I'm reading the issue where blower doesn't come on after

Customer Question
I'm reading the issue where...
I'm reading the issue where blower doesn't come on after combustion but does work in manual or when heat pump runs.
JA: Did you double-check the thermostat's settings? And what about the filters?
Customer: Filters are temporarily removed to eliminate possibility. I'm getting fault indicator of 4 red flash.
JA: Do you plan on doing the work yourself?
Customer: Yes, and I've replaced several parts already. This post says it's the control board for my circumstance. Where do I get it?
JA: Anything else we should know to help you best?
Customer: So whatever happened caused the blower motor to fail and the inducer motor to burn up. Both replaced. I then got a different error and tried replacing pressure switches and limit switch. Still getting error.
Submitted: 1 month ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
11/14/2017
HVAC Technician: airheatman, HVAC Technician replied 1 month ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,592
Experience: Furnace, A/C and heat pump specialist.
Verified

What is model on furnace?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
York PV9C20n100up11C
Customer reply replied 1 month ago
Initial problem was blower and inducer motors burned up. Replaced. Blower works now in manual and heat pump modes but does not come on after combustion. Getting 4 red flash indicating limit switch but I replaced a limit switch and pressure switches already. Wasn't sure if the limit switch I replaced was the right one.So now it's either the wrong switch or control board.
HVAC Technician: airheatman, HVAC Technician replied 1 month ago

THanks for this information.The error 4 means limit is opening because blower does not come on.

Since motor works in other mode. we know the issue is that motor is not getting signal to come on in heat mode.

Tell me about the thermostat .What is model on thermostat and what is model on outdoor unit?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Honeywell but don't see a model #. Outside heat pump is York 4 ton. Don't know model.
HVAC Technician: airheatman, HVAC Technician replied 1 month ago

Remove front cover on thermostat to get model.And there should be a label on side of heat pump

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I can see the call for heat. Everything is working fine except Aux or emergency heat when blower doesn't come on. I'll get models.
Customer reply replied 1 month ago
Thermostat model TH832071008
HVAC Technician: airheatman, HVAC Technician replied 1 month ago

The reason I want models is to verify setup. Some thermostats have settings to bring blower on from thermostat and others to bring blower on through furnace board.Looking up manual on stat now

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 1 month ago

Do you know how to get to setup menu?If so make sure function 0180 is set to 0

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Heat pump model Affinity 8T series # YZE04811A
HVAC Technician: airheatman, HVAC Technician replied 1 month ago

Thanks for this info

Do you know how to get to setup menu?If so make sure function 0180 is set to 0

We want 0180 to 0 so blower is controlled through furnace board in heat mode

Ask Your Own HVAC Question
Customer reply replied 1 month ago
The Thermostat does have a manual blower control but I don't know where if it sends request to control board.
Customer reply replied 1 month ago
No I don't know how to get to setup
HVAC Technician: airheatman, HVAC Technician replied 1 month ago

Open this link and scroll to page 6 to get to setup menu so we can check function 0180

https://customer.honeywell.com/resources/Techlit/TechLitDocuments/69-0000s/69-1896ES.pdf

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 1 month ago

Also make sure 200 is set to 1

Ask Your Own HVAC Question
Customer reply replied 1 month ago
0120 and 20
Customer reply replied 1 month ago
There isn't a 0180 function. goes from 0170 to 0190
Customer reply replied 1 month ago
manual says that function is for oil and electric. mine is LP
Customer reply replied 1 month ago
Misread manual 0 is gas but I don't have the 0180 function.
HVAC Technician: airheatman, HVAC Technician replied 1 month ago

What is function 0170 set to?

Ask Your Own HVAC Question
Customer reply replied 1 month ago
200 is set to 1. confirmed
HVAC Technician: airheatman, HVAC Technician replied 1 month ago

Make sure 0170 is set to 12

Ask Your Own HVAC Question
Customer reply replied 1 month ago
170 is 7
HVAC Technician: airheatman, HVAC Technician replied 1 month ago

Change it to 12 and see if we get function 0180 option

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Okay hold on.
HVAC Technician: airheatman, HVAC Technician replied 1 month ago

Your heat pump is a 2 stage plus the backup

Ask Your Own HVAC Question
Customer reply replied 1 month ago
Set to 12 and saved and went back in but still no 0180 option. This unit has an ECM 2.3 motor so isn't it most likely controlled by board since it's variable speed?
Customer reply replied 1 month ago
At this point, what is your gut feel? Since I'm shotgun replacing it seems my only unreplaced items are control board which is what another thread I was reading suggested. If not control board, what else could it possibly be?
HVAC Technician: airheatman, HVAC Technician replied 1 month ago

If thermostat is setup correctly showing furnace blower controlled by the furnace and not tstat, My next suspicion would also be the board.

Ask Your Own HVAC Question
Customer reply replied 1 month ago
I'll try and get a control board but could use your help if you have a resource. Can you tell me what the control board part # is from York? If you have a resource to look that up it would be great and while you're there could you get the part # for the blower control board? I don't suspect it but voltage makes it's way there somehow and might as well have the part # if available.
HVAC Technician: airheatman, HVAC Technician replied 1 month ago
Ask Your Own HVAC Question
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 8,592
8,592 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,877 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Luxaire9v serires furnace Blower won't go into second stage.
Luxaire9v serires furnace Blower won't go into second stage. I replaced pressure switch and still no working. … read more
airheatman
airheatman
HVAC Technician
8,592 satisfied customers
Carrier furnace blower fan comes on without heat set point
Carrier furnace blower fan comes on without heat set point being triggered … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My furnace blower stopped suddenly. I live in about 2,000sq
My furnace blower stopped suddenly. I live in about 2,000sq feet single family home. I called an HVAC technician. They arrived and installed a new motor. However, after they left I run the furnace and… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Have an older luxaire commerical furnace blower motor runs
have an older luxaire commerical furnace blower motor runs all the time … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,877 satisfied customers
My furnace blower wiil not start. Hopefully. Furnace tries
my furnace blower wiil not start JA: Did you check the furnace's filters? Customer: no JA: Do you plan on doing the work yourself? Customer: hopefully JA: Anything else we should know to help you best… read more
airheatman
airheatman
HVAC Technician
8,592 satisfied customers
My evcon furnace blower fan cycles every day at 8:20 with no
My coleman evcon furnace blower fan cycles every day at 8:20 with no demand and no exhaust fan operation. It just co es on runs for 2 minutes then shuts down, and there was no previous heat dema d … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My Nordyne furnace blower starts immediately when I turn on
My Nordyne furnace blower starts immediately when I turn on the switch. The LED light on the control board flashes 5 times. There is no flame. … read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
My '92 Carrier model 58ssc furnace blower motor has finally
Hi! My '92 Carrier model 58ssc furnace blower motor has finally quit. I wonder what I can replace it with … read more
airheatman
airheatman
HVAC Technician
8,592 satisfied customers
We have a question about a furnace blower that is not
We have a question about a Bryant furnace blower that is not working. The model number is ***** We have noticed a blinking light error that has two short and four long blinks. … read more
airheatman
airheatman
HVAC Technician
8,592 satisfied customers
I have a loud noise coming from furnace blower motor. Do i
I have a loud noise coming from furnace blower motor. Do i need to oil up the motor? Its a lennox g40uh (x) … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I'm replacing a furnace blower motor and assumed it would be
I'm replacing a furnace blower motor and assumed it would be plug and play. Old motor had 5 wires; white, brown, black, red and blue. The brown and white went to the cap, with another white wire comin… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
355 satisfied customers
My furnace blower won't shut off. Have confirmed it's not
My furnace blower won't shut off. Have confirmed it's not the thermostat (by disconnecting same). Could the fan relay cause this? … read more
derekh1966
derekh1966
0 satisfied customers
Our lenox furnace blower doesn't come on when on auto
Our lenox furnace blower doesn't come on when on auto setting. Still comes on when set to on. Ideas of what maybe going on? … read more
Tim Ohms
Tim Ohms
HVAC Journeyman
31 satisfied customers
My furnace blower will turn on but the AC condenser wont. I
My furnace blower will turn on but the AC condenser wont … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,877 satisfied customers
Furnace blower cycle on and off even when thermostat is in
furnace blower cycle on and off even when thermostat is in the off position. … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
Sometimes my mobile home intertherm propane furnace blower
Sometimes my mobile home intertherm propane furnace blower does not run and the unit gets really hot. Then after a while (maybe cools down) then the blower runs and things seem normal. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
The furnace blower fan will not shut off even when the wires
Hi, the furnace blower fan will not shut off even when the wires are disconnected. (I am typing this for my Brother) he is working on the furnace. … read more
airheatman
airheatman
HVAC Technician
8,592 satisfied customers
Frigidaire Furnace - Blower starts running when heat is
Frigidaire Furnace - Blower starts running when heat is called, but there is no flame - Green LED flashing when heat called - Green and Red solid when no heat called… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x