I have a loga max 142-45 the water relief valve started

I have a loga...

I have a loga max 142-45 the water relief valve started leaking water. Replaced the expansion tank and releif valve. Still leaking. now contractor wants to replace the hot water heater. please help with other suggestions

Contractor's Assistant: How long has this been going on? And how severe is the problem?

Since Friday. Water is still dripping from relief valve and pressure stays up to 27psi+. Even when relieving off some water to bring down the pressure to 13 psi. Water is still coming from the relief valve

Contractor's Assistant: Do you plan on doing the work yourself?

No I have a contractor I am questioning

Contractor's Assistant: Anything else we should know to help you best?

No I have a contractor. They are guesign at this tim

Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 minutes by:
11/20/2017
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,631
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

It's common for a relief valve to not seat properly (and leak) after a discharge so replacing the valve is the first step. If the water heater were the cause (I assume you have an indirect fired heater, coil in the tank) you can rule it in or out by shutting off the cold water into the tank then open a faucet (hot only) to dissipate the pressure. If the pressure does not rise (start at 10 to 15 psi) then the tank is the culprit. If it continues to rise and the boiler is off (not firing) then the feed valve that controls water pressure let into the boiler is the likely culprit.

Ask Your Own HVAC Question
Customer reply replied 9 months ago
I will try this. If after replacing the boiler relief valve and it still leaks at even 20 psi, does it need to be replaced again?
Also, the water heater is only 8 years old, I had the annode replaced last year and it was not that bad (had a few years left before it really needed to be replaced) so water is good in the area. Very disappointed in Buderus equipment. What would you recommend that with go with this system that is better quality?

SuperStor Ultra (stainless steel tank) is a better tank option. I suspect your gauge is off if a new relief valve starts to leak at 20 psi. I'd verify the actual pressure with a test gauge (you can get one at the bigbox stores) before replacing the relief valve again. You screw the test gauge onto any hose type valve on the sytem then open the valve to read the pressure.

Ask Your Own HVAC Question
Customer reply replied 9 months ago
had to replace the water heater so now the relief valve has stopped leaking. What pressure range should the Buderus Logamax142-45 boiler be running at now?

12 to 15 psi when it's cold up to ~25 psi when it's hot.

I'd appreciate a favorable rating. The thread won't go away and I'll answer related follow up questions even after you rate me favorably

Ask Your Own HVAC Question
Customer reply replied 9 months ago
Thank you. Since the water heater was installed, when the heat goes on, we hear water rushing through the baseboard when heat is called for. Never heard that before. It's very noisy. Do they usually need to be bled or will it go away?

Yes, part of the job is to purge the air out of the system. If it isn't eventually an air ocket will form and stop the water from circulating. Call your plumber back and tell him to finish the job properly.

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,631
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,631
24,631 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Water pressure input. recommended values, please. tem[p
water pressure input. recommended values, please. tem[p setting on one i am working on is "B". the pop off valve is leaking. it was replaced. it continues to act the same. … read more
Rick
Rick
HVAC Supervisor
24,631 satisfied customers
I have a Weil McLain CGi direct vent boiler approx. 13 years
I have a Weil McLain CGi direct vent boiler approx. 13 years old. The boiler temp reaches the limit temp before the call temp is met. … read more
Rick
Rick
HVAC Supervisor
24,631 satisfied customers
Phil - I have a Triangle Tube Prestige Excellence Water
Hi Phil - I have a Triangle Tube Prestige Excellence Water Boiler (Heating and DHW). It continues to dribbe water from the Pressure Relief Valve (which was replaced by a technician about 2 weeks ago).… read more
Rick
Rick
HVAC Supervisor
24,631 satisfied customers
Pressure gage on boiler wont go lower than 20 psi regulator
pressure gage on boiler wont go lower than 20 psi regulator is set at 12 lbs turn water on a week later relief valve went off why is this and could the boiler be damaged… read more
Rick
Rick
HVAC Supervisor
24,631 satisfied customers
Water drips in the back of my boiler through the relief
Water drips in the back of my boiler through the relief (safety) valve, and the boiler pressure stays around 35-38 psi. The tech replaced the relief valve, and the boiler pressure was initially slight… read more
Rick
Rick
HVAC Supervisor
24,631 satisfied customers
What is the normal working PSI rating Ultra 230, 230,000 BTU
What is the normal working PSI rating for the Ultra 230, 230,000 BTU Natural Gas Boiler. What should the PSI rating be on the pressure relief valve. The boiler is less than a year old.… read more
Rick
Rick
HVAC Supervisor
24,631 satisfied customers
. I have a weil mcclain gv 90+ which is about 2 years
Hello. I have a weil mcclain gv 90+ which is about 2 years old. As it circulates, it gets up to around 70-80 psi. The temperature on the below part of the gauge gets up to the red arrow, which is arou… read more
Rick
Rick
HVAC Supervisor
24,631 satisfied customers
Boiler dripping out the overflow relief pipe. I flipped the
Boiler dripping out the overflow relief pipe. I flipped the lever a few times to clear any debris that might have been causing it to not close properly, now it's worse. A five gallon bucket would have… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Hydrotherm R-250 boiler. The problem is that there
I have a Hydrotherm R-250 boiler. The problem is that there is water on the floor under the pressure relief valve. I can never catch the moment when the relief valve is set off but I have seen a drop … read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
Have a RSA furnace. Preasure relief valve leaking. Water temp
Have a RSA furnace. Preasure relief valve leaking. Water temp is reading 230. and water preasure is reading 0. I know that it should be at 190 and 15 psi. And im not understanding the cause and effect… read more
Rick
Rick
HVAC Supervisor
24,631 satisfied customers
I have a Smith boiler, 8 Series, S/W 3. When the boiler fires
I have a Smith boiler, 8 Series, S/W 3. When the boiler fires up there is a leak from the pressure relief valve (amounts to about a gallon per day). The relief valve on my water heater simultaneously … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
I have an older Thermo Dynamics S-100 boiler and there was
I have an older Thermo Dynamics S-100 boiler and there was quite a bit of water coming out of from the pressure relief pipe. I cleaned the lime off of the pressure release valve and then ran about 2 g… read more
Rick
Rick
HVAC Supervisor
24,631 satisfied customers
Hello--In the last week or so since we have been having really
Hello--In the last week or so since we have been having really cold weather. I notice that by boiler pressure relief valve has been draining sometimes. I have called a plumber, but he probably won't c… read more
Rick
Rick
HVAC Supervisor
24,631 satisfied customers
I have a hot water oil fired boiler heating system. The relieve
I have a hot water oil fired boiler heating system. The relieve valve [ 30 psi ],expansion tank,and ato water feed have been changed .The relieve valve discharges hot water every 30 minutes when the b… read more
Rick
Rick
HVAC Supervisor
24,631 satisfied customers
What max pressure should the pressure relief valve be on a
What max pressure should the pressure relief valve be on a Weil-McLain Model CGs residential gas/water boiler… read more
Rick
Rick
HVAC Supervisor
24,631 satisfied customers
I have a like-new natural-gas hot water heating system that
I have a like-new natural-gas hot water heating system that lately builds up pressure of over 30psi despite properly working Honeywell L8148E 1265 Aquastat set to 185F max. The burner is working betwe… read more
Rick
Rick
HVAC Supervisor
24,631 satisfied customers
On an oil fires peerless boiler I noticed some water under
On an oil fires peerless boiler I noticed some water under the pressure relief valve in back of the boiler. Why would that be leaking water and is it a problem?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have an apollo water heating system that is now leaking water
I have an apollo water heating system that is now leaking water through the pressure relief valve on the hot water heater. I have replace the pressure relief valve and it still leaked. Yesterday, I re… read more
Rick
Rick
HVAC Supervisor
24,631 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x