Maybe, just one day. I just installed a reznor udap 150 unit…

Customer Question
Just one day....

Just one day. I just installed a reznor udap 150 unit heater replacing my old unit heater. it fires up for about 3 minutes then cuts out even though the thermostat is still calling for heat

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

No filter in the udap

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

The led light comes on saying that it is calling for heat yet is wont turn back on for about another 5 minutes. surely it should heat until the thermostat tell it to stop

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 10 months ago
No it says its operating normally. LED is green flashing constantly which means the thermostat is calling for heat
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Does the green flash slow down when thermostat is off?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Not tonight as I am at home. I was hoping for an answer from here. I could call tomorrow night as i'll be there
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

WE can troubleshoot when onsite tomorrow night.Just come back to question then

Ask Your Own HVAC Question
Customer reply replied 10 months ago
No it just stays flashing the same pace and I checked that is normal op.
Customer reply replied 10 months ago
Have you had much experience with the reznor unit heaters?
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

It should stay flashing until thermostat is satisfied.Otherwise we should get an error code.Yes, very familiar with the Reznor.HVAC contractor since 1989 and been in the business since 1974.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
OK cool. im pretty sure the green light stops flashing when there is no call for heat. I just flashes fast even though the thermostat is still calling for heat. So the thing comes on for 3 minutes then stops for about 5 but the whole time the green light is flashing. So it gets the room to temp but not efficiently.
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Actually light will be just steady on until call for heat and flash on call. But anytime it is flashing it should stay on unless a pressure switch or limit opens

Ask Your Own HVAC Question
Customer reply replied 10 months ago
the room was at 7celcius and I had the therm set to 25. so the light was flashing constantly as was call for heat. then it did as i said but even after the flame stops the light keeps flashing and the room is still only at 7 celcius
Customer reply replied 10 months ago
it does this on and off thing until the room gets to temp.
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Here are a few things you can check when you get there.

Make sure grounds are all good

Make sure pressure switch is staying closed

Make sure the ceramic on flame sensor is not cracked

Make sure polarity is right

Make sure the 9 pin connector I making good contact and all wires are seated good in the connector

Make sure gas pressure is staying within the 3.5 to 5" WC range

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Ok i'll check all that. Only thing I wont be able to check is gas pressure as i dont have the manometer or what ever its called.
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

But in all actuality if the burners are ever off, thermostat calling for heat and we do not get an error code such as open limit, weak flame, open pressure switch,etc, the circuit board is failing to do it's job.

New does not necessarily mean good as these boards must all come from China or Mexico.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
yep for sure i had a brand new dishwasher that the Main board blew up in the first week. Is it bad that it is coming on and off like that? I would hate to change out the board and it not be the problem
Customer reply replied 10 months ago
i'll take another look at it tomorrow. PCB is $250 from the first place I looked at so not a cheap part exchange
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

I understand. Thought it was new and figured warranty would cover, You might also try bypassing limit and once unit starts the pressure switch One may be opening board just not giving error.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,542
9,542 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I HAVE A 1500 SQUARE FOOT METAL BUILDING WITH 18 FOOT HIGH
HELLO, I HAVE A 1500 SQUARE FOOT METAL BUILDING WITH 18 FOOT HIGH CEILING AND R19 WALLS AND CEILING INSULATION IN GLENWOOD SPRINGS, COLORADO. NEED TO SIZE TWO UDAP UNITS TO HEAT. ANY IDEA WHAT SIZE UN… read more
airheatman
airheatman
HVAC Technician
6 years college
9,542 satisfied customers
Reznor UDAP150 has not ran for over 1.5 years due to no gas
Reznor UDAP150 has not ran for over 1.5 years due to no gas meter present. Gas meter is now installed, thermostats installed and verified working. Upon initial fire the furthest heater fired up for 5 … read more
airheatman
airheatman
HVAC Technician
6 years college
9,542 satisfied customers
I am having trouble, my heater fires and runs great then the
I am having trouble , my heater fires and runs great then the flame slowly gets smaller and smaller until unit shuts down . If i hit reset it fires up perfect , good flame but then the flame slowly ge… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I would like to swap my current digital Aprilaire thermostat
I would like to swap my current digital Aprilaire thermostat to a Nest (Gen 3) to control my new Renzor UDAP 60. Current installation: The t-stat has R (red), W (white), G (green), W2 (blue), as well … read more
airheatman
airheatman
HVAC Technician
6 years college
9,542 satisfied customers
I spoke to you a while ago about our dornback unit heater.
hi, I spoke to you a while ago about our dornback unit heater. we changed the roll out switchs and it has worked for a while. now we have another issue. the heater wont start in the morning when we tu… read more
airheatman
airheatman
HVAC Technician
6 years college
9,542 satisfied customers
I have a reznor udap 125 unit heater. Runs fine up until a
I have a reznor udap 125 unit heater. Runs fine up until a temperature of about 80 degrees. We used to get up to 90 degrees. greenhouse application. At 80 degrees it cuts off and light on circuit boar… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Reznor UDAP 45 overhead garage heater that has quit
I have a Reznor UDAP 45 overhead garage heater that has quit working. The power supplying it has been checked to be good but it wont start or run?… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
i have honeywell heat only thermostat with W (heat relay, C
i have honeywell heat only thermostat with W (heat relay, C (24vac common), and R (power) and am hooking up a Reznor udap45 gas heater with R,G,W1,W2 as options. What goes to what? I can not find wher… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have Reznor XL-30 in garage. In warmer months I occasionally
I have Reznor XL-30 in garage. In warmer months I occasionally turn it on and runs great. In the winter {Alaska} it will cycle on and off frequently until it hits the correct temp. It seems that maybe… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
hello I installed a new reznor model udap 45,000 heater yesterday.
hello I installed a new reznor model udap 45,000 heater yesterday. It is a natural gas unit that is replacing an older unit previously installed. The unit works well except for one thing. The fan will… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
I have a Reznor UDAP 75. Everything sounds fine. Induction
I have a Reznor UDAP 75. Everything sounds fine. Induction motor, than clicking and you cna hear/smell gas. No ingnition. Fast blinking green light after three tries.… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have a reznor UDAP 60 and when it goes to start, the ventoer
I have a reznor UDAP 60 and when it goes to start, the ventoer motor and the fan start at the same time. I get 3 flashes for a limit switch problem, it doesn't try to light, the fans cycle and then I … read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
I have a Reznor UDAP 45 garage heater just installed. I know
I have a Reznor UDAP 45 garage heater just installed. I know some units are designed to draw combustion air from within the garage, but with this one they punched a 5" hole in the side wall, put in a … read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Reznor gas heater Mod. # UDAP30. How can I check
I have a Reznor gas heater Mod. # XXXXX How can I check the flame sensor to see if it is good?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
my furnace lights up, burns fine, blower comes on. after a
my furnace lights up, burns fine, blower comes on. after a few minutes, sometimes quite a few, the burner stops. the fan continues blowing, the burner fan starts back up but the burners will not relig… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have has a new LF24-45A #5610E09056 installed in my garage
I have has a new LF24-45A #5610E09056 installed in my garage and i turned in on for the first time today. It doesn't seem to run as it should. As the thermostat calls for heat the burner comes on and … read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
reznor UDAP 60 newly installed and running fine until today when
reznor UDAP 60 newly installed and running fine until today when thermostat is set exhaust blower comes on and unit fires when it reaches temperature the air fan does not come on and unit shuts down t… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Beckett AF2-150. 3 yrs old. Problems with outo shut downs(very
Beckett AF2-150. 3 yrs old. Problems with outo shut downs(very hard smokey starts,very shakey running and un called for cycling of motor). Replaced pump last year (leaking). Tech did not use beckett r… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x