I have a munchkin model T80mr2. I cleaned the electrodes which were clean and still no spark. Any ideas?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Just started, 10 years old never had a problem before.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

There is gas in the tank

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
11/16/2017
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,378
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your

issue. First I’ll need some more info so I have a more complete picture of your situation. WHat's the electrode gap? Should be the thickness of 2 quarters

Ask Your Own HVAC Question
Customer reply replied 8 months ago
the gap is 1/4 inch
Customer reply replied 8 months ago
electrodes are cleane
Customer reply replied 8 months ago
set to specs in manual
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

If you have a good ground pull the hot lead off the board and hold it no more than 1/4" away from a bare metal section the boiler chasis. Hold it with insulated pliers. Do you get an arc?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
do you mean pull the hi voltage lead off the igniter. I have not tried that yet.
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

Yes, it's line voltage.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
should I try that and get back to you.
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

Ok

Ask Your Own HVAC Question
Customer reply replied 8 months ago
what time are you there to?
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

~ 7 pm ET. I do take breaks. I'll respond as soon as I can. Back ~ 9 am

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a Richmond 6G40PV-40F water heater. The flash code is
I have a Richmond 6G40PV-40F water heater. The flash code is failed ignition. I turned the switch on the inducer fan off then on to watch it cycle. Ignitor started working and it ignited... this was l… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
I have a. P1-140REV2 boiler it ran fine till we added the
Hi, I have a. P1-140REV2 boiler it ran fine till we added the Peerless Partner indirect water heater to it with the Honeywell controller. Now the boiler at first the boiler was running but kept quitti… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
Munchkin 140M R2 for baseboard heat and with Superstor for
munchkin 140M R2 for baseboard heat and with Superstor for domestic hot water. … read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
I have been working with, on a Modine Model PAH 180 AF
Hello, I have been working with Tim, on a Modine Model PAH 180 AF serial 150120206992, gas unit heater. So far the relay,gas valve, pilot assemble, sensor rod and lead and primary control have been re… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
I have a munchkin 140mR2 nat. gas boiler. When the boiler
I have a munchkin 140mR2 nat. gas boiler. When the boiler ignites sometimes it will make a loud bang. I have replaced the ignitor with correct gap and performed coil cleaning inside unit with clr clea… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
Have a munchkin boiler that won't fire Unit turns on ....can
Have a munchkin boiler that won't fire Unit turns on ....can smell the gas when it sparks But won't fire Trouble code F09… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
Good Morning: Question about VR8204A2266 unit. Sparking but
Good Morning: Question about VR8204A2266 unit. Sparking but will not pass gas to light. I checked all electrical connections. Any ideas?… read more
Rick
Rick
HVAC Supervisor
24,378 satisfied customers
Hi Tom. I have a munchkin h/e heater with the 925 controller,
Hi Tom. I have a munchkin h/e heater with the 925 controller, can't get a spark from the electrode (which I've cleaned). Try restarting, no spark and F09 error after three tries. Any suggestions?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Same problem. Have spark , runs on and off for a few seconds
Same problem. Have spark , runs on and off for a few seconds than shuts down. Munchkin 140 r2… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
Munchkin F09 problem. Followed Toms help here hvac/4s0jd-munchkin-boiler-fault-code
Munchkin F09 problem. Followed Tom's help here hvac/4s0jd-munchkin-boiler-fault-code-f09-according.html and it started right up. Problem is it didn't start a second time and now the F09 won't clear. A… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I have a Munchkin boiler and once in a while, I get an F09
I have a Munchkin boiler and once in a while, I get an F09 error. When it happens, I usually just change the spark electrode 7250P, but they never come in the same exact size: the gap ranges from 1/8 … read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
We have a twelve year old Amana propane four-burner cooktop
We have a twelve year old Amana propane four-burner cooktop stove. it is a great unit and we have had no problems with it until recently, when the two burners on the right will not ignite. We hear the… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
For a Munchkin High Efficiency Boiler: The Boiler will trip
For a Munchkin High Efficiency Boiler: The Boiler will trip out with code F10 and the unit needs to be reset often. In the past, I would remove the spark electrode and clean it which would correct the… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have an older Munchkin hot domestic water heater 199vwh,
I have an older Munchkin hot domestic water heater 199vwh, about 8-12 yrs old. It has a Honewell controll board 199M. The diagnostic for fault is by the blinking green led. Lately it run very sporadic… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
Munchkin 140 boiler, shut down with fault code F10 low pressure
Munchkin 140 boiler, shut down with fault code F10 low pressure fault. The customer checked his propane tank and he is at 18%. Probably the issue... however now when he tries to fire the unit, the tan… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
Hello, I have a Ferroli Tempra 24 which keeps lighting the
Hello, I have a Ferroli Tempra 24 which keeps lighting the gas burner and then almost immediately the gas goes out...on and off, on and off. It's the same when it supplies hot water or central heating… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
I have Munchkin 80 MLP boiler. Error is Ignition failure (4
I have Munchkin 80 MLP boiler. Error is Ignition failure (4 pulses). Manual says," check that the gas valve is operating correctly and the plug is fully connected to the valve (nothing in the schemati… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Hi I have a munchkin high efficency boiler. Its been online
Hi I have a munchkin high efficency boiler. Its been online with zero problems or maintenance for 3 years now. In the past week it has developed a problem that is getting worst. It rumbles loudly then… read more
Problem solver
Problem solver
Hvac technician
Vocational, Technical or Trade Scho
33 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x