I have replace the board and the the limit switch and the…

Customer Question
I have replace the...

I have replace the board and the the limit switch and the flame sensor. now and before the exact thing happens.... exhaust would come on and the igniter would glow orange flame would kick on and then kick whole system would kick off

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

About a week

Contractor's Assistant: Do you plan on doing the work yourself?

Preferable

Contractor's Assistant: Anything else we should know to help you best?

Rheem furn. model RGDJ-07EAUER serial no. EC5D302F309708200

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 14 minutes by:
11/15/2017
HVAC Technician: airheatman, HVAC Technician replied 10 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,529
Experience: Furnace, A/C and heat pump specialist.
Verified

Do you get an error code on board by flashing green light?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
between the retries or start ups i get 4 blinks, after that i get the lock out blinks
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Let me grab a manual

Ask Your Own HVAC Question
Customer reply replied 10 months ago
according to the schematic on the furn.1 blink is lock out
2 blink is pressure switch is open
3 blink is limit switch is open
4 blink is lock out
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Not finding a manual for this one.You never get a 2 or 3 blink before the lockout?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
my apologies 4 blink is pressure switch shorted.
to answer you question no
i did before i replaced my limit switch
now i do not
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Next I want you to locate the pressure switch. It will be a small round canister with a hose attaching it to the inducer housing. Remove hose from inducer housing and leave it attached to the pressure switch. Power off and back on to reset board again, Then call for heat at thermostat. Allow inducer to start then suck on the end of hose still attached to pressure switch and see if switch will close and burners ignite.

Pressure switch may be metal or plastic, See below

http://i.imgur.com/xz4NcnM.jpg

http://i.imgur.com/at2Z27r.jpg

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Keep sucking and see if it will stay lit

Ask Your Own HVAC Question
Customer reply replied 10 months ago
ok i did that in 2 different cycles, it only kick on for a few seconds then kicked off,
like it has been
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

If furnace ground is good, and flame senser is good I am going to say you got a bad board again.Not so unusual as these things are coming out of Mexico and China these days. Let's swap board if they will exchange

Ask Your Own HVAC Question
Customer reply replied 10 months ago
huh!? so i am not crazy thinking that. okay it may be a few days before i get back to you about this. in mean time is there anything that i can do to try to do? other than switch out the board
HVAC Technician: airheatman, HVAC Technician replied 10 months ago

Not that I can think of .You have already changed the limit and flame sensor and imitated closing pressure switch by sucking.Only other thing I could think of is if there is another limit somewhere in circuit but it doesn't sound like it runs long enough for a limit to be issue

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,529
9,529 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a ruud achiever 90 plus. Blower works on manual but
I have a ruud achiever 90 plus. Blower works on manual but will not fire up or stay on when I click over to the heat button on thermostat. Both green lights are on 1) power 2) ok. The unit worked last… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i am getting a 3-4 code on my byrant model 340 furnace.changed
i am getting a 3-4 code on my byrant model 340 furnace.changed the filter.checked and ruled out air blockage from exhaust and return.did see a corrected tube with a spring clip just hanging there? don… read more
airheatman
airheatman
HVAC Technician
6 years college
9,529 satisfied customers
I am trying to fix a rheem gas furnace. model number rgdg-07eauer
I am trying to fix a rheem gas furnace. model number rgdg-07eauer serial number cwsd302 f3893 1445. The burners come on but go out after about 3 seconds like its not sensing the flame. I changed the f… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,634 satisfied customers
Hello.. I have a Rheem Centurion 2.. Turn it on,exhaust blower
Hello.. I have a Rheem Centurion 2.. Turn it on,exhaust blower starts and I get one green light on the board. Approx. 30 sec. later the igniter starts to glow and I get a second green light. Approx. 3… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a goodman GMP075 and startup sequence is not correct,but
I have a goodman GMP075 and startup sequence is not correct,but shut down sequence is OK. I'm thinking control board,but need to verify. thanks… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have RHEEM gas furnace RGDJ _07EAUER with hot surface Igniter.(HSI).
I have RHEEM gas furnace RGDJ _07EAUER with hot surface Igniter.(HSI). This HSI does not glow. I replace it with new one. Inducer works. May be lock out . I light it with long gas lighter and it works… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a Rheem RGDJ-07EAUER and the main blower is not coming
I have a Rheem RGDJ-07EAUER and the main blower is not coming on in either auto or on position on the thermostat. pre-induction motor comes on, ignitor heats up, gas comes on and burners blow but the … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Rheem Super Quiet 80 furnace and the furnace is not
I have a Rheem Super Quiet 80 furnace and the furnace is not reaching my desired temperature. It runs for 5 min then shuts off for an hour. Then back on for 5 and off for an hour. This is a 3 week pro… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Rheem Furnace Model - FGPJ-10EBRJR Serial - EB5D307F199900304 I
I have a Rheem Furnace: Model - FGPJ-10EBRJR Serial - EB5D307F199900304 I have replaced the igniter, flame sensor, and the IFC board. Furnace will still not heat. Induced draft blower motor starts, 5 … read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a Nordyne M1MB 056A BW furnance. It quit working on
I have a Nordyne M1MB 056A BW furnance. It quit working on me last night, sometime between 1 am and 7:30. The red light was blinking 4 times, which means "Lockout due to failed ignition". I turned the… read more
TimVZ26
TimVZ26
Service Foreman
Vocational, Technical or Trade Scho
157 satisfied customers
I have a ruud silhouette gas furace, model UGLH-07EAUER, serial
I have a ruud silhouette gas furace, model UGLH-07EAUER, serial number DAID302 F2794 0596, 7500 btu down draft. I havent used it for about a year, I relocated it to a new location in the house. Everyt… read more
Tom
Tom
HVAC Technician
Vocational, Technical or Trade Scho
770 satisfied customers
Im having a problem with a Rheem furnace in my shop, Im a
I'm having a problem with a Rheem furnace in my shop, I'm a licensed electrician. It started out when I noticed the blower and the induced draft fan would not shutoff, running whenever the power is tu… read more
Paul
Paul
Vocational, Technical or Trade Scho
108 satisfied customers
HI. I have a Lennox furnace that is about 5 years old (I dont
HI. I have a Lennox furnace that is about 5 years old (I don't remember the model number as I'm at work). Anyways, I changed the Hi/Low switches and cleaned the flame sensor because I had a problem wi… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
the green light is flashing on the circuit board and the blower
the green light is flashing on the circuit board and the blower runs all the time, it will only stop if i shut the whole system down via the isolating main switch… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Furnace is Corsaire by Rheem, Model FGPJ-07EAUER, Serial EB5D302F429810676 Problem
Furnace is: Corsaire by Rheem, Model FGPJ-07EAUER, Serial EB5D302F429810676 Problem: No Heat - I see the heating element get hot, 3 jet-type burners light with flames, (kinda cool to watch), air blows… read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I have a Rheem Criterion furnace model RGDJ-07EAUER. My problem
I have a Rheem Criterion furnace model RGDJ-07EAUER. My problem is when it first starts the cylcle, the ignitor glows, then a blower comes on I think to get rid of any excess gas. Then a valve opens t… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have a rheem-corsaire 1x2000 furnace and the fan would not
I have a rheem-corsaire 1x2000 furnace and the fan would not kick on and the ignition would not operate unless i unplugged two red wires that are connected to what appears to be a sensor. Is this an i… read more
Roger (Mr. Fixit)
Roger (Mr. Fixit)
Service and Sales Manager
Bachelor's Degree
16 satisfied customers
I have a rheem classic 90 plus, it is 3 years old. It is a
I have a rheem classic 90 plus, it is 3 years old. It is a gas furnnse. It is turning off and on, sometimes it does not fire up, and just blows cold air. Othertimes it runs like a champ.… read more
JBM HVAC
JBM HVAC
HVAC/R Technician
Vocational, Technical or Trade Scho
50 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x