I have a York central heat unit. The problem is it wants to…

Customer Question
I have a York...

I have a York central heat unit. The problem is it wants to turn on to give heat but shuts off after about 2 seconds and keeps on doing the same thing. Had this problem 3 weeks ago. Unplugged limit switche and it worked just fine but no heat. Replaced limit switch worked just fine. Same problem now figured I bought a faulty switch. Got new switch put it in didn't fix prob like last time

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Settings on heat and new filter with first new switch it's still clean.

Contractor's Assistant: Do you plan on doing the work yourself?

Hopefully It does give me a code same code as last time

Contractor's Assistant: Anything else we should know to help you best?

The code it gives me says control failure

Submitted: 7 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 minutes by:
11/18/2017
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 921
Experience: Owner at Gaztech
Verified

Hi I am Gaztech1, a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE after we are done. this will credit me for assisting you.

This sounds more like a dirty flame sensor, located to be positioned in front of burner, with purple wire pluged to it. take it out and sand the metal end clean. then retry.

http://s3.supplyhouse.com/images/products/zoom/9006106205-3.jpg

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Ok. Took it out sanded it to shiny metal out back in and didn't fix problem
Customer reply replied 7 months ago
Like I said I did that and it still has the same problem
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago

OK

Do you get burners to light for those 2 seconds?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
If it sits left alone for a while and i turn it on the burner turns on I see it glow red It will try for about 5-7 seconds to actually ignite than shuts off. From there on out no red glow and it only has a 1-2 second attempt. This is the same problem in every way I had 3 weeks ago. Replaced limit switch cleared code and it's been running jus fine since Than. Until today. I even replaced limit switch because I thought the limit switch I bought three weeks ago just was a faulty one
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago

And what error code are you getting this time?

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Control failure
HVAC Technician: Gaztech, HVAC Technician replied 7 months ago

Opting out, have to let another tech assist you

Ask Your Own HVAC Question
Customer reply replied 7 months ago
Opting out ?? So I have to go thru all this all over again with another tech ?????
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 921
921 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
What does it cost for the correct answer? How much is the
York Gy9s0b12up11jL "Limit switch open - blower failure" error code. Unit runs but on cold days if running too long flame shuts down. It will restart immediately with a power reset. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
York Furnace GY9S was dormant two years. Saw that the gh
Customer: York Furnace GY9S was dormant for about two years. Saw that the high limit switch was missing, so I bought a replacement and hooked up the two wires. Replacement part 140 open, 110 close sam… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have problems w/ a Coleman DGAA 70 gas furnace. Runs fine
I have problems w/ a Coleman DGAA 70 gas furnace. Runs fine for about 3~4 cycles then I get a green flashing light. Reset switch and runs fine for another 3~4 cycles. Help… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Trane Gas Furnace that stopped working. The problem
I have a Trane Gas Furnace that stopped working. The problem is it won't light. The code on the control board indicates its the high limit sensor, but have checked it and it's good. The igniter is goo… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
Hi I have a Coleman evcon furnace in a mobile home I bought
Hi I have a Coleman evcon furnace in a mobile home I bought and it has an intermittent problem that I have to reset the furnace and then usually works fine. Doesn't even happen daily but it flashes th… read more
type2technician
type2technician
253 satisfied customers
Hello, I have a York 90 Diamond P3UR with an intermittent
Hello, I have a York 90 Diamond P3UR with an intermittent problem. Sometimes after a heating cycle the blower will run continuously, blowing cold air, until I shut down the unit locally (turning the t… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
Hello Charles. RPJ II Furnace Flame Cycles on/off about every
Hello Charles. RPJ II Furnace Flame Cycles on/off about every 2 minues while blower remains on. Hunter digital thermostat reads HEAT during this time. Is something overheating or a temperature sensor … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My York diamond 80 is blowing cold air onlyFan comes on fine.
My York diamond 80 is blowing cold air only Fan comes on fine. Furnace burners are not coming on. Filter is new ( replaced a week ago) See red light blinking code 4 in small view window… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Replaced inducer on york gy9s080b12up11j furnace and now cant
Replaced inducer on york gy9s080b12up11j furnace and now cant get room temp back to normal. Keep getting 4 flash limit open and furnace shuts down. Why would these be related and why does it lock out?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a RiteTemp 8050 hooked to my gas furnace. It was working
I have a RiteTemp 8050 hooked to my gas furnace. It was working fine up until three days ago, but over the last couple of days it is no longer keeping the temperature constant in the house. The temper… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a Weathermaker 9200. It has been working just fine
I have a Weathermaker 9200. It has been working just fine until sometime last night. Heat does not come one. It is flashing a code 23. When I cycle power on the unit, the blower starts for approx 60-9… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
We have a york furnace and it blinking 4 times code says its
We have a york furnace and it blinking 4 times code says its an open high limit. what does this mean and can i fix it myself?… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Hey guys. Having problems with my furnace. Last december,
Hey guys. Having problems with my furnace. Last december, the blower motor went out. Had it replaced and everything was good. Last month, it started to act up again. Sometimes it would work fine, othe… read more
GreenHeating
GreenHeating
Owner / Installer
Boiler / Steam Engineering
59 satisfied customers
Carrier 58sta/stx 6 years old. found code 33. starts up fine.
Carrier 58sta/stx 6 years old. found code 33. starts up fine. inducer and flame kick off and blow runs for 2-3 minutes and then it starts rigth back up. had stupid tech come out and he cleaned the fla… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a York Affinity 9.S SERIES furnace model number G1UA048S21G.
I have a York Affinity 9.S SERIES furnace model number G1UA048S21G. The furnace is 4 years old and is still covered by a 5 year parts warranty. This system provides heat and cooling to 3 zones. Over t… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Wve got an 80% gas furncae and have been having some issues
W've got an 80% gas furncae and have been having some issues: About six mos. ago control board diagnostics flashed a "high limit open" code. I replaced the unit and it worked fine until about two week… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
hello; my question involves the central heating in my home.
hello; my question involves the central heating in my home. as far as i can tell it functioned well over night. this a.m. i kicked the temp up several degrees as i usually do after i get up. now the u… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
getting a error 6 code.....on my Coleman house furnance installed
getting a error 6 code.....on my Coleman house furnance installed in 2002 no problems till now....starts up fine after 10 to 30 minutes gas burner shut off and blower keeps on working… read more
Jason Martin
Jason Martin
Maintenance Supervisor
Vocational, Technical or Trade Scho
88 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x