I have a reznor f50 heater I am tying to get in use. I see…

I have a reznor...

I have a reznor f50 heater I am tying to get in use. I see two wires n do not know where they go. It seems they are on some ECO part

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

An hour got the unit free. Replaced the 24 volt transformer. Got spark for flame nothing else.

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

Thermostat works. No filters on unit.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes.

Contractor's Assistant: Anything else we should know to help you best?

Really wondering what purpose the two wires are for. Its a eco part aboout a inch long

Show More
Show Less
Ask Your Own HVAC Question
Answered in 23 minutes by:
11/18/2017
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,398
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

There are 2 terminals on the gas valve (not TH or TR). That's where you connect the ECO leads,

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Is it necessary to use the eco piece. There is nothing to wire to there.

It's possible the gas valve was replaced. The ECO is a redundant over temp safety. It's not critical to the function of the unit.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
The gas valve does not stay open. I hear it but it closes.

Then you have a different issue. Do you have a standing pilot or electronic ignition?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Electronic

How far into the igniton sequence does it get? Does the igniter arc? do the burners fire up then go out? do you have a multi meter?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
The igniter runs it's cycle. But valve doesn't open. I have a multi tester.

Ok, you need to check for 24 volts at the gas valve. My schematic shows 2 possible gas valves. So depending on which one you have you either probe P & C terminals or PV & PVMV. You should read 24 volts while the electrode is arcing

Ask Your Own HVAC Question
Customer reply replied 8 months ago
36 at pv mv

Ok, that's way too high (you are on an AC scale). 29 volts is max. Likely the transformer has failed and needs to be replaced. You may have fried the gas valve as well but I'd try a new transformer before replacing the gas valve.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
No brand new transformer puts out 27.8

then there's no way you have 36 volts at PV & MVPV. Just noticed you said pv & mv = wrong terminals

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Readings at pv pv mv and my are all the same just over 19.8

Ok, borderline too low which usually means a bad connection between the transformer and the valve

Ask Your Own HVAC Question

Do you have more questions?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Checked all connections has to be a bad board.

If you have 27.8 volts into the ignition control and only19 out then yes a new control would be the next step

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,398
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,398
24,398 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a 1994 Reznor F50-E. It wont start. Tested the Tstat
I have a 1994 Reznor F50-E. It wont start. Tested the Tstat and I believe it's ok. I don't believe I'm getting power at the ignition control. Though I can't tell if the reset button has been tripped. … read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
I have a reznor f50;hooked up propane and power.thermostat
I have a reznor f50;hooked up propane and power.thermostat on, nothing happens … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
We purchased two new Reznor gas shop heaters in 2015. One
hello my name is***** purchased two new Reznor gas shop heaters in 2015. One will not start. SER , BNH796EN13749X , MODEL UDAP200. IT IS GETTING GAS TO UNIT. … read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
I can't believe this, you're really there? One hour so far.
yes. I have a Honeywell Gas Valve for a Reznor 30,000 btu sealed combustion furnace. The Honeywell part # is VR8205K8905. … read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
Looking for a solution for heating my garage. Currently have
Hey - looking for a solution for heating my garage. Currently have a Reznor (model UDAP45). I have a cheap digital thermostat hooked up to it. Currently, I have to leave it on to about 7 degrees Celci… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
INSTALLED A NEW 1.25 INCH NATURAL GAS SUPPLY LINE TO HEATER
INSTALLED A NEW 1.25 INCH NATURAL GAS SUPPLY LINE TO HEATER LAARS LITE 2. BLED THE LINE BUT IT BURST INTO FLAMES. SHUT OFF THE GAS. NOW THE HEATER WON'T RESPOND TO THE SWITCH TO TURN IT ON. IT DOESN'T… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
I have a Reznor UDAP 125 unit heater running on propane
I have a Reznor UDAP 125 unit heater running on propane heating my garage. Recently the heater has begun shutting off before it reaches the thermostat's set temperature. The green light flashes contin… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
, I have a Reznor gas heater in my shop. It keeps lighting
Hello, I have a Reznor gas heater in my shop. It keeps lighting the burners (yellow flame) for 5-8 seconds, then shutting off. The blower fan is running, and the pilot is lighting correctly. We've blo… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a reznor hanging heater that flashes 2 (failure to sense
I have a reznor hanging heater that flashes 2 (failure to sense flame) vent motor runs but i only heard it try to ignight once. After that it sounds like the gas valve is opening but doesnt even try t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hey Paul. I have another unit strangely enough nearly identical
Hey Paul. I have another unit strangely enough nearly identical to the Rheem we chatted about this morning.Saturday.With the same problem. Wont spark to light burner. I get 3 blinks on the board. Can … read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
I have Reznor model F50-E-3 in my garage. When I turned it
I have Reznor model F50-E-3 in my garage. When I turned it on nothing happened. Before when I turned it on it made a click and the burner would come on. I tried bypassing the thermostat still nothing.… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
looking for service manual for coleman furnace 8645d766. System
looking for service manual for coleman furnace 8645d766. System will not respond to thermostat. Attempted to check voltage at transformer and got no reading. Is it safe to provide 15 to 24 volts sc to… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Our air conditioner as well as heater will not come on. I have
Our air conditioner as well as heater will not come on. I have checked the disconnect outside, the breakers and still nothing. I had someone helping me earlier but he opted out. Can anyone else help?… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hi. I have an elderly Empire H3-10210. The pilot stays lit,
Hi. I have an elderly Empire H3-10210. The pilot stays lit, but the main burner does not ignite. Thermostat is calling for heat. Any ideas?… read more
mranswer
mranswer
TECHNICIAN
Bachelor's Degree
481 satisfied customers
hi i have a f50 heater and the unit blew the eco out and the
hi i have a f50 heater and the unit blew the eco out and the man replaced and two days later its out again if i jumper wire it it works good heat comes on and goes off at the temp set on thermostat co… read more
Rick
Rick
HVAC Supervisor
24,398 satisfied customers
I have an old trailor house, with a White-Rogers 2 wire thermostat,
I have an old trailor house, with a White-Rogers 2 wire thermostat, for a forced air electric heater. Can I use a RTH2310B, and where do I hook up the two wires that come from the furnace? The old uni… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hello, i have a problem with with Hvac, it stop working yesterday...
Hello, i have a problem with with Hvac, it stop working yesterday... looks like thersomstat does not send signal to start neither heating or cooling can you guide me throught trouble shooting on my un… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I have a Reznor F75-E gas heater that has quit working. It
I have a Reznor F75-E gas heater that has quit working. It will light the ignitor and then a small blue pilot lite will ignite, but the unit will not fire up the large burners. I have removed the flam… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x