valve out. The switch in them goes bad as well. The other thing is the roll out switch which you have already checked so that should be good. The other thing is the draft hood spill switch located on the flue pipe.

I would say your problem is more then likely the flue damper.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Webb-Guy Your Own Question
Webb-Guy
Webb-Guy
Webb-Guy, HVAC Mechanic
Category: HVAC
Satisfied Customers: 3,306
3,306 Satisfied Customers
Experience: maitenance tech at casto

Webb-Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have Weil-MclAIN GOLD CGA GAS BOILER....AND FLAME LIGHT IS
HI.I have Weil-MclAIN GOLD CGA GAS BOILER....AND FLAME LIGHT IS BLINKING. WHAT THAT MEAN ? HOW THAT FIX ? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Weil-mclain boilers cga series 2 gas fired water boiler
weil-mclain boilers cga series 2 gas fired water boiler model 1135-605 need to replace circulator pump how much will it cost and where can I get one … read more
Webb-Guy
Webb-Guy
HVAC Mechanic
3,306 satisfied customers
My boiler went off pilot light is on I have turned off and
my boiler went off pilot light is on I have turned off and then back on the pilot is the only thing that is working and my oven will not go on no smell of gas put my burns on my stove are working. I h… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We have in our basement a Weil-McLain (probably between 15
We have in our basement a Weil-McLain (probably between 15 and 25 years old) system that heats water (using natural gas from the street) for baseboard-water heating of our rooms and for hot water comi… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have a Weil-McLain EG50 natural gas steam boiler with Honeywell
Have a Weil-McLain EG50 natural gas steam boiler with Honeywell gas valve and standing pilot. House gas pressure seems OK. The boiler flame is on but not at full output. Is this a problem with the gas… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
i have a weil mclain gold gv boiler that starts the purge light
i have a weil mclain gold gv boiler that starts the purge light comes on and it shuts off no heat… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Weil Mclain Gold gas CGa boiler operated buy dual
I have a Weil Mclain Gold gas CGa boiler operated buy dual zone Taco SR 502 relay controller. My problem is that slowly over time the boiler is not lighting with either thermostat, though the circulat… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a weil mclain gold cga gas boiler converted to propane
I have a weil mclain gold cga gas boiler converted to propane that is 10 yrs old. it is a 105000 btu input. at the end of last heating season i noticed it was using a lot more gas and sometimes it wou… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Weil McLain Gas boiler does not fire. What do I do?
I have a Weil McLain gas boiler, pilots lit but it won't fire off. I put 24 volt relay power to the main gas valve, the one with the two blue wires and bam it fired off and running good. But it is not… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have a Weil McLain Gold CGa boiler. Home inspector found
I have a Weil McLain Gold CGa boiler. Home inspector found that during unit operation the boiler exceeded "normal operating pressure" causing the pressure relief valve to open and discharge water. The… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
2003 140,000 BTU Weil- Mclain Gold CGa pilot light Boiler. I
2003 140,000 BTU Weil- Mclain Gold CGa pilot light Boiler. I turned off main 110 Volt supply at the boiler two days and now boiler will not fire up. Pilot light is on. My boiler is wired to run as a h… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a gas furnace Weil Mclain Gold CGa. The burner tubes
I have a gas furnace Weil Mclain Gold CGa. The burner tubes at teh bottom of the furnace are falling and this causes the falme to spread. Could you advice me on what needs to be done and whether this … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My W-M Gold CGA boiler model # 1107-2 will shut off even when
My W-M Gold CGA boiler model # XXXXX will shut off even when the thermostat is calling. The amount of time the boiler fires is becoming less and less. Any suggestions?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Weil-McLain Gold GV Series 3 gas fired boiler. What
I have a Weil-McLain Gold GV Series 3 gas fired boiler. What is the operating pressure of the boiler?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My son bought a new Weil-McLain GOLD CGa gas fired water boiler
My son bought a new Weil-McLain GOLD CGa gas fired water boiler (UR8200C1074) for his new shop. The boiler came set up for natural gas. Since natural gas isn't available in his location, it also came … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Weil McClain CGA gas boiler. The boiler has Honeywell
I have a Weil McClain CGA gas boiler. The boiler has Honeywell VR8200 gas valve. For the past couple of weeks, the boiler has a problem with the flame; not all the heating elements on the boiler light… read more
Daniel A.
Daniel A.
Vocational, Technical or Trade Scho
3 satisfied customers
We have a Weil Mclain Gold CGa gas-fired water boiler and it
We have a Weil Mclain Gold CGa gas-fired water boiler and it has stopped working. The pilot light is still on, but when we kick up the thermostat nothing happens. This morning we were able to hear wat… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We have a new Weil McLain CGA Gold heater. When it starts
We have a new Weil McLain CGA Gold heater. When it starts up it sound like a "sonic boom". It is one year old; however, we just moved in September and house was empty for the year. Is there a problem … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x