I have a Coleman T.H.E. 90 furnace, model 2970E766. A couple of days ago, the high speed blower wire (black) at the blower relay melted. I replaced it with a new 1/4 female blade terminal. Now the red wire at the relay that supplies the 120 volts melted at the relay terminal. This would suggest excess current draw but the blower motor runs smoothly and the fan blades rotate freely. Help!

Contractor's Assistant: Did you check the furnace's filters?

Yes, first thing I did was to clean it

Contractor's Assistant: Do you plan on doing the work yourself?

For now, yes

Contractor's Assistant: Anything else we should know to help you best?

The furnace is 26 years old.

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
11/14/2017
HVAC Technician: airheatman, HVAC Technician replied 8 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,181
Experience: Furnace, A/C and heat pump specialist.
Verified

If amp draw is not high replace the relay. Overheating wires are caused by one of two things. Loose connections or high amp draw. The contacts inside relay are most likely not making good contact inside relay

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I checked for voltage drop across the relay and got zero voltage drop
Customer reply replied 8 months ago
the connection is good. What next?
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,181
9,181 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
On a Goodman ARUF182416BA air handler the blower motor drops
On a Goodman ARUF182416BA air handler the blower motor drops out at intermittent times but only when the T 87 thermostat is in auto mode and the compressor is on. It NEVER drops out with the compresso… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have added in-line duct fans to help boost air flow to the
I have added in-line duct fans to help boost air flow to the second story of my house. Right now they are just running continuously. How can I hook them up to run when my HVAC blower runs?… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
My Coleman Evcon furnace is set up for propane. When it first
My Coleman Evcon furnace is set up for propane. When it first kicks on the evac blower comes on, the ignitor element comes on, propane ignites and runs for a few minutes. A relay clicks, but the blowe… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
my evaporator froze up completely while away for weekend, and
my evaporator froze up completely while away for weekend, and now the blower in the air exchange will not go on.... do you know if there is a separate fuse or breaker within the unit?… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have a bryant plus 90 model ck5a, the blower is inop, although
I have a bryant plus 90 model ck5a, the blower is inop, although i hear a high pitched noise coming from furnace… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
coleman furnace 6806 (1970s) connection point for 110vac
coleman furnace 6806 (1970's) connection point for 110vac fan cycle, electronic air cleaner addition.… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a ten year old Luxaire furnace, the control board was
I have a ten year old Luxaire furnace, the control board was blinking four times indicating the high temperature limit switch. So, I reset the limit switch and the burner came on successfully but when… read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
New furnce and heat pump were installed in March of 09. Have
New furnce and heat pump were installed in March of 09. Have a Trane XR 13 Heat pump. Furnace label says International Comfort Products model FSM2X3600A1. Thermostat is set at 70 and it's 76 inside an… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
please show me a drawing wireing diagram on how to wire a duct
please show me a drawing wireing diagram on how to wire a duct detector sensor (system sensor)to a thermostat terminals on the thermostat are RH, RC, Y, O, C, G , ritetemp thermostate brand… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I will like to know how to wire the 24 volts from the secondary
I will like to know how to wire the 24 volts from the secondary side of the transformer to the normally open and Normally closed relay. I know that the 120 volts is staged down to 24 volts for control… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
I have a Coleman T.H.E. 90 Furnace when heat is called for
I have a Coleman T.H.E. 90 Furnace when heat is called for the hot surface ignitor glows the gas valve clicks as if it's opening but burner doesn't light… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
I have an Amana Air Command 80 furnace, model GUI115B35B.
I have an Amana Air Command 80 furnace, model GUI115B35B. Several years ago, a tech asked if I wanted the fan speed boosted to improve warm air circulation. I said "Sure" and it sounds like I've had a… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
The control board in my Trane condensing type furnace fried.
The control board in my Trane condensing type furnace fried. The failure occured at the high voltage terminals for the fan wiring. The board was last replaced in March of 2008 after a similar failure.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
What is the proper way to wire in a humidifier to a G7TC My
What is the proper way to wire in a humidifier to a G7TC? My old furnace would power the humidifier transformer when the blower ran but I am not clear where I should wire the transformer. My furnace i… read more
DanielC
DanielC
Service manager
High School or GED
95 satisfied customers
Heater Limit Switch location on Coleman Evcon Presidential
Heater Limit Switch location on Coleman Evcon Presidential EB15A electric furnace ? Thanks , Dan… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
hi, I have the g 16 series gas unit with air conditioning,
hi, I have the g 16 series gas unit with air conditioning, my 120 to 24 vac transformer keeps burning out, I accidentally put the 120 wire on the 24v side of the blower relay, now Im not sure what par… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have a Ruud Silhouette II and it quit running a while ago.
I have a Ruud Silhouette II and it quit running a while ago. The ok light blinks 5 times and then repeats. I have checked the outside unit and it runs fine, and I put a different t-stat on and it made… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a lennox furnace and I connected wires from my t-stat
I have a lennox furnace and I connected wires from my t-stat to the furnace. I ran a red wire to R from the t stat to the furnace, and a white wire to the W from the t stat to the furnace, and I ran a… read more
Rick or Nick in Texas
Rick or Nick in Texas
General Manager-Lead Tech
Own and run HVAC business 29yrs
44 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x