My boiler will not come up to temp.Weil-McLain Gold GV

Customer Question
My boiler will not...

My boiler will not come up to temp.Weil-McLain Gold GV boiler (Series2) I have gone through the trouble chart listed in the owner manual but have come to a dead end. The circulating pump is operating

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

It started last night. I have also checked the block switch and it is closed. The limit switch is closed as well. I have changed out the control module with another boiler and still have the same results. The power light is on and when it cycles through the purge light comes on and the fan functions. Then the ignitor comes on for the usual time then the flame light comes on. Sometimes it will stay on for 5 or 10 seconds and other times it will stay on for about 2 minutes.Each time it fails there is a clicking sound in the gas valve and the unit shuts down. Do you think I have a faulty gas valve or some other problem

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

I have three zones and all stats are calling for heat. There is no filter on this model.

Contractor's Assistant: Do you plan on doing the work yourself?

I am very handy and will give it a try.

Contractor's Assistant: Anything else we should know to help you best?

I think that is the full story

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 3 minutes by:
11/15/2017
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,391
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

When the burner shuts down what LED is flashing on the control?

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Boiler does not turn on. Just this morning but happened be
This is a weil McLain boiler Three red lights is out… read more
Rick
Rick
HVAC Supervisor
24,391 satisfied customers
I have a Weil McLain gold GV-2. When it tries to fire, I can
I have a Weil McLain gold GV-2. When it tries to fire, I can see the ignitor come on through the sight glass, the I can see the flame come on, the it shuts off for no flame. How does it achieving flam… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
454 satisfied customers
Weil-Mclain Gold GV 1) Thermostat calls 2) Relays click and
Weil-Mclain Gold GV 1) Thermostat calls for heat 2) Relays click and blower motor starts up (replaced last season) 3) Runs for about a minute and shuts down. No Error Lights flashing. It appears that … read more
Rick
Rick
HVAC Supervisor
24,391 satisfied customers
i have a weil mclain gold gv boiler that starts the purge light
i have a weil mclain gold gv boiler that starts the purge light comes on and it shuts off no heat… read more
Rick
Rick
HVAC Supervisor
24,391 satisfied customers
I have BW1 Dunkirk boiler making a banging noise when it starts
I have BW1 Dunkirk boiler making a banging noise when it starts to heat the water what I have done is I flushed the out and removed all air in the lines… read more
Rick
Rick
HVAC Supervisor
24,391 satisfied customers
No heat Have gas. GV-6 90+ Weil Mclain boiler 5 zones and superstor
No heat Have gas. GV-6 90+ Weil Mclain boiler 5 zones and superstor Just had antifreeze last month. Had system purged 4 days ago. was having problem with no hotwater. Control indicates power light is … read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
I have a Weil Mclain Gold gas CGa boiler operated buy dual
I have a Weil Mclain Gold gas CGa boiler operated buy dual zone Taco SR 502 relay controller. My problem is that slowly over time the boiler is not lighting with either thermostat, though the circulat… read more
Rick
Rick
HVAC Supervisor
24,391 satisfied customers
I have a Weil-McLain gold GV boiler and am not getting any
I have a Weil-McLain gold GV boiler and am not getting any heat. The system is doing this according to the control module lights.... It is starting up with the green power and first red. then going to… read more
Rick
Rick
HVAC Supervisor
24,391 satisfied customers
my weil-mclain gv-3 series 2 will not fire. I have a full
my weil-mclain gv-3 series 2 will not fire. I have a full LP tank and other gas appliances are working; the valve serving the LP is open to the furnace. It has power. I have an LED panel with 5 bulbs … read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
I have a Weil-McLain Gold-GV ..................I notice this
I have a Weil-McLain Gold-GV ..................I notice this morning that the power indicator light was green but the purge button was flashing red. What does this mean?… read more
Rick
Rick
HVAC Supervisor
24,391 satisfied customers
Please forgive spelling and punctuation because I am dictating
Please forgive spelling and punctuation because I am dictating this I have a Weil McLean boiler vintage 1991 with the United Technologies 1013 – 100 controller. The boiler is a Gold GV series. It has … read more
Rick
Rick
HVAC Supervisor
24,391 satisfied customers
Our Weil McLain Gold GV failed to reset following a power outage
Our Weil McLain Gold GV failed to reset following a power outage this summer. We heat our water from the boiler. I have followed the reset instructions, shutting off the GAS AND POWER FOR 5 MINUTES AN… read more
Phil
Phil
Mechanical Engineer
7,426 satisfied customers
We have a weil-mclain gold gv boiler that will not put out
We have a weil-mclain gold gv boiler that will not put out heat. It continues to cycle through the Seq of Oper. It has 5 indicator lights, Power, Purge, Ignitor, Valve and Flame. The first 3 stay on a… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Weil-Mclain mdl# CG5SPN boiler baseboard heating system.
I have a Weil-Mclain mdl# XXXXX boiler baseboard heating system. I can't seem to stop the loud gurgling sound of water flowing through the pipes??? Tried to flush the zones at the boiler, but no help.… read more
Rick
Rick
HVAC Supervisor
24,391 satisfied customers
I have a Weil-McLain Gold GV Series 3 gas fired boiler. What
I have a Weil-McLain Gold GV Series 3 gas fired boiler. What is the operating pressure of the boiler?… read more
Rick
Rick
HVAC Supervisor
24,391 satisfied customers
Weil Mclain Gold GV 4 Boiler (circa 1989 ) --- Has been very
Weil Mclain Gold GV 4 Boiler (circa 1989 ) --- Has been very reliable, with minor parts all replaced to date- gas valve,control module,ignitor. Past 2 years , no problems, but just started making loud… read more
johnincolorado
johnincolorado
8 satisfied customers
I have a weil mclain boiler gv-5, series 1 gas boiler to heat
I have a weil mclain boiler gv-5, series 1 gas boiler to heat my home I replaced the integrated boiler control three weeks ago. It's a weil mclain part. #(NNN) NNN-NNNN I do not get hot water to all o… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
HEATING BOILER HAS NO FLAME NO FIREMAKER WEIL-MCLAIN MODEL# GU-4
1,HEATING BOILER HAS NO FLAME NO FIRE MAKER:WEIL-MCLAIN MODEL#:GU-4 SERIAL#: 2 THERE ARE 5 SIGNAL LIGHTS. AMONG THEM ONLY FLAME LIGHT IS NOT ON. 2,PRESURE GAUGE IS NOT PROPERLY WORKING,FIXED ON UPPER … read more
Rick
Rick
HVAC Supervisor
24,391 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x