Have a York D1NP042N09006 DUAL AC/GAS HEAT unit. had blower replaced and since then fan speed is too high(35 40 degree difference in/out) how do adjust? or is ST9120 2002 board bad?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

All good

Contractor's Assistant: Do you plan on doing the work yourself?

If possible yes

Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
11/15/2017
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,181
Experience: Furnace, A/C and heat pump specialist.
Verified

If they are using the black wire for cool speed ,you can move the blue to the cool relay and slow fan down and move black to unused terminal. Let me know what terminals currently being used.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Has Genteq variable speed Eon motor. Sending pics, control board has empty terminal marked sp up
A91AC024-9D07-4975-9990...jpegA91AC0...jpeg986622DA-5813-4D82-8431...jpeg986622...jpeg073B8EB0-F789-44C3-9EE4...jpeg073B8E...jpeg12EA3125-1997-4440-83D5...jpeg12EA31...jpeg37AA228F-EFA0-49AD-8B5B...jpeg37AA22...jpeg7865B8CE-C0FC-428E-9A25...jpeg7865B8...jpeg

Since this is a variable speed ecm you can not change speeds by changing wires.These motors must be programmed for the specific furnace it is installed in.Perhaps not programmed properly

Ask Your Own HVAC Question
Customer reply replied 8 months ago
okay , is this something a regular tech can do ? I am reaching out to a different company because 4 techs couldn't figure this out.

Does your motor have a 4 and 16 wire harness or a 2 and 4 wire harness?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
motor control # EON HD01 1HP 3/24/2015 . Has plug with black-purple and green. 2nd plug has 8 wire orange,yellow,black,blue,white,red , and 2 tan.TheDealerToolbox.com is supplier

See if it looks like this motor and verify connections

Ask Your Own HVAC Question
Ask Your Own HVAC Question
Customer reply replied 8 months ago
no it's the Eon motor. I went on Genteq site ,it seems that the controls in the unit have to signal the motor /controller.they speak of dip switches to set speed but I don't see any except ones in the Honeywell board marked heating speed delay off adjust(secs) seems strange to have variable speed motor but no speed control but I'm a locksmith!

Did the furnace originally have an ecm?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I have not been able to get a manual for this unit. have to assume it did because it had the Eon controller module mounted to the blower housing before being replaced.

OK if it is the motor with the 16 pin connector those have tobe pre programmed to match your furnace.The distributor who sold motor to installer should have the equipment to match the motor to the furnace.It doesn't sound like this was done.

airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,181
Experience: Furnace, A/C and heat pump specialist.
Verified
airheatman and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 8 months ago
now that makes sense if the unit doesn't communicate to the motor. maybe I should contact TheDealerToolbox direct. thanks
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,181
9,181 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I own a goodman GMNT100-4 HVAC. THE PROBLEM IS A BLOWER WILL
I own a goodman GMNT100-4 HVAC. THE PROBLEM I'M HAVING IS A BLOWER WILL NOT TURN ON WHEN IN HEAT THUS CAUSING THE HIGH LIMIT SWITCH TO TURN ON PREVENTING THE FURNACE TO CONTINUE ACTIVATION. THE BLOWER… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Frigidaire branded packaged dual fuel hvac unit.
I have a Frigidaire branded packaged dual fuel hvac unit. Made by Nordyne. It has 2 cools 2 heat pump heats and 2 natural gas heats. I have it wired for two stage aux heat. Jumper removed from gas val… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have Trane furnace about 13 years old, the upper limit
Hi I have Trane furnace about 13 years old, the upper limit switch fails about once a year. I have installed 5 different switches in the past at $50 each. Just had another fail, have bought several pl… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Ac is working and brand new, but the furnace fan motor speed
Ac is working and brand new, but the furnace fan motor speed is to slow the limit switch shuts ac off quite often at 40 degrees. The thermostat and zone board are fine, but am wondering if the board t… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox dual fuel furnace. I had a blower test done
I have a Lennox dual fuel furnace. I had a blower test done recently on my house to assess for air leaks,and ever since then, my auxiliary heat comes on when I set up the thermostat 3 degrees each mor… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
If my furnace wont run unless I put fan on after 30 secs set
If my furnace won't run unless I put fan on after 30 secs set it to auto what could be causing my furnace not to run. Once the temp is met only way to get furnace to run is reset the fan to on and set… read more
airheatman
airheatman
HVAC Technician
9,181 satisfied customers
I think I got some bad avice last time. I replaced the board
I think I got some bad avice last time. I replaced the board on my York furnace and now I have exactly the same problem as before. Model number is XXXXX Problem is that when thermostat calls for heat … read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
What are the differences and pros and cons between the Bryant
What are the differences and pros and cons between the Bryant 580JP12D224G1A0AA High Efficiency Gas/Electric Rooftop unit vs the Bryant 580CED12A2A5-OAOAO (10 ton cooling, roof mounted, 230-3-60 elect… read more
V12Tech
V12Tech
252 satisfied customers
I have Nordyne E2EB-015HA furnace. All is working except the
I have Nordyne E2EB-015HA furnace. All is working except the fan motor does not rotate. T/S and all the speed inputs connected have 120volts along with the C input. Heating elements get hot on heat an… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
have a trane xl 90 want to adjust speed of blower fan blower
have a trane xl 90 want to adjust speed of blower fan blower motor has 4 wires white going to neutral black unhooked blue to high speed yellow to med speed strip has high - med - med low - low spade c… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Ive been having a problem with my Carrer Gas Pack.
I've been having a problem with my Carrer Gas Pack. Unit intermittently does not respond to calls for heat especially when temp drops below 30 degrees. I'm getting error codes indicating that there is… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am checking my system before winter really rolls in in Texas
I am checking my system before winter really rolls in in Texas and when I set my thermostat to heat, the furnace (Luxaire G8T06012UHA11A) ignites without any issue, but the blower fan does not come on… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Heil 9mpv furnace and I was wondering if there is
I have a Heil 9mpv furnace and I was wondering if there is a way to keep the blower running on high all the time? Currently, it is on low all the time and then goes to high speed when the furnace is h… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
My circuit breaker (15A) trips whenever the thermostat is set
My circuit breaker (15A) trips whenever the thermostat is set on "Cool" and Fan switch on the thermostat is set to "on". It does NOT trip with thermostat set to "Heat" and Fan switch is "On". Although… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
rooftop package unit PGF060H100C cannot energize fan on heat
rooftop package unit PGF060H100C cannot energize fan on heat mode changed board same problem has smart valve SV9501 honeywell cannot get reading off orange wire from valve to 6 point plug on board doe… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Goodman GMNTE120-5 has been shutting off after 2 minutes
My Goodman GMNTE120-5 has been shutting off after 2 minutes of the natural gas burner coming on. The main limit operates and opens the circuit shutting down the burners. The duct blower fan kicks into… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
York model p4hub16n06401a with multispeed blower. Changing
York model p4hub16n06401a with multispeed blower. Changing tap location does not lower blower speed enough.Lowest speed only allows outlet temp of 110F and is very noisy. Could a rheostat be used to l… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
HVAC fan blows weaker at vents. Is the fan adjustable?
Our house hvac fan does not blow very strong. Gets weaker at vents the further out from the attic unit. Is the fan output adjustable? I turned on the fan only switch to check this. Same output if on h… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x