Goodman two stage gas furnace, 3 years old, currently is…

Goodman two stage gas...

Goodman two stage gas furnace, 3 years old, currently is code in system status code says LO , its firing up but not staying on?

Contractor's Assistant: Did you double-check the thermostat? And what about the pilot light?

Pilot light is on, theremostat says 21inside, 24degrees, heat on hold, we shut the emerency shut off switch just in case,,, its Celsius

Contractor's Assistant: Do you plan on doing the work yourself?

If its a simple fix, possibly?

Contractor's Assistant: Anything else we should know to help you best?

Not really, just need heat, lucky snow is not here yet,,,

Show More
Show Less
Ask Your Own HVAC Question
Answered in 13 minutes by:
11/19/2017
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,709
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

Hello, one minute while I get some information together. Note it takes time to type so please be patient.

Ask Your Own HVAC Question

That means LOW stage heating, does the inducer motor come on and ignitor glow up then go out with no flame?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
it fires up , then shut off, has a flame

If it lights up then goes out right away then repeats this process you need to remove and clean the flame sensor rod off on the unit. The flame sensor rod is what detects the flame after lighting and tells the board to keep sending power to the gas valve to keep the flame going. Over time these get corroded and even go bad failing to send the correct Milliamp signal to the board. Normally a good cleaning with some sand paper will clean them right up and they will work fine again and in other instances they need to be replaced. The part is on the burner manifold and typically will only have 1 wire attached to it and will either be a straight metal rod with a porcelain base or a bent metal rod with a porcelain base. Get that out and clean it off then try it and see what happens. Here is an image of what you would be looking for to take out and clean off with sand paper.

CLICK HERE

All I ask is please select the 5 STAR rating at the top of your page before leaving otherwise I receive ZERO credit for assisting you. Thanks and you can come back anytime for free followup questions.

HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,709
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified
HVAC Guru and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 8 months ago
Well, I have to say it worked, wasnt easy getting the sensor off, but it seems fine now. thank you for your assistance, greatly appreciate it especially with the cold weather upon us. I am extremely satisfied.
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,709
18,709 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Goodman GMVC80805CN furnace. Just quit operating.
I have a Goodman GMVC80805CN furnace . Just quit operating. It starts than just shuts down. Can hear that small fan up top starts and runs....... circulating fan does not and shuts down. LO is status … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
hi. i have goodman heat pump two stage with furnace gms 80703ana
. i have goodman heat pump two stage with furnace gms 80703ana heat pump/gas .the problem is when turn on heat system kick on and gas blow only 5 second and cut off and circle 3 times then system lock… read more
type2technician
type2technician
253 satisfied customers
I have a goodman gas furnace model GD075-3 Rev s. Worked fine
I have a goodman gas furnace model GD075-3 Rev s. Worked fine last night but was cold this morning and could not get it to come on when changed temp on thermostat. I can turn the switch to fan on and … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
my furnace will not work. It has been installed only two years.
my furnace will not work. It has been installed only two years. How can I get it to start please? I have followed directions for restarting but it will not fire up. Please help… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Amana furnace has a 7 segment LED that is flashing HI 9.
My Amana furnace has a 7 segment LED that is flashing HI 9. My Aprilaire thermostat is reading LO in the space where the current temperature is normally displayed. What is the cause?… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Goodman furnace Model GMVC950704CXBA that seems to
I have a Goodman furnace Model GMVC950704CXBA that seems to be running on HI gas mode all the time even though the control board shows LO and the circulator fan runs at the low heat speed. The furnace… read more
A-1 Tech
A-1 Tech
Service Manager
Vocational, Technical or Trade Scho
361 satisfied customers
The furnace is a weather master 8000 pilot kicks on and off
The furnace is a weather master 8000 pilot kicks on and off every few minutes and temp on thermo drops down to minimum 68 degrees as if you set it there yourself but really it was set for a higher tem… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
goodman 70K 95% 2 stage furnace i installed was running perfect
goodman 70K 95% 2 stage furnace i installed was running perfect now will not fire... flashing no codes… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
What does fault code 14 mean for Carrier weathermaker Model
What does fault code 14 mean for Carrier weathermaker Model 58SXB? How do i fix it or get my furnace to work until the technician gets here tomorrow?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Hi, I have a newer Trane heater model XR90 natural gas furnace
Hi, I have a newer Trane heater model XR90 natural gas furnace at a new house i just bought and is has a very simple & basic Honeywell thermostat (non-programmable). I want to use a Honeywell TH8110U1… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a model 350AAV gas furnace (two actually). #1 is not
I have a model 350AAV gas furnace (two actually). #1 is not heating. Was working fine until a week or so ago. If I shut down the system (turn off 110V) and then turn it back on the LED diagnostic ligh… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
I have a status code of E1 - Low stage pressure switch stuck
I have a status code of "E1" - Low stage pressure switch stuck closed at start of heating cycle. Is there something I can do to unstick it? If I turn it off and on or drop the temp setting below the c… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Our Lennox G71 MPP series - 36B - 070 model # 5908M01913
Our Lennox G71 MPP series - 36B - 070 model # XXXXX The sight glass in the Blower access panel keeps flashing the following series of numbers H40A350. Please explain what this means.… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Have honeywell Thermostat T8131C1012..gas heating unit one
Have honeywell Thermostat T8131C1012..gas heating unit one year old..power was off for 2 days..power on now..error message on thermostat 6AE LO..fan will turn on but heat unit will not start… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello, Technicians I have a Payne 125,000 BTU Natural gas
Hello, Technicians I have a Payne 125,000 BTU Natural gas furnace model #394gaz048125. It's approximately 20 years old & was given a clean bill of health 3 months ago by a technician. Now it's NOT wan… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
MY GOODMAN FURNACE DOES NOT LIGHT FIRE IN FIREBOX. VENT BLOWER
MY GOODMAN FURNACE DOES NOT LIGHT FIRE IN FIREBOX. VENT BLOWER MOTOR WORKS, IGNITER GLOWS, BUT AFTER 30 SECONDS, SYSTEM SHUTS DOWN. STATUS LIGHT REMAINS STEADY, NO BLINKING.JUST NOT FIRING UP. CAN GAS… read more
KenCan
KenCan
Vocational, Technical or Trade Scho
111 satisfied customers
I have a 10 yr old Goodman Model GMP 075-3 REV B Furnace (heat
I have a 10 yr old Goodman Model GMP 075-3 REV B Furnace (heat Only). It has the following: 1. Ignites and runs for about 2 minutes then shuts down. 2. Will not re-lite unless power is shut off. 3. Ci… read more
HVAC DOCTOR
HVAC DOCTOR
President
Vocational, Technical or Trade Scho
74 satisfied customers
Hello. Our Amana air command 80 (model GUI-D upflow) is not
Hello. Our Amana Air Command 80 gas fired warm air furnace (model GUI-D upflow) is not working properly. I turned the gas off yesterday to install a new range in the kitchen. When, I try to restart th… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x