I have 30 year old gas furnace (no air conditioner). the

Hi, i have 30 year...
Hi, i have 30 year old bryant gas furnace (no air conditioner). the problem is that the fan doesn't stop. searched internet and learned that mostly the problem is with the fan limit switch. however, i can't find such part in this old furnace.
JA: Did you double-check the thermostat's settings? And what about the filters?
Customer: i replaced the filter but it didn't help. thermostat i set to 70 right now. actually, the burner itself operates OK. it detects the temperature and starts but the fan just keeps on running. i had to shot of the switch manually everytimr.
JA: Do you plan on doing the work yourself?
Customer: if possible.
JA: Anything else we should know to help you best?
Customer: do you know if this old furnace has the "fan limit switch"?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 30 minutes by:
11/19/2017
Webb-Guy
Webb-Guy, HVAC Mechanic
Category: HVAC
Satisfied Customers: 2,329
Experience: maitenance tech at casto
Verified

Hello, and welcome to JustAnswer. My name is ***** ***** I will be the one to assist you. Sorry to hear that you are having this trouble. I apologize for the extended wait time you experienced, I've only just come online now and would like to assist you with your question if you are still needing help that is?

Ask Your Own HVAC Question
Customer reply replied 26 days ago
ok. let me know if you need more info from me.
Customer reply replied 26 days ago
well, i guess chatting is better so that i can have the information from you in doc.
Customer reply replied 26 days ago
hello?

just one moment please If the site offers the phone call its not from me please disregard it.

Ask Your Own HVAC Question

ok now what is the model number of your Bryant furnace?

Ask Your Own HVAC Question
Customer reply replied 26 days ago
actually, it's very hard to locate the model. i don't know where to find it. but, it looks like the one in this youtube link. it's has "payne" emblem on the front though.https://www.youtube.com/watch?v=pQtMRjWNWUo

does yours have a tag in the front like this video?

Ask Your Own HVAC Question
Customer reply replied 26 days ago
nut it has "payne" on it.

and there is no numbers on it?

Ask Your Own HVAC Question
Customer reply replied 26 days ago
no

ok ​your limit switch should be against the back it should have an arch to it with 4 wires coming out of it. (this information is based on the age of the unit you are saying you have. )

Ask Your Own HVAC Question
Customer reply replied 26 days ago
arch?
Customer reply replied 26 days ago
it is on the unit or separate?

yes sort of round with an arch in it. It is on the unit itself yes.

Ask Your Own HVAC Question
Customer reply replied 26 days ago
do you have any picture or drawing?

well without a model number its hard to pull up which one you have but its like a box looking thing that has a dial on it something similar to this

https://www.searspartsdirect.com/part-number/5D51-35/0042/387.html?utm_source=bing&utm_medium=cse&utm_term=5D51-35&sid=SPDxBING&k_clickID=8487e5ed-41d0-40a2-abe3-0e6cb5dc15fb​

Ask Your Own HVAC Question
Customer reply replied 26 days ago
you said it's on the back, not in front?

yes due to the age I believe yours will be located in the back.

Ask Your Own HVAC Question
Customer reply replied 26 days ago
hmm. there is no cover i can open on he back. well, sounds like i should find the model first. i will try myself with the info you sent to me then.
Customer reply replied 26 days ago
id you can spend a little more time, i can send you the picture of the front. is it OK?
Customer reply replied 26 days ago
i mean, the inside behind the front cover.
Customer reply replied 26 days ago
you spent pretty good time already so it's ok if you cannot.
Customer reply replied 26 days ago
does it help?
Customer reply replied 26 days ago
hello, are you on line?

sorry I had to step away for a minute we are having a storm and it knocked the power out but its back on now. One minute.

Ask Your Own HVAC Question
Customer reply replied 26 days ago
uh ok.

ok ​so that is your gas valve is that a black box behind that though? That sort of looks like your fan switch from what I am seeing behind what you just sent me.

Ask Your Own HVAC Question
Customer reply replied 26 days ago
let me check.

what is with the cord hanging at the bottom? It looks like your glow plug? Has someone else been working on this unit? It looks like it may have been stuck up there to rig it at some point.

Ask Your Own HVAC Question
Customer reply replied 26 days ago
there is a black plastic panel screwed to the wall of the unit. two wires are coming out of it. if i unscrew, maybe, a box (you mentioned) may be in it. as for the cord, i have no idea. what is the white knob. on the top of the valve? i can turn it. does it control the gas flow?

yes it controls the gas.

Ask Your Own HVAC Question
Customer reply replied 26 days ago
ok. i will try to unscrew the black panel tomorrow and see what's inside.

sounds good it should be the fan limit switch

My goal is to give you the best experience possible! I hope I have earned a 5 star rating! Please remember to rate my service by selecting the 5 stars at the top of the screen before you leave today. If you need more assistance, please use the reply box and let me know.

Webb-Guy
Webb-Guy, HVAC Mechanic
Category: HVAC
Satisfied Customers: 2,329
Experience: maitenance tech at casto
Verified
Webb-Guy and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 26 days ago
ok. i'll give you 5 stars. ad, if i have further questions, i will contact you again. thx.
Customer reply replied 21 days ago
Thanks for the follow-up. i think i found the limit switch. i ordered it from eBay. if i have further question when i install it, i will contact you again.
Ask Webb-Guy Your Own Question
Webb-Guy
Webb-Guy
Webb-Guy, HVAC Mechanic
Category: HVAC
Satisfied Customers: 2,329
2,329 Satisfied Customers
Experience: maitenance tech at casto

Webb-Guy is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,877 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
1 yr old furnace not working...1 quick flash followed by 3
1 yr old bryant furnace not working...1 quick flash followed by 3 long flashes … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I put New board on Bryant furnace code 25. Old board ok. I'm
I put New board on Bryant furnace code 25 JA: Did you check the furnace's filters? Customer: Old board ok JA: Do you plan on doing the work yourself? Customer: I'm hvac Tec JA: Anything else we should… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a 1990 bryant furnace - the pilot light is off - how
I have a 1990 bryant furnace - the pilot light is off - how do I turn it back on? … read more
Rick
Rick
Supervisor
22,424 satisfied customers
We have a Bryant Furnace/AC unit, Model FBANF042, and the
We have a Bryant Furnace/AC unit, Model FBANF042, and the electric heat has quit working. There is AC power to attic mounted unit. The T841A1001 thermostat lights are not lit. Moving thermostat lever … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a furnace model 350MAV. The main blower motor runs
I have a Bryant furnace model 350MAV. The main blower motor runs but the furnace does not get a call for heat, the igniter does not glow. The hot surface ignition pilot does not heat up. I cleaned the… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Have a furnace 90 plus run board thru test all okay.remove
Have a bryant furnace 90 plus run board thru test all okay.remove vent piping vacuum same lots of leaves now clear .Remove pressure switch piping all clear jumper main gas valve it opens .Install elec… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
310278-401 REV E furnace and it won't light. Where can I
310278-401 REV E furnace and it won't light. Where can I find trouble shooting guide? … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a furnace that powers up and runs the blower for 90
I have a Bryant furnace that powers up and runs the blower for 90 seconds then produced a rapidly flashing red LED light. What does it mean?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Having trouble with a furnace. Heat not coming on, showing a
Having trouble with a Bryant furnace. Heat not coming on, showing a trouble code. Inducer motor just replaced in February. Would like help troubleshooting. I do have a multi-meter… read more
Rick
Rick
Supervisor
22,424 satisfied customers
I changed the condensation pump on my gas furnace and now
I changed the condensation pump on my gas furnace and now the furnace won't start. The old pump was direct wired through the kill switch and the new one had a plug. The new one also had a yellow wire … read more
Rick
Rick
Supervisor
22,424 satisfied customers
I have a furnace 17 years old. renters say are experincing
I have a bryant furnace 17 years old. renters say are experincing maybe a co2 leak. any advice.… read more
Kenton Guidry
Kenton Guidry
HVAC Technician
Vocational, Technical or Trade Scho
963 satisfied customers
I have a Furnace, Model FV4BNB006. The air filter is 21x23".
I have a Bryant Furnace, Model FV4BNB006. The air filter is 21x23". I cannot locate a replacement filter. Suggestions?… read more
ComfortZone
ComfortZone
Associate Degree
515 satisfied customers
Ryant furnace led flashes 2 slow then 4 fast flashes
ryant furnace led flashes 2 slow then 4 fast flashes … read more
Charles Bodenheimer
Charles Bodenheimer
Owner
Associate Degree
78 satisfied customers
Second opinion] I have a furnace (3946AW036125) that was
Second opinion] I have a Bryant furnace (3946AW036125) that was converted from Nat gas to LP (both the gas valve and orifices on burners). We have about 10" WC of gas pressure feeding gas valve and ab… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
355 satisfied customers
My son's furnace keeps popping the flame rollout switch with
My son's Bryant furnace keeps popping the flame rollout switch with a code '13'. He doesn't notice the issue until it goes into a lockout with code '33' which I believe is why the t-stat is going off.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Bryant furnace about 15 years old. Light flashing 3 long 2
Bryant furnace about 15 years old. Light flashing 3 long 2 short. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Bryant Furnace Model 345MAV048100AFKA that runs
We have a Bryant Furnace Model 345MAV048100AFKA that runs all the time, heats up, but doesn't push heat through the plenum. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,877 satisfied customers
My Bryant Furnace frequently does not start heating when the
My Bryant Furnace frequently does not start heating when the temperature drops. I to the furnace and turn the electric switch off then back on and the furnace runs. This happens twice to four times a … read more
Kcrand36
Kcrand36
Technician/Owner
Vocational, Technical or Trade School
71 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x