Hi, I have a 1989 vintage Vaillant boiler that continues to ignite and then shuts off. What would cause this problem?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

I think only for a week or so.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes or if too hard i can get help.

Contractor's Assistant: Anything else we should know to help you best?

All the zone valves were recently replaced and all seem to work properly and the house is warm and comfortable then this popped up.

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 7 hours by:
11/20/2017
HVAC Technician: Andrew Smith, HVAC Technician replied 8 months ago
Andrew Smith
Andrew Smith, HVAC Technician
Category: HVAC
Satisfied Customers: 3,781
Experience: City & Guilds Plumbing and Heating Engineer
Verified
It doesn't know it is lit. Try cleaning all the electrodes and that does not work then replace them and their leads
Ask Your Own HVAC Question
Customer reply replied 8 months ago
I forgot to mention that I had a local plumbing company do a full service and diagnostic check, they could not give me a good reason for this problem. It still does the same thing. I did find the model # on it, it's a Vaillant GA92-080 . I am thinking it may be time to replace it.
HVAC Technician: Andrew Smith, HVAC Technician replied 8 months ago

It may just be a £40 fix?

Is there a model name on the boiler case?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
no not that I could find just the model & serial and technical info.
HVAC Technician: Andrew Smith, HVAC Technician replied 8 months ago

Could it be the EcoCraft?

It sounds quite old?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I don't know, no name anywhere on the boiler. And yes is a bit old , installed in 1989 but not sure of the model year of the boiler.
HVAC Technician: Andrew Smith, HVAC Technician replied 8 months ago

A decent engineer would know to look at the electrodes.

Perhaps give another engineer a ring and explain the problem before they come out to see you?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Andrew Smith Your Own Question
Andrew Smith
Andrew Smith
Andrew Smith, HVAC Technician
Category: HVAC
Satisfied Customers: 3,781
3,781 Satisfied Customers
Experience: City & Guilds Plumbing and Heating Engineer

Andrew Smith is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Can't seem to stop the heat in one of the two zones in our
can't seem to stop the heat in one of the two zones in our loft. This happened earlier this year and our plumber made some adjustment to correct. I believe it is related to the Honeywell zone valve. I… read more
Rick
Rick
Supervisor
24,233 satisfied customers
I am a general contractor and have 2 things I need answered.
I am a general contractor and have 2 things I need answered. First, I have a Teledyne Laars 85,000 btu mini therm II boiler that is supplying 5 radiant floor zones. I believe that this boiler was inst… read more
Rick
Rick
Supervisor
24,233 satisfied customers
I am having trouble with my honeywell aquastat relay type
Hi i am having trouble with my honeywell aquastat relay type l8148e on a crown boiler, my boiler will not start unless i prop open the switching relay, i checked all my thermostats and they have power… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Lochinvar Knight model WHN085. It is set up for 2
I have a Lochinvar Knight model WHN085. It is set up for 2 zones. Even with both thermostats set to 50 degrees F, the temp in the house is nearly 80. It appears that the boiler is not cycling off.… read more
Rick
Rick
Supervisor
24,233 satisfied customers
I have 2 Burnham Alpine 80s. Installed new, a month ago. Oil-to-gas conversion. Had noi
I have 2 Burnham Alpine 80s. Installed new, a month ago. Oil-to-gas conversion. Had noise issues and both boilers required "tuning" - adjusting CO2 levels and other settings. Now my boiler is quiet an… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a honeywell aqua l8124l with two thermostats, two erie zone valves and one grundfo
I have a honeywell aqua l8124l with two thermostats, two erie zone valves and one grundfos circ pump. I think the circ pump is only running when the boiler is on and not when the therm is still callin… read more
Nathan Marshall, MP
Nathan Marshall, MP
Master Plumber,HVAC Tech,Tradesman
Vocational, Technical or Trade School
275 satisfied customers
I recently had a new Vaillant combi boiler fitted to replace
I recently had a new Vaillant combi boiler fitted to replace an ancient hot water tank system. Before this was done my thermostatic shower worked fine. When you initially turned the shower tap on cold… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
The circulator on my Weil Mclain boiler doesnt repsond to the
The circulator on my Weil Mclain boiler doesnt repsond to the thermostat. I closed the manual flow valve to prevent the baseboards from "heating" during the summer. I recently had to open the valve to… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I have a white-rodgers comfort plus zoning system. We live
I have a white-rodgers comfort plus zoning system. We live a a three story town house. Recently, the second or first were not cooling properly. After much investigation, I found the system light on th… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
We have a Taco 3 Zone switching relay. The system was working
We have a Taco 3 Zone switching relay. The system was working very well for several years until recently. We use two heat zones. Recently the heat in the basement zone is not turning off, even when we… read more
Rick
Rick
Supervisor
24,233 satisfied customers
My Vaillant GA 100 PV boiler makes a thumping sound when heating,
My Vaillant GA 100 PV boiler makes a thumping sound when heating, particularly at near shut-off temps. I just had the igniter replaced, and the service repair guy increased the system pressure. My gue… read more
Rick
Rick
Supervisor
24,233 satisfied customers
Hello! We have a 17 year old Vaillant 100,000 BTU floor mounted
Hello! We have a 17 year old Vaillant 100,000 BTU floor mounted boiler. Model GA92. For the past 3 months it has been making what sounds like "popping" noises almost constantly when the furnace is run… read more
Rick
Rick
Supervisor
24,233 satisfied customers
My 13 year old Burnham V-713 boiler continually builds pressure
My 13 year old Burnham V-713 boiler continually builds pressure until it triggers the pressure relief valve. This happens about every 24 hours and has been happening for about a year and a half. Befor… read more
Rick
Rick
Supervisor
24,233 satisfied customers
I have an Honeywell Magicstat 3200 thermostat that seems to
I have an Honeywell Magicstat 3200 thermostat that seems to have a mind of its own.No problems with it over the past 4 years but in the past couple of days it will run the temperature up to 77 when it… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
I have a Honeywell Triple Aquastat Relay type L8124A, C L8151A.
I have a Honeywell Triple Aquastat Relay type L8124A, C L8151A. Our boiler is used to heat water as well as the house. We have a multi-zone heating arrangment. Our water is extremely hot and can cause… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
I have a beckett forced hot water boiler system that also provides
I have a beckett forced hot water boiler system that also provides hot water for the house. It is an oil burner and now seems to run quite frequently even when the thermostats are turned down and ther… read more
Rick
Rick
Supervisor
24,233 satisfied customers
working on a dual system (back boiler/oil burner) when oil
working on a dual system (back boiler/oil burner) when oil burner is on the water is boiling in back boiler and whistling through system. All valves are working,thermosstat working and both pumps work… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,216 satisfied customers
I would like Mark Henley to answer this question. Mark I discussed
I would like Mark Henley to answer this question. Mark I discussed this problem with you on 4/5/09. My baseboard gets warm even though my thermostat is turned low. I disconnected the wires to my therm… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,216 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x