The 3 amp fuse blew up when calling for heat When disconnect…

Customer Question
Hello The 3 amp fuse blew...
Hello
The 3 amp fuse blew up when calling for heat
When disconnect the pressure valve tube the flue fan works but when connecting the limit sensors the fuse blew even when disconnecting the gas valve output
When calling for heat the fan comes on after few minutes and the flue fan run but once connecting the limit switches wire the fuse blew
Even when i bypass the limit sinsors and connect the in and out wires for limi sensor and disconnect the gas valve wire the fuse blow out
Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 minutes by:
11/17/2017
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 922
Experience: Owner at Gaztech
Verified

Hi I amCustomer a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE after we are done. this will credit me for assisting you.

Is the fuse burning ever since you replaced the new board, is it possible your wiring is wrong?

It is clear that you have a short with the limit sensor circuit, inspect all wiring and sensors,

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Thank you
It keeps blowing
I bypassed all sensors and connect the in and out of The limit switch and is still burning the fuse
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

Is the fuse burning ever since you replaced the new board, is it possible your wiring is wrong?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
This is the board and the low voltage socket has 5 wires in and out to pressure switch and in and out to all limit switches and out for valve
If I break the limit switches crircuit the fuse stays and even whe I disconnect the gas valve wire and connect the in and out for limt switches directly and bypassing all switches the fuse blew .
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

Again!!!

Is the fuse burning ever since you replaced the new board, is it possible your wiring is wrong?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
keep blowing
Are you talking about the low voltage
The low voltage has only 5 wires coming in and out of the socket and I did not change the socket or the wires so the go to the correct locations and also what will make the fuse blow once i bypass the limit switchs with a clean wire to make sure it is not touching a ground
Do you think any of the high voltage might be a reason
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

I am thinking that you got a defective board with internal short.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
That is what I thought and i changed it twice
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

.

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

OK, Then a close inspection of all wiring (burnt wire touching to ground)

Follow wiring diagram to all components for possible error.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Is this for the low-voltage or for the high-voltage or for both because in the low-voltage iPod I passed all the hits limit switches so I have a very clean wire connecting directly and also for the power out for the van I disconnect it so it is a small wire and I was trying to measure if I am getting power from it out the problem is once i Connect the in and outs for the limit to switch the fuse blow up
Customer reply replied 8 months ago
Is there any low voltage out of the board other than to the gas valve
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

Yes,

  1. Limit switchs
  2. pressure switch
  3. thermostat
  4. outdoor AC contactor relay
Ask Your Own HVAC Question
Customer reply replied 8 months ago
The cooling works fine
The pressure switch works fine and send signal but once the limit switches cuirct closes the fuse go out even when the wire to the valve was disconnected
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago
OK, Then a close inspection of all wiring (burnt wire touching to ground)Follow wiring diagram to all components for possible error.
Ask Your Own HVAC Question
Customer reply replied 8 months ago
There is no too many low voltage wires to inspect because the pressure switch works fine the limit wires are eliminated and i bypass all of the with a short wire and I disconnect the gas valve wire right after the control board
Does high voltage has anything to do with this
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago
No.
Ask Your Own HVAC Question
Customer reply replied 8 months ago
When bypassing all limit switches by connecting the in and out wire will this creatute the short cuircit or these are just switches with no resistance
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

They are just on off switchs, no load, but may have resistance if contacts are dirty.

Load components are gas valve, and relays

Just by chance, try disconnecting control wires that go to AC or heatpump if you have that.

Y , C, O, R terminal on control board of furnace.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
The ac low voltage go directly from the thermostat to the AC unit
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

AC, OK forget that.

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

I think that you did not find a shorted wire or component, using a ohm meter should help you find it if you are familiar with diagnostic proceedures.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
What should i check with the ohm meter
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

All wiring and components, if you are familiar with diagnostic proceedures. I am sure you can find many videos on youtube to teach you how.

Ask Your Own HVAC Question
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

I noticed question is still open, rate the 5 star rating AT THE TOP OF PAGE if we are done. this will credit me for assisting you.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Do you mean low voltage wires
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

Yes

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Gaztech Your Own Question
Gaztech
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 922
922 Satisfied Customers
Experience: Owner at Gaztech

Gaztech is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have been having issues with my cheap Gibson Furnace which
Matthew: I have been having issues with my cheap Gibson Furnace which lays in the crawl space. About 3 weeks ago the limit switch in the heat chamber, stuck open, and the blower kept running. I tapped… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
768 satisfied customers
My carrier furnace is not blowing heat. We get error code
My carrier furnace is not blowing heat. We get error code 33 … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My burners won't turn on. I replaced gas valve and furnace
My burners won't turn on. I replaced gas valve and furnace control board. It worked for 3 days and now goes into lock out after 3 tries.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a Lennox furnace in my shop that blows the three amp
I have a Lennox furnace in my shop that blows the three amp fuse. It's a LF24-150A-2 Serial number 6396J05175. I have replaced many parts but when I put power to it blows the three amp fuse … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
RUUD Gas Furnace Model# UGVC-07EAAER, shorts out transformer
RUUD Gas Furnace Model# ***** shorts out transformer in Cool mode, runs fine in Heat mode.I disconnected the (2) Tstat wires that go to the outside unit, set Tstat for cool, it blew the 5 amp inline f… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I am having problems with a TempStar furnace. It has a Honeywell
I am having problems with a TempStar furnace. It has a Honeywell smartvalve and a ST9120 fan control board. The pressure switch seems to be working fine, the limit and rollout switches are closed. Bot… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
So I changed the fuse and got my furnace going, or at least
So I changed the fuse and got my furnace going, or at least power to it again. Back to my original problem. Igniter not working. Code blinking prove switch problem. Cleaned out flue, cleaned tube from… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Reznor UDAP. 3amp control board fuse blows after a day or two.
Reznor UDAP45. 3amp control board fuse blows after a day or two. What can I check since it does not blow right away… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have a carrier model 58PAV135-20 furnace. It wont start
I have a carrier model 58PAV135-20 furnace. It won't start and the LED appears to be flashing a code (2 short flashes followed by 4 long flashes). Is there a place online that describes these codes?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i have a amana air command 80 sse, blows cold air, cleaned
i have a amana air command 80 sse, blows cold air, cleaned flame sensor, nothing? thanks Jim… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
we have a 25 year old furnace upflow DAYA F042no7oc we have
we have a 25 year old furnace upflow DAYA F042no7oc we have spark ignition but no pilot light , replaced the gas valve , changed , the 3 wire pilot assembly, blew throught the pilot tube, checked volt… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Have a Coleman Model 8975a676 Heater in a mobile with AC added.
Have a Coleman Model 8975a676 Heater in a mobile with AC added. This is an up flow unit. When the TS calls for heat, the flue booster fan comes on, the ignition system energizes the 120VAC silicon car… read more
Jason  Hvac
Jason Hvac
Hvac Tec
Vocational, Technical or Trade Scho
120 satisfied customers
Rheem furnace. blower motor runs continuously. thermostat
Rheem furnace. blower motor runs continuously. thermostat set to auto. green LED flashing on control panel. 2 flashes pause, 2 flashes pause etc. furnace electronic ignitor will not come on therefore … read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
We have a Carrier 9200 Weathermaker Gas Furnance. It is not
We have a Carrier 9200 Weathermaker Gas Furnance. It is not providing heat. We have turned off the breaker, turned off the switch on the furnance, and turned off the gas switch and back on. That's wor… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
my Bryant heater is not working - the led code is #21 - what
my Bryant heater is not working - the led code is #21 - what is involved and what is the cost to fix that problem?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello, Over the past week my furnace has been blowing the 3A
Hello, Over the past week my furnace has been blowing the 3A fuse on the circuit board. The furnace will run and cycle properly for approximately 6-8 hours before it blows the fuse. I then have to wai… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i have a gms81155cna heating unit. it keeps blowing the 3 amp
i have a gms81155cna heating unit. it keeps blowing the 3 amp fuse. when replaced it runs but reoccurs allmost immed. i dont get any diognostic flashing what could be causing it.… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,038 satisfied customers
Trane furnace ignites but won't stay lit. Get error code 3
My Trane XL 80 ignites but won't stay lit. After the flame goes out the indicator lamp flashes 3 times indicating a pressure switch failure according to the diags listed on the control. Where is the p… read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x