Customer Question
My American standard freedom 80...
My American standard freedom 80 two stage furnace is very sporadic. I have changed ignitor, flame sensor, and filter. 50 percent of the time it will not reach set temperature and short cycles giving an error code 2 flashes-external lockout. Is there anything else I can check for this issue?
Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 20 minutes by:
11/17/2017
HVAC Technician: Gaztech, HVAC Technician replied 10 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 939
Experience: Owner at Gaztech
Verified

Hi I amCustomer a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE after we are done. this will credit me for assisting you.

Your furnace has a slot on each side of the each burner that allows the flame to spread to the burner on either side of it. Most likely they are clogged and some burners not lighting up to satisfy flame sensor.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
The flame will ignite and all burners will ignite 50 percent of the time however it will cut out the natural gas after 5 to 10 minutes before reaching set temp. I can hear the gas valve click off when this happens
HVAC Technician: Gaztech, HVAC Technician replied 10 months ago

Is it possible that burners dont all light up 100% of the time, have you taken them out to clean the bridges between burners, they have a rusting issue

Ask Your Own HVAC Question
Customer reply replied 10 months ago
All burners light when the ignition burner lights. I have cleaned all burner compartment and orifices . Just will randomly shut down gas before cycle completes. Flame roll outs are also functioning properly
HVAC Technician: Gaztech, HVAC Technician replied 10 months ago

Possible temperature high limit situation, due to improper air flow

  1. instal new filter
  2. inspect underside of A/C coil for restriction
  3. all air vents are opened and unostructed.
Ask Your Own HVAC Question
Customer reply replied 10 months ago
Wouldn’t the sensor board bring a code of high limit of that were the gas? And not external lock out?
Customer reply replied 10 months ago
Sorry if that were the case wouldn’t it show high limit instead of external lockout(retries exceeded)
HVAC Technician: Gaztech, HVAC Technician replied 10 months ago

external lock out is due to furnace trying to cycle but locks out after multiple tries

Ask Your Own HVAC Question
Customer reply replied 10 months ago
I see the board with a call for heat, heat exchanger kicks on, igniter lights, I hear gas valve click to open and 50 percent of the time it does not fire at all and 50 percent of the time it short cycles
Customer reply replied 10 months ago
then it will retry 2 times before lock out. Sometimes it retries with success but not often
HVAC Technician: Gaztech, HVAC Technician replied 10 months ago

Mesure voltage at gas valve, 24V should be steady while thermostat is calling for heat,

it may be a defective gas valve.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Well obviously it has 24v until it doesn’t and it shuts off what would tell the gas valve to shut off prematurely with a new flame sensor installed and no code for high limit
HVAC Technician: Gaztech, HVAC Technician replied 10 months ago

Have you checked the inducer motor vacume line, it may be restricted

Each end of the tubing fits on to a nipple on each component. Remove the tubing and inspect for blockage. Also look directly into the nipple on the inducer motor. It should be clear, but I have repeatedly seen some sort of substance blocking the nipple. I use a shopvac and a thin wire probe to draw the material out of the inducer motor.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
How to I clear an external lockout in my furnace? It is
No. I get a flashing light that is the external lockout… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an American Standard Freedom 80 gas furnace. The
Hello, I have an American Standard Freedom 80 gas furnace. The flame sensor appears to be off – I replaced it last year. Now, the unit runs normally (both in heating mode and waiting mode), however, t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a American Standard Freedom 80 furnace that is
I have a American Standard Freedom 80 furnace that is working intermittently. It uses an Emerson / /White - Rodgers 50A50 - 473 control module. Sometime the furnace will run normally for 15 minutes or… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Is a jumper needed on the board, in order for the Am
is a jumper needed on the board, in order for the Am Standard freedom 80 to work correctly? … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
there. I have an American Standard Freedom 80 Single Stage
there. I have an American Standard Freedom 80 Single Stage that has been lighting intermittently. I cleaned the burners and it worked well two weeks. When this happens it won't light at all and goes t… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Have a american standard freedom 80 gas furnace. comes on flames
Have a american standard freedom 80 gas furnace. comes on flames for 10 seconds then flames go out. furnace blows cold air. error code 2 flashes: system lockout check line polarity… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
792 satisfied customers
I have an American Standard Dual Stage Freedom 90 (AUX080R942W1).
I have an American Standard Dual Stage Freedom 90 (AUX080R942W1). Last season the furnace would not come on, no fan/heat/sounds. The indicator would flash three times, inducer fault. Power cycling wou… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My American standard freedom 80 two stage furnace has a red light that
My American standard freedom 80 two stage furnace has a red light that I'd blinking 3 times what do I do about a pressure switch error… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi We have an American Standard Freedom 80 2-stage furnace
Hi We have an American Standard Freedom 80 2-stage furnace Model# XXXXX Over the past 2 weeks, the furnace keeps cutting out. It will fire up but no forced air. The fan is running but nothing is comin… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Have a American Standard Freedom 80 2 stage furnace-5 years
Have a American Standard Freedom 80 2 stage furnace-5 years old. The furnace will ignite and get up to temperature, then shut off. However, after awhile the furnace starts to make loud clicking sounds… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I have an american standard freedom 80 2-stage gas furnace.
I have an american standard freedom 80 2-stage gas furnace. The unit tries to light but as soon as burners ignite the unit shuts down. trouble inicator blinks twice. what is the problem?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have an American Standard model Freedom 80 furnace. It is
I have an American Standard model Freedom 80 furnace. It is connected to a White Rogers programmable thermostat. If I turn on the heater switch, put the themostat in heat position and get the set poin… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
After night time setback, my furnace goes on and runs for a
After night time setback, my furnace goes on and runs for a short time and then goes out. The code light flashes red 9 times continuosly for about 15 minutes and then the furnace ignites and runs for … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a freedom 90 American Standard 2 stage propane gas furnace.
I have a freedom 90 American Standard 2 stage propane gas furnace. The furnace will fire up and suddenly flame out and of course I get the trouble red light flash 2 times stating it shutdown. I change… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Freedom 90 American Standard propane gas furnace.
I have a Freedom 90 American Standard propane gas furnace. Lately, it fires up and then within seconds it will shut down after igniting. It will retry and sometimes ignite and run and other times it w… read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
American Standard Furnace error codes 2 flashes. Blowing cold air.
We have an American Standard Furnace that has had problems since installation approx. 6 years ago. The furnace will ignite (sometimes) and heat will be distributed -- then switch to cold air and cycle… read more
G Wurtz
G Wurtz
Instructor of HVACR Program
Master's Degree
57 satisfied customers
I have an American Standard Freedom 80 furnace which I have
I have an American Standard Freedom 80 furnace which I have to replace the ignitor for frequently. The filter is new, the flame sensor has been replaced and it seems to go into external lockout often.… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I need to go to my furnace twice a day and spin the fan by
I need to go to my furnace twice a day and spin the fan by hand to get it to start up. There is a diagnostic light on the white rogers control flashing four times. The code chart indicates "thermal pr… read more
Mario
Mario
Owner Of At Your Service Plumbing & Heat
High School or GED
672 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x