I have a 80uhg that when i call for heat the gas burner

Customer Question
I have a 80uhg...

I have a 80uhg that when i call for heat the gas burner doesnt light and the blower comes on

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Are you there

Contractor's Assistant: Do you plan on doing the work yourself?

Thermostat auto and heat, and filters are new

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
11/20/2017
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago
Webb-Guy
Webb-Guy, HVAC Mechanic
Category: HVAC
Satisfied Customers: 3,309
Experience: maitenance tech at casto
Verified

H​ello, and welcome to JustAnswer. MY name is ***** ***** I will be the one to assist you. Sorry to hear that you are having this issue. From the sounds of it your ignitor or thermocouple has went bad and is going to need to be replaced.

Ask Your Own HVAC Question
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

is​ there any flashing lights that are happening?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Led 1 is on led 2 is flashing slow, and both roll out swithes are closed
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

have you tried resetting the roll out switches yet? If not lets try that first and we can go from there. This could possibly be a clogged inducer motor or your inducer motor may have gone bad.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Tried reset neither one was triped
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

ok so what I need you to check is the hoses to the inducer motor you can try blowing through them by your mouth if your careful or somehow making sure there is nothing clogging those hoses.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Are you talking about the hose from the combustion blower to the presure switch?
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

yes

Ask Your Own HVAC Question
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

have you tried testing the roll out switches with a multimeter?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
No
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

ok now did you check the hoses first?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
i checked the hose
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

ok lets try ohming out the roll out switches

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I did and both were closed
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

well the code you are getting is

Rollout switch open. OR: 9 pin connector improperly attached.

Ask Your Own HVAC Question
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

le​ts try one more thing can you test the pressure switch for me

Ask Your Own HVAC Question
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

because the only other option is that you have a bad board and I want to rule out what we can before diagnosing that.

Ask Your Own HVAC Question
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Ask Your Own HVAC Question
HVAC Technician: Webb-Guy, HVAC Mechanic replied 8 months ago

I noticed that your question was still open were you needing anything further?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Webb-Guy Your Own Question
Webb-Guy
Webb-Guy
Webb-Guy, HVAC Mechanic
Category: HVAC
Satisfied Customers: 3,309
3,309 Satisfied Customers
Experience: maitenance tech at casto

Webb-Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
We have a trane gas furnace (xr-90). our blower was on
We have a trane gas furnace (xr-90). our blower was on continuously with no heat. the glo plugs came on but the burner did not. I tested the themostat for continuity on the R and G terminals and got c… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox 80UHG Series heater that the blower does not
I have a Lennox 80UHG Series heater that the blower does not blow. … read more
Tim Ohms
Tim Ohms
HVAC Journeyman
31 satisfied customers
I have a lennox g2604/5-100-1... the gas will not stay on
Hi, I have a lennox g2604/5-100-1... the gas will not stay on when the heat is called for. In fact, more appropriately said, the gas will not ignite at all. The only way to get heat is to go through t… read more
Rick
Rick
Supervisor
24,226 satisfied customers
My rheem gas furnace heat does not ignite in manual or auto
my rheem gas furnace heat does not ignite in manual or auto mode but the blower comes on in manual mode with no heat. … read more
Rick
Rick
Supervisor
24,226 satisfied customers
My gas furnace is blowing cold air, the burner unit isn't lighting.
My gas furnace is blowing cold air, the burner unit isn't lighting. Checked thermostat settings, everything is OK. All breakers are on and power is getting to the package unit. I've tried resetting th… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
a vacation home is heated with gas furnace but to save money
a vacation home is heated with gas furnace but to save money the gas is turned off and the home got winterized. the owners forgot to turn off the furnace before leaving. the owners left the electricit… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Rheem Imperial 80-plus downdraft gas furnace, hot surface light,
Rheem Imperial 80-plus downdraft gas furnace, hot surface light, no A/C, mfd. 1988, MODEL # XXXXX Must leave fan on for burner to operate correctly. No apparent problem with hot surface ignitor or oth… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
Billy~ My furnace pilot light lights, stays on, the burners
Billy~ My furnace pilot light lights, stays on, the burners engage and everything shuts off in 30 to 60 seconds?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi - I have an American Standard Freedom 78 gas furnace. The
Hi - I have an American Standard Freedom 78 gas furnace. The furnace starts up and you can hear the click to call for heat and the inducer motor is running. Burners do not come on and the blower does … read more
warmneighbor
warmneighbor
owner
Vocational, Technical or Trade Scho
162 satisfied customers
I have an AMANA GUCA90AX40 in a home I just purchased. When
I have an AMANA GUCA90AX40 in a home I just purchased. When the thermosat calls for heat, everything seems to sequence properly meaning the blower for the burner comes on, I see the igniter glow, gas … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Rheem Criterion II furnance 10 years old. Heat and blower
Rheem Criterion II furnance 10 years old. Heat and blower comes on, when room temp is reached, heat turns off blower keeps running. When temp drops below thermostat setting heat comes back on but blow… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
I have an American Standard Freedom 90 I cant find a model
I have an American Standard Freedom 90 I can't find a model number are serial number. It is 11 years old. The burner lights but Blower does not come on. I can jumper the blower and it works. Can the f… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
Lennox Elite Gas Furnace starts inducer fan motor for 5 to
Lennox Elite Gas Furnace starts inducer fan motor for 5 to 10 seconds then stops. Green light on igniter control lights after inducer fan motor starts goes out when it stops. If fan switch on thermost… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
We have a Nordyne furnace and when heat is set on auto we can
We have a Nordyne furnace and when heat is set on auto we can hear it kick on however it never starts blowing. When we flip the switch to heat and on it only blows cold air. The pilot light is on.… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
my furnace is 25 years old ,Carrier . problem when thermostat
my furnace is 25 years old ,Carrier . problem when thermostat is calling for heat, the main gas valve comes on and then the blower starts, just after the blower is on for a few minutes the main gas bu… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
I have a carrier weathermaker 8000 two speed furnace i just
I have a carrier weathermaker 8000 two speed furnace i just installed a new hunter thermostat model number 44860 i set the programs the thermostat will turn on my blower but it will not ignite the bur… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have an older model Luxaire furnace. The pilot is lit and
I have an older model Luxaire furnace. The pilot is lit and strong but the burners wont stay lit. When I shut it down, including turning the pilot off, the burners will light for one minute then shut … read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a Carrier 58mxa 080-16 gas furnace. Installed 1/30/04.
I have a Carrier 58mxa 080-16 gas furnace. Installed 1/30/04. When heat is called for the hear goes on and the blower motor starts with 60 sec delay. The blower motor goes off after @ 10 min even thou… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x