There is no hot air blowing out of your vents. Heat is set…

Customer Question
There is no hot...

There is no hot air blowing out of your vents

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Heat is set for 62 and has been for a few days but the thermostat will not get above 54

Contractor's Assistant: Do you plan on doing the work yourself?

If the fix ends up being simple than yes, if not than no

Contractor's Assistant: Anything else we should know to help you best?

Rheem classic 90

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
11/13/2017
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,414
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

What is the model number of your unit? It on the rating tag inside the burner compartment

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Hold please i am checking
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

ok

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Would it say p/n?
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

It will start with 4 letters. The first letter is an R

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I do not see the model #
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

I'm going to open this up to my colleagues so one of them can help. Please don't respond (even to acknowledge this post)until you get a response from us. If you respond first it will only delay your answer.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Rheem RRNA-Bo36JK08E not blowing hot air. Fan and A/C works
Rheem RRNA-Bo36JK08E not blowing hot air. Fan and A/C works but no air on heat. Outside unit turns on but blows no air through inside vents … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My Rheem Classic 90 plus fan won't run in ON mode. It will
My Rheem Classic 90 plus fan won't run in ON mode. It will run in AUTO when heating and cooling. What do I look for… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Honeywell CT87N that I tried to connect up to my
I have a Honeywell CT87N that I tried to connect up to my Carrier 58MCA, but it keeps blowing the fuse on the furnace controller. … read more
Charles Bodenheimer
Charles Bodenheimer
Owner
Associate Degree
78 satisfied customers
Our Honeywell VisionPro TH8110 (or could be TH8320 or
Our Honeywell VisionPro TH8110 (or could be TH8320 or TH8321) thermostat is under-heating our home We have the temperature set for 68. The gas furnace (about 10 years old) calls produces heat when cal… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have Totaline model # P474-2300 REC and Totaline wireless
I have Totaline model # ***** REC and Totaline wireless transmitter P474-1100 RE. These were here when I purchased the home. Everything has been working since December 2015 and I have a temperature of… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Outside compressor blowing cool air. Inside temp set at 70
Outside compressor blowing cool air. Inside temp set at 70 on thermostat but won't go below 72. It has been in the mid 70's outside. The temp at vent outlet is 62? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
, just saw the link while researching. Happy you are here.
Hi, just saw the link while researching. Happy you are here. Hope all is well at your end. Probably something very simple to you, but this woman turned in her tools and decreased DIY activities a few … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have a Lennox ML195UH and it is flashing 3 times
We have a Lennox ML195UH and it is flashing 3 times indicating "pressure switch open with combustion air inducer engergized." What does this mean and is it a simple fix we could do by resetting the ma… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Should the outdoor compressors come on one the heat is turned
Should the outdoor compressors come on one the heat is turned on in the house? Currently they are not running, but the heat is on and it is blowing mostly cold air.… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Hi, I have a Rheem 90 Classic Plus furnace. I am not seeing
Hi, I have a Rheem 90 Classic Plus furnace. I am not seeing any ignition, partial or temporary, when I turn on heat. Blower turns on, and at times will remain on for an extended period of time blowing… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
Hi: the home I recently purchased has a Rheem Classic High
Hi: the home I recently purchased has a Rheem Classic High Efficiency OBF Upflow oil fired furnance. I've noticed that when the t-state calls for heat the zone panel on the furnace blinks cold and the… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a rheem raka-030jaz model unit. The Unit is AGAIN
I have a rheem raka-030jaz model unit. The Unit is AGAIN blowing out warm air. Approximately 31 days ago it did this and it ended up being just a fuse replacement. I tried that this time and no luck o… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
I have a Totaline wireless thermostat (P474-1100RF) that controls
I have a Totaline wireless thermostat (P474-1100RF) that controls our upstairs heat pump. Recently, when the exterior heat pump turns off, the fan continues to run resulting in cold air being blown in… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
The air that comes out of my vents is 70 degrees consistently
The air that comes out of my vents is 70 degrees consistently even though the booklet says it should be between 90 and 105 degrees. The filters have been cleaned regularly. Is it the battery in the ca… read more
Tim H.
Tim H.
Lead building engineer
Vocational, Technical or Trade Scho
3,962 satisfied customers
I have a ranch home with the heating and air conditioning duct
I have a ranch home with the heating and air conditioning duct work running through the attic. The house never seems to get to temperature even with the heater running for over an hour. My x-husband u… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
Why would my Rheem heat pump blow cold air when set to heat?
Why would my Rheem heat pump blow cold air when set to heat but blow hot when the aux heat kicks in?… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
I have a Rheem Classic 90 Plus furnace. The A/C and the heat
I have a Rheem Classic 90 Plus furnace. The A/C and the heat is off but it is still blowing air. I turned the controls at the TSTAT off and it still blows, any ideas?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a 3 yr old Rheem classic 90 gas furnace. Today it is-5
We have a 3 yr old Rheem classic 90 gas furnace. Today it is-5 below zero with a wind chill of -32. The house will only go to 62 degrees with the termostat set at 75. What gives?? The people who just … read more
coolman1973
coolman1973
AC/Heat Tech
Vocational, Technical or Trade Scho
162 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x