HI, having a problem...

HI, having a problem with our fireplace... looking for some assistance in troubleshooting

Contractor's Assistant: Just to clarify, what type of fireplace is this?

Heatilator CNXT4236ILT

Contractor's Assistant: Do you plan on doing the work yourself?

I'm trying

Contractor's Assistant: Anything else we should know to help you best?

Not that I can think of

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 8 months ago
It worked fine last year. When I turn the power on this year, the pilot doesn't light. I read the troubleshooting in the manual and tested the module for spark. It did not spark, so we ordered a new module. Replaced it and still no pilot or spark from the module.
Answered in 20 hours by:
11/17/2017
HVAC Technician: Iohn Keffer, HVAC Technician replied 8 months ago
Iohn Keffer
Iohn Keffer, HVAC Technician
Category: HVAC
Satisfied Customers: 73
Experience: Maintinances HVAC at Hainesville baptist church
Verified

This answer is based on the information you have given.If you have any additional information you would like to add, you can use the reply box below for additional questions, comments, or would like to upload helpful photos.

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue.

I see were there is a DC. Battery power supply voltage must be at least 4 volts. If below 4 volts,

replace batteries The batters are int the pilot circuit.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE after we are done. this will credit my account for assisting you. thanks

Ask Your Own HVAC Question
Customer reply replied 8 months ago
From what I am reading the batteries are only required for a power outage? Also, there were no batteries in it last year when it worked fine.
HVAC Technician: Iohn Keffer, HVAC Technician replied 8 months ago
my computer went down yesterday and I can't get this phone to work I would like for you to request another expert to help you under the circumstances thank you
Ask Your Own HVAC Question
HVAC Technician: Jerry, Service Technician replied 8 months ago
Jerry
Jerry, Service Technician
Category: HVAC
Satisfied Customers: 3,367
Experience: HVAC Technician. Hearth Products Specialty
Verified

Welcome to Just Answer!n Sorry I have not been logged on for a while and I saw this question was still open. There are a couple things I would look at. 1. Make sure you have power coming into the module, from the transformer plug in. You should have about 3-4 volts. 2. make sure the ground wire is secure, I have replaced several parts on these only to find the ground had over heated and broke off from the fireplace. Let me know if you need further help.

Thanks for using Just Answer.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Jerry Your Own Question
Jerry
Jerry
Jerry, Service Technician
Category: HVAC
Satisfied Customers: 3,367
3,367 Satisfied Customers
Experience: HVAC Technician. Hearth Products Specialty

Jerry is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a heatilator model CG300 that i think has a bad
I have a heatilator model CG300 that i think has a bad control module. It will not produce a spark. Spark ignitor replaced and transformer working properly … read more
Stan's Repair Service
Stan's Repair Service
repair tech.
High School or GED
2 satisfied customers
I have an outdoor fireplace that has a battery pack. The
I have an outdoor fireplace that has a battery pack. The battery pack has become corroded and needs to be replaced. I have ordered the part. Shouldn't the gas still come on even without the battery pa… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a heatilator model CD4842IR-C fireplace. It doesn't
I have a heatilator model CD4842IR-C fireplace. It doesn't start often. I reset the module, then turned power on and it lights but then the pilot drops off in seconds.… read more
Charles Bodenheimer
Charles Bodenheimer
Owner
Associate Degree
78 satisfied customers
We have a Heatilator gas fireplace with an intermittent
We have a Heatilator gas fireplace with an intermittent pilot system. We had a fuse blow on the breaker a few nights ago, and now the fireplace will not light. All of the plugs are good, and the fuse … read more
Chad DeYoung
Chad DeYoung
11 satisfied customers
Electronic ignition on my furnace does not spark. Any suggestions?
I have a Rheem 80 plus furnace Model # RGDC-10EC1JR with electronic ignition. I'm getting no spark to the ignitor. Already replaced ignition module and ignitor. Any other suggestions? It will light pi… read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,942 satisfied customers
I have a heatilator system with an IPI ignition. Gas is
I have a heatilator system with an IPI ignition. Gas is getting to the valve, but is not coming out of it. Can this be due to a faulty control module?… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I'm ***** *****, working on gas fireplace I'm a master
Customer: hi i'm ***** *****, working on gas fireplace I'm a master electrician and controls tech but not experienced with these units. it is a Dexen IPI system Pilot lights fine and does not keep spa… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a heatilator fireplace with the Intellifire ignition
I have a heatilator fireplace with the Intellifire ignition system that won't light. Always has before without any problems. By the "trouble shooting" instructions, voltage to the ign. module," under … read more
Nathan Marshall, MP
Nathan Marshall, MP
Master Plumber,HVAC Tech,Tradesman
Vocational, Technical or Trade School
275 satisfied customers
Hi! Im installing a Honeywell TH6320R1004 wireless thermostat,
Hi! I'm installing a Honeywell TH6320R1004 wireless thermostat, with a THM5320R1000 Equipment Interface Module (EIM), to control a gas fireplace insert, Heatilator Model GNRC36. The Heatilator manual … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a 1997 vintage Heat N Glo Model 6000 xls natural gas
I have a 1997 vintage Heat N Glo Model 6000 xls natural gas fireplace. The pilot has gone out and I can't restart. I also can't locate the users manual. Can you assist?… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have two gas fireplaces and neither will work right now
We have two gas fireplaces and neither will work right now (they were both working fine just a couple days ago). They're only 7 years old or so. We aren't smelling gas and our pilot light is on for ou… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a gas fireplace Heatilator gc300. When I turn on the
I have a gas fireplace Heatilator gc300. When I turn on the firplace it will light the back burner than a second later it lights the front burner than the flames dies out. I have a robertshaw ignition… read more
V12Tech
V12Tech
252 satisfied customers
Hello. I was trying to help an older man with his Laars JVS100
Hello. I was trying to help an older man with his Laars JVS100 that has not undergone any maintenance for several years. I jumped some of the wires to bypass a bad fuse and attached the vent damper an… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Please can you help me troubleshoot my Heat-n-Glo fireplace?
Hi, I have a Heat-n-Glo model SL 750 TR IPI fireplace which we can't seem to get going for the Fall Season. It was only used once or twice last year. We have two wall switches, when both are turned on… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My Heatilator gas fireplace shuts off after a while. Why?
I have a Heatilator gas fireplace with electronic ignition installed in 1996. The fireplace lights for a moment and then shuts off. There is no blockage in the venting system. The ignitor was replaced… read more
Jerry
Jerry
Service Technician
3,367 satisfied customers
Hello, Ive got a Heatilator fireplace GC150 E with a Robert
Hello, I've got a Heatilator fireplace GC150 E with a Robert Shaw 832 controller DSI unit. The unit has been slowly failing, I get a good spark, it would sometimes come on and burn for as long as 15 m… read more
Jerry
Jerry
Service Technician
3,367 satisfied customers
Pilot switch fails to ignite my Heatilator Model GNDC36
I have a Heatilator Model GNDC36. The switch fails to ignite the fireplace. It has worked for several years, but no longer. This happened in the past. At that time I disconnected the switch at the wal… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I hane a Heatilator Fireplace with a Robertshaw 845 igniter
I hane a Heatilator Fireplace with a Robertshaw 845 igniter box. the fireplace lights for a few seconds and then shuts off. the LED on the box is flashing.I have replaced the Ignitor unit and sured up… read more
Jerry M.
Jerry M.
Senior HVAC Technician
High School or GED
133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x