I have an TACO SR502 that controls 2 pumps one for zone1 for

Customer Question
Hello, I have an TACO SR502...
Hello,
I have an TACO SR502 that controls 2 pumps one for zone1 for Hot water loop and the other for zone2 for baseboard heat and I also have a new TACO ZVC406 that control one other pump that supply heated floor loops. They both work fine except that when the ZVC406 request heat the pump goes on but not the boiler.
Is there a wiring thing that needs to be done between the SR502 and the ZVC406 so the boiler will start when the ZVC406 requests it? Thanks for your help.
Submitted: 27 days ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 minutes by:
11/18/2017
HVAC Technician: Rick, HVAC Supervisor replied 27 days ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 22,609
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

You could connect the boiler end switch to the boiler control TT terminals (same termnals SR502 XX endswitch is connected to). I'm assuming they're using the pump end swtch terminals on the ZVC to control the pump.

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 27 days ago

Do you have more questions?

Ask Your Own HVAC Question
Customer reply replied 26 days ago
That does not answer my question. Or tell me how I connect the ZVC to the SR502.
HVAC Technician: Rick, HVAC Supervisor replied 26 days ago

I beg to differ. I did answer your question which was how to get the burner to fire up when the ZVC calls for heat. You can't connect the ZVC to your SR502 which already has both zones accounted for. If you want the DHW on priority then you need an SR503. Let me know if you don't know where to connect ZVC boiler end switc leads.

Ask Your Own HVAC Question
Customer reply replied 26 days ago
I need to know how to connect so that when the ZVC request heat the boiler turns on. I don't know what contact from the ZVC connects to the SR502 or the boiler to achieve that.
HVAC Technician: Rick, HVAC Supervisor replied 26 days ago

I told you what to connect in my last 2 answers. One more time: ZVC boiler end switch leads to boiler control thermostat terminals. Same place your SR502 end sitch terminals are connected. I'm offline for at least 3 hours, maybe the rest of the day. Back online ~9 am ET tomorrow

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 26 days ago

I gave you that info in my last 2 answers. One more time: ZVC boiler end switch terminals to boiler control thermostat terminals. Same place your SR502 end switch terminals are connected. I'm offline for at least 3 hours, maybe the rest of the day. Back online ~9 am ET tomorrow

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 22 days ago

Do you have more questions?

Ask Your Own HVAC Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,877
6,877 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,877 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Im working on a boiler right now and the boiler is running
Hi pearl im working on a boiler right now and the boiler is running but is not heating the downstairs not the upstairs. I can't figure out why. Yesterday I replaced the pressure relief valve and the e… read more
Rick
Rick
HVAC Supervisor
22,609 satisfied customers
I have a boiler that is having issues starting, It is a
okay I have a boiler that is having issues starting, It is a ingniter type of igntion … read more
Rick
Rick
HVAC Supervisor
22,609 satisfied customers
Alpine boiler making interment rumbling noise in exhaust
alpine boiler making interment rumbling noise in exhaust during post purge … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
I got a viessmann boiler. And when it ignites sometimes it
I got a viessmann boiler. And when it ignites sometimes it makes a loud noise. And it was a flash back from the fresh air vent to the burner … read more
Phil
Phil
Mechanical Engineer
6,877 satisfied customers
I have an enerjet boiler and recently the relay on the
I have an enerjet boiler and recently the relay on the Honeywell L8148E relay stuck and I had a run away boiler would not shut down. I tapped the relay and it disengaged and shut the boiler down. I in… read more
Rick
Rick
HVAC Supervisor
22,609 satisfied customers
Rick, The thermostat terminals on the ZVC404 Zone Valve
Hi Rick,The thermostat terminals on the ZVC404 Zone Valve Control are marked as 24 VAC. Does this mean that when the terminals on the thermostat are closed, the circuit is completed and energized with… read more
Rick
Rick
HVAC Supervisor
22,609 satisfied customers
My munchkin boiler has a POR fault but the pressure is
my munchkin boiler has a POR fault but the pressure is 18psi? … read more
Rick
Rick
HVAC Supervisor
22,609 satisfied customers
Have a well mclain boiler that tries to light and shuts
Have a well mclain boiler that tries to light and shuts itself off after pilot light comes on … read more
Rick
Rick
HVAC Supervisor
22,609 satisfied customers
My boiler stopped working. Since wendesday. If posible. The
my boiler stopped working JA: I'll do all I can to help. How long have you been dealing with this? Customer: since wendesday JA: Do you plan on doing the work yourself? Customer: yes if posible JA: An… read more
Rick
Rick
HVAC Supervisor
22,609 satisfied customers
I have a 1989 vintage Vaillant boiler that continues to
Hi, I have a 1989 vintage Vaillant boiler that continues to ignite and then shuts off. What would cause this problem? … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
Weill-McNeill EG gas boiler w/o tankless water heater.
Weill-McNeill EG gas boiler w/o tankless water heater. … read more
Rick
Rick
HVAC Supervisor
22,609 satisfied customers
I have a Hydrotherm Boiler that needs a pressure switch
Second opinion] I have a Hydrotherm Boiler that needs a pressure switch BM8026. Model of Boiler is HI-165B. Can you help me … read more
Elliott Oxton
Elliott Oxton
NVQ Level 2
4 satisfied customers
I have a Hydrotherm Boiler that needs a pressure switch
I have a Hydrotherm Boiler that needs a pressure switch BM8026. Model of Boiler is HI-165B. Can you help me … read more
Phil
Phil
Mechanical Engineer
6,877 satisfied customers
Burnham boiler will not start. It was way over filled. I
Burnham boiler will not start. It was way over filled. I have drained mostly clean water out. Site glass is two inches empty. Red light on black box comes on when I switch the unit on. Other units in … read more
Phil
Phil
Mechanical Engineer
6,877 satisfied customers
Boiler is calling for HW but nothing is on? Cadet heating
trying if its easy enough and not required plumbing work … read more
Rick
Rick
HVAC Supervisor
22,609 satisfied customers
I bought a used Weil Mclain PFG 5 boiler. It came with 5
I bought a used Weil Mclain PFG 5 boiler. It came with 5 zone valves. Information I can find says connect end switch wires to terminals TT on boiler. I cannot find TT terminals. … read more
Rick
Rick
HVAC Supervisor
22,609 satisfied customers
This is a boiler. The past 10 days. The Munchkin 80M boiler
the past 10 days. The Munchkin 80M boiler is a gas-fired boiler that was designed for residential homes. This boiler is rated at 92% efficiency and an Input Btu's of 27,000 to 80,000 Btu's. … read more
Rick
Rick
HVAC Supervisor
22,609 satisfied customers
Brought a boiler from nome heating. Bought a boiler from
bought a boiler from mike west nome heating for eght thousand dollars need to insurance for my boiler … read more
Rick
Rick
HVAC Supervisor
22,609 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x