We have a Carrier Model 40FQ916090 & 40FS160300 heater 7 A/C…

Customer Question
We have a Carrier...

We have a Carrier Model 40FQ916090 & 40FS160300 heater 7 A/C unit. The heater is blowing cold air only, regardless of the temp setting. Do you have any ideas? It's 1:00 a.m. and the house is cold.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes. Thermostst settings are on 72, (were 75). I just checked & cleaned the filters. They were dirty & clogged.

Contractor's Assistant: Do you plan on doing the work yourself?

If there is a quick fix or troubleshoot that I can do right now, otherwise I will have to call a tech in the morning.

Contractor's Assistant: Anything else we should know to help you best?

I don't think so.

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 8 months ago
Output temperature is staying at a constant 67 degrees. Thermostat setting was at 75, but is currently at 72.
Answered in 4 hours by:
11/17/2017
HVAC Technician: airheatman, HVAC Technician replied 8 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,181
Experience: Furnace, A/C and heat pump specialist.
Verified

If furnace is not coming on or does not stay on , there should be an error light flashing on the control board in blower compartment to indicate what has failed. If you can locate this and tell me the pattern of the flash, that will point us in the right direction for troubleshooting.

Also let me know if you have a multi meter for troubleshooting.WE will go from here

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have a honewell model TH8320R1003, woke up house showed 67
Have a honewell model TH8320R1003, woke up house showed 67 and was set on 72, only working on emergency heat … read more
Chris Wagner
Chris Wagner
None
27 satisfied customers
We have a Comfortmaker furnace Model G9MXE0801716A installed
We have a Comfortmaker furnace Model G9MXE0801716A installed new in May 2015. The furnace keeps shutting off intermittently (mostly during the night when the temperature drops) with Error codes 4 and … read more
airheatman
airheatman
HVAC Technician
9,181 satisfied customers
I have a 2009 Luxaire Acclimate Modulating gas furnace...it
I have a 2009 Luxaire Acclimate Modulating gas furnace...it is turning on at correct programmed time, but not to desired temperature. Thermostat has been replaced. It is supposed to come on at 6am and… read more
airheatman
airheatman
HVAC Technician
9,181 satisfied customers
My air-conditioner is a 2 year old Carrier. We live in a new
My air-conditioner is a 2 year old Carrier. We live in a new house, the A/C seems to run practically of the time, even when the setting is set 75 Degrees and the current temp is 71 degrees and the hum… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
Trane xl624 in hold mode...set point 72....room temp 70.....takes
Trane xl624 in hold mode...set point 72....room temp 70.....takes forever to turn on furnace???… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
all readings on my a/c look like system is running properly.
all readings on my a/c look like system is running properly. but i can't get more than 13/14 degree difference from supply and return. Lately my a/c seems to work really well when its only mid 80 or s… read more
Expert
Expert
Have a Lennox C33-38A-2F-2 A/C unit. Compressor was running
Have a Lennox C33-38A-2F-2 A/C unit. Compressor was running and so was fan but only blowing hot Air. Set @77 indoor temp was 83. I looked at the attic unit and noticed a build up of Ice around the com… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Our heating system doesnt seem to be working properly. The
Our heating system doesn't seem to be working properly. The furnace ins a Bryant 355 MAV, installed 6 years ago. I replaced the thermostat 2 months ago. Occasionally (about once/week), the temp in the… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
Our GMS9/GCS9 is blowing out cold air. The thermostat is set
Our GMS9/GCS9 is blowing out cold air. The thermostat is set to 72 and the temperature is currently 63 and dropping. the unit is blowing air, its just not warm air. It has worked fine this winter up u… read more
theplumber717
theplumber717
Plumber
Vocational, Technical or Trade Scho
791 satisfied customers
The inside fan is running, the outside fan is running, the
The inside fan is running, the outside fan is running, the pipes are room temperature. The outside unit seems to be quieter than it had been previously and I notice the lights dim when the A/C is enga… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I have a Carrier Air conditioner and it has stopped cooling
I have a Carrier Air conditioner and it has stopped cooling as much as normal. The fan is still running and it's still cooler than outside but I've got it set at 70 and it's 80 inside. It is 11 years … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I AM LOOKING FOR A PROGRAMABLE THERMOSTAT THAT HAS 5 OR 6 HEATING
I AM LOOKING FOR A PROGRAMABLE THERMOSTAT THAT HAS 5 OR 6 HEATING STAGES. CAN YOU HELP? THIS THERMOSTAT WILL BE USED BY A CHURCH WHICH NEEDS TO HAVE SEVERAL HEATING STAGES. THE CHURCH IS HEATED BY HIG… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a 10 year 3.5 ton Rhreem A/C system on a 1,600sqft dwelling,
I have a 10 year 3.5 ton Rhreem A/C system on a 1,600sqft dwelling, with a 5 year compressor. A few days ago it stated during the day not to cool bellow 81 degrees and you can feel the heat inside the… read more
Paul
Paul
Vocational, Technical or Trade Scho
108 satisfied customers
Re Model 58PHA/PHX System off during the night. Turned
Re: Model 58PHA/PHX System off during the night. Turned on at 6:00 am, thermostat set to 68 degrees. It takes 4 hours to reach 68 from an original house temp of 60 degrees. Is it normal for the system… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have my thermostat set for 65 beginning at 11 00 p.m. and
I have my thermostat set for 65 beginning at 11:00 p.m. and 72 at 7:20 a.m. Lately it has not always come on when it is supposed to in the morning and I have to push it off and on frequently until it … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
we have 2 Carrier, 6 year old, 3 ton units which are currently
we have 2 Carrier, 6 year old, 3 ton units which are currently not cooling. A local Carrier company suggests that the internal components of the line dryer have broken down and are probably clogging t… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
My company have Carrier A/C units and the Programmable thermostat
My company have Carrier A/C units and the Programmable thermostat P/N CS450-01. Our building is occupied from 7:30 a.m. until 5:45 p.m. only. Occasionally some may work on week-ends for a couple of ho… read more
drcool299
drcool299
shop owner
Bachelor\u0027s Degree
22 satisfied customers
What is the best thermostat setting for a house,and should
What is the best thermostat setting for a house,and should i leave it on one setting around the clock, or program it to go down when we leave for work and school, and at night, and back up when we awa… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x