I have been replacing 1361 2 wire zone valves at the rate of one per yeAR. iS THERE ANOTHER ZONE VALVE THAT WOULD BE MORE RELIABLE?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

ABOUT 3-5 YEARS.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I have 4 zones in my house and the two lower level zones work fine but the 2 upstairs which baiscally are the most lived in. Also I have 2 transformers for 4 thermostats . All thermostats are are programable except one. The basic system was created in 1970.

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

I don't think the thermostats are the problem as they did a good job when changing the different temp levels

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
11/18/2017
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,378
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

I'm not a fan of White Rodgers zone valves. Honeywell or Taco would be a better choice but you'd have to replace all the zone valves

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Is ther something aboutAre there something about the W_R valves that don't stand up?w-
HVAC Technician: Rick, HVAC Supervisor replied 7 months ago

It's the 3 wire config. Severly limits thermostat options.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I'm trying to figure out how to get my 2 Nest 3rd Gen
I'm trying to figure out how to get my 2 Nest 3rd Gen thermostats to control their respective White-Rogers 1311-102 zone valves in my boiler system. I already ran new wires from the valves to the ther… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
Attempting to replace my downstairs (main level) thermostat
Attempting to replace my downstairs (main level) thermostat with a Nest. I have wires on O&B but do not have a heat pump. Cannot find anywhere that this scenario would be possible. I do have a humidif… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Have new S90 slant fin boiler with a hydrostat 3200
Hello, Have new S90 slant fin boiler with a hydrostat 3200 controller,have 2 honeywell ct87a 3 wire stats and 2 whiterodger zone valves,one a 1361 the other a 1311. Looking for a wiring diagram.… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
Rick, I need to verify the wiring to a Rodgers zone valve
Rick, I need to verify the wiring to a White Rodgers zone valve used to heat DHW. Attached is the current wiring. Is this correct? The transformer seems to have been burned out and don't know if the w… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
, I have a Carrier 2 Comfort Zone 2 system installed
Hi, I have a Carrier 2 Comfort Zone 2 system installed with 2 zone thermostats at the house. Now the problem is second thermostat says C1 on the display and main thermostat cannot read the second zone… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am trying to install a Honeywell RTH8580WF thermostat, replacing
I am trying to install a Honeywell RTH8580WF thermostat, replacing an old T87 very basic 2 wire model. The system is hot water baseboards with an oil fired ESSEX boiler (also convertible to wood, but … read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
Hi Matthew, Our gas furnace is working properly downstairs,
Hi Matthew, Our gas furnace is working properly downstairs, but upstairs the temp won't get above 66 even if I push it up to 74 and turn it to "On". I just changed all of the filters. It's a 2 zone sy… read more
TheHouseDoctorJA
TheHouseDoctorJA
14 satisfied customers
I have White Rodgers 3-wire 1311 zone valve and have old White
I have White Rodgers 3-wire 1311 zone valve and have old White Rodgers 3 wire mercury thermostat. As recommended by local mechanical service and sales purchased a Honeywell Pro2000 TH2110D1009 program… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a bryant thermostat that is programable for 7 days and
I have a bryant thermostat that is programable for 7 days and 2 zones. I have had the thing replaced 3 times in 10 years. Even between replacements it will do things like blank out when you are touchi… read more
SWFLHVAC
SWFLHVAC
67 satisfied customers
Wire diagram White Rodgers Zone A Flow Water Valve 1361-103
Have a White Rodgers Zone A Flow Water Valve 1361-103. Wires accidentally pulled out! Need wiring diagram for this 30 year old valve. Need to connect: 1. 2Wire from 12 V transformers, 2 2Wire from aux… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
Hi there Ive just recently bought a new house/home. The
Hi there I've just recently bought a new house/home. The heating system is quite antiquated and needs upgraded. The boiler is ok, with separate output for CH and HW, but the controllers are analog (an… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
I have a heating issue. My house is a split level with 2 zones.
I have a heating issue. My house is a split level with 2 zones. Zone 1 is upstairs bedrooms mid level Kitchen and living room. Zone 2 is half of the mid level and the lower level family room. Zone 2 s… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
We live in Memphis, and puchased one of 12 homes that have
We live in Memphis, and puchased one of 12 homes that have hot water boilers. Our system has it's own mind. We have 2 thermostates. One for upstairs and one for down. We have to turn the upstairs ther… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Rick it has been some time but we are working at the hous ewith
Rick it has been some time but we are working at the hous ewith the peerless oil fired boiler again. The system is running but not correctly. I must have the zone valves wired wrong. The system has a … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
My thermosat goes to a box on the wall with several wires.
My thermosat goes to a box on the wall with several wires. I have a red/white wire coming from transformer going to zone valve 1361 white/rodgers. I have 1 red and 1 white coming from box on wall goin… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
We had a new Trane xli16 and new furnace I believe an XV80
We had a new Trane xli16 and new furnace I believe an XV80 installed. Getting a lot of condensation now in the vents in the lower level of our home. We bought a dehumidifier that holds 8 gallons and e… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a chronotherm III with troll-a temp that probably was
I have a chronotherm III with troll-a temp that probably was installed in 1986 when the house was built. There are 3 t-stats and 3 dampers. The problem is that the t-stats will not regulate the room t… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello. I live in a duplex condominium and as the days get
Hello. I live in a duplex condominium and as the days get colder we notice a greater temperature difference between the upper and lower level (today it was 62 deg. on the lower level and 87 deg. on th… read more
hvacmrfixit
hvacmrfixit
disabled
Vocational, Technical or Trade Scho
118 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x