I have a York r-22 outdoor split system ac/heater. This

Customer Question
I have a York...

I have a York r-22 outdoor split system ac/heater. This morning, the fan seems to be working but no heat. When I looked into the unit, there is a flashing red light. Can you identify what this issue may be?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes. Additionally, with "auto" fan on, it tries to start up but shuts down, since no heat. The fan works because when I put on "fan" it works constantly (still no heat)

Contractor's Assistant: Do you plan on doing the work yourself?

If simple fix yes, if not, then no. Just asking questions here to see if a simple fix.

Contractor's Assistant: Anything else we should know to help you best?

We have a two unit system (large house), and the other unit works fine so we are not "frozen out"

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
11/14/2017
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago
Gaztech
Gaztech, HVAC Technician
Category: HVAC
Satisfied Customers: 922
Experience: Owner at Gaztech
Verified

Hi I am Gaztech1, a independent technician, I will assist you with your issue.

Don't forget to rate the 5 star rating AT THE TOP OF PAGE after we are done. this will credit me for assisting you.

What is the exact model and be more specific about details

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Not at home right now will answer later
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

Ok

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Owners manual says York R-22 Outdoor Split System Air Conditioner; Models 13 and 14 Seer Series, 1.5 to 5 Tons
HVAC Technician: Gaztech, HVAC Technician replied 8 months ago

Sorry your info is insufficient, Model numbers are found on rating plate on the side of outdoor unit.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Model number is *****
HVAC Technician: airheatman, HVAC Technician replied 8 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,195
Experience: Furnace, A/C and heat pump specialist.
Verified

THanks for your patience. I am a different technician.Not sure why previous expert wanted info on outdoor, but since it is the furnace you are having issues with,give me model in furnace.It will be on a label inside burner compartment.https://i.imgur.com/U8b0GXT.jpg

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I am sorry I need to end this - due to cold weather I couldn't wait any longer and called a technician - please process a refund / thank you
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a totaline p474-1035. Fan stops running after two
I have a totaline p474-1035. Fan stops running after two seconds in the fan auto postion. It works fin in Fan on. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am trying to troubleshoot my outside HVAC. It is a TRANE
Hi. I am trying to troubleshoot my outside HVAC. It is a TRANE system. There is a slow green flashing led on it, but the unit does not engage (no compressor, no fan). I have just replaced the capacito… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I replaced my old thermostat with the honeywell RTH111
i replaced my old thermostat with the honeywell RTH111 series. now the fan moter wont come on in the auto or the on position. the thermostat says cool on but no fan. if i switch it to heat the ac cool… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Replaced my old round thermostat with a Honeywell RTH 9580
Hi Replaced my old round thermostat with a Honeywell RTH 9580 wf. Connected the wires to the same similar terminals as the old. Worked yesterday. Set up a schedule. Came in this morning and the fan wo… read more
airheatman
airheatman
HVAC Technician
9,195 satisfied customers
My Honeywell programmable 8120 thermostat has a red blinking
My Honeywell programmable 8120 thermostat has a red blinking snowflake on top right corner. I have a York infinity 8 heat pump, and the temp outside dropped to 2 yesterday. I followed the reprogrammin… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
York heat pump is flashing 7 times indicating ambient sensor
York heat pump is flashing 7 times indicating ambient sensor fault.I turned the system and breakers off trying to reset the system.It did not work.I replaced the ambient sensor and I am still getting … read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
How to replace a 6 wire thermostat with a 5 wire Honeywell thermostat
How do replace on old 6 wire thermostat, with a Honeywell (5) wire thermostat. The extra wire is orange Honeywell Model is a Th5110D… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
since installing new thermostat,the blower does not come on
since installing new thermostat,the blower does not come on with central air. I have oil heater.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We had a power outrage last night. This morning, after power
We had a power outrage last night. This morning, after power came back up, I went to re-program the thermostat , but it read "battery low". When I open to replace battery, there were no batteries!!! I… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I recently purchased a Honeywell RTHL2310/RTHK221 series digital
I recently purchased a Honeywell RTHL2310/RTHK221 series digital thermostat to replace my old mercury one. I have an incredibly simple hot water furnace-only system with just a ground and a hot lead. … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We purchased a Honeywell 3000 series thermostat for our new
We purchased a Honeywell 3000 series thermostat for our new 2.5 ton Goodman heat pump and wonder if we could have some advice regarding installing the thermostat. Seems the wiring diagram to the heat … read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
1,019 satisfied customers
we have a carrier 58mcb in a new home the fan/blower is on
we have a carrier 58mcb in a new home the fan/blower is on 24/7 i had a repairman out and he said theres no timer so the blower will always be on Is this correct,its a nuisance to hear it blowing at n… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a ritetemp 6020 with a trane heat pump. If I want heat
I have a ritetemp 6020 with a trane heat pump. If I want heat I have to turn the switch to heat and fan, the auto does not work. I put it on auto it will run about 2 minutes and shutoff. AC is fine wi… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
honeywell focus pro 6000 series with yellow,white,green,blue,red
honeywell focus pro 6000 series with yellow,white,green,blue,red what wires connect to carrier a/c unit wires yellow with blue stripe and brown with yellow stripe… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Trane AC stopped working. I opened the panel door under
My Trane AC stopped working. I opened the panel door under the furnace and noticed that 2 LEDS (green & red) are flashing. Is there anything I can do so the unit will work?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
HVAC Question-I have a duplex property with split system electric
HVAC Question-I have a duplex property with split system electric heat air handlers and electric condensing units. Late last fall both condensing units compressors stopped working. I though I would wa… read more
Paul
Paul
Vocational, Technical or Trade Scho
108 satisfied customers
I have an LG LSP122T-5 split air conditioner. What is the
I have an LG LSP122T-5 split air conditioner. What is the electrical connection between the indoor and outdoor unit like. The manual shows a 3-wire cable, the unit has a 5-wire terminal. I think a spl… read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
My Trane EX 80 was working OK until I cleaned the filter. I
My Trane EX 80 was working OK until I cleaned the filter. I replaced the covers and followed the startup procedure but cannot get the unit to work. Everything seems normal incl seeing the ignition lig… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x