I have a wiring issue. I’m going from a digital back to

Customer Question
Hi I have a...

Hi I have a wiring issue. I’m going from a digital back to analog. The way it was wired on digital was Y1 had yellow (with a jumper to W1), Rc had red wire (with jumper to Rh), G was green wire and W

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

Sorry white wire went to

Contractor's Assistant: Do you plan on doing the work yourself?

Today

Contractor's Assistant: Anything else we should know to help you best?

Sorry yes the white wire went to O. ??? The a/c works fine but when I connected White wire to W instead of O in the analog thermostat the a/c and heat came on together and a/c alone didn’t work?

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Yes.

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 5 minutes by:
11/13/2017
HVAC Technician: HVAC Guru, HVAC TECH replied 10 months ago
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,886
Experience: 20yrs in the HVAC industry with certificates and degrees.
Verified

Hello, one minute while I get some information together. Note it takes time to type so please be patient.

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 10 months ago

The yellow wire should go to Y by itself no jumper and White should go to W by itself no jumper try that and it should work.

All I ask is please select the 5 STAR rating at the top of your page before leaving otherwise I receive ZERO credit for assisting you. Thanks and you can come back anytime for free followup questions.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
I did try that. I recognized and have read up on it that’s why I’m asking for help.
HVAC Technician: HVAC Guru, HVAC TECH replied 10 months ago

OK so you have RH to R jumpered which is right, you should just have Y to Y and W to W do you have a HEAT PUMP?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
On digital:
Green wire -G
Red wire- arc (jumper to Rh)
Yellow wire- Y1 (jumper to W1)
White wire- O
I hooked wires to analog like you said.
Y-yellow
W-white
G-green
Really-red with jumper to rh.
Neither just a/c OR HEAT CAME ON SEPERATELY. So I connected white to O and a/c works only?
Customer reply replied 10 months ago
I don’t believe it is. There’s a compressor outside and a unit in attic
HVAC Technician: HVAC Guru, HVAC TECH replied 10 months ago

Ok you have a heat pump if anything was connected to O on the old one. If that is the case does your analog have an O terminal?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
I have white to it. Ac works heat doesn’t
Customer reply replied 10 months ago
I need to put a jumper for W and Y ?
HVAC Technician: HVAC Guru, HVAC TECH replied 10 months ago

Disconnect that WHITE wire from the Y terminal that should not be there..

Ask Your Own HVAC Question
Customer reply replied 10 months ago
It’s from the board. Do I connect it to white then?
HVAC Technician: HVAC Guru, HVAC TECH replied 10 months ago

Is that going to RC? The white wire?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
No it’s going to Y. That’s how it was originally connected
Customer reply replied 10 months ago
I put that blue jumper between rev and rh.
Customer reply replied 10 months ago
Arg Rc and Rh
HVAC Technician: HVAC Guru, HVAC TECH replied 10 months ago

Take that out and see if they both do not come on. DO you have the make and model?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Roberthaw sb-4a-5aj
Customer reply replied 10 months ago
That’s theromastat. Came with house we rent. Cox put in digital and need to replace analog cuz were moving
HVAC Technician: HVAC Guru, HVAC TECH replied 10 months ago

OK great now when you select heat it does nothing only cools correct?

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 10 months ago

Does it only cool, no heat correct?

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 10 months ago

Put a jumper from Y to W what happens?

Ask Your Own HVAC Question
Customer reply replied 10 months ago
I took white wire from board that was connected to Y where yellow wire is and ac doesn’t work again and nothing happens on heat.
Customer reply replied 10 months ago
Ok so I’m gonna hump w and yellow with that white wire not connected now
HVAC Technician: HVAC Guru, HVAC TECH replied 10 months ago

Yes correct and leave your White wire on O

Ask Your Own HVAC Question
HVAC Technician: HVAC Guru, HVAC TECH replied 10 months ago

That should work, if not let me know

All I ask is please select the 5 STAR rating at the top of your page before leaving otherwise I receive ZERO credit for assisting you. Thanks and you can come back anytime for free followup questions.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Auto doesn’t work and on ON compressor outside wont come on
Customer reply replied 10 months ago
Have Luke warm smelly air
Customer reply replied 10 months ago
Wait
Customer reply replied 10 months ago
Compressor came on. Have ac let me check heat
Customer reply replied 10 months ago
Ok auto doesn’t work and no heat
Customer reply replied 10 months ago
Nothings on. That white wire that’s on the board is also shown on the picture of this specific thermostat and it’s connected to the yellow too
Customer reply replied 10 months ago
That didn’t work
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask HVAC Guru Your Own Question
HVAC Guru
HVAC Guru
HVAC Guru, HVAC TECH
Category: HVAC
Satisfied Customers: 18,886
18,886 Satisfied Customers
Experience: 20yrs in the HVAC industry with certificates and degrees.

HVAC Guru is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have an Amana (installation date 2009) heat pump (2-stage)
I have an Amana (installation date 2009) heat pump (2-stage) and I'm trying to determine if a Honeywell Lyric thermostat is compatible. The thermostat wires I have configured to digital thermostat are… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Need assistance with a couple wires and a config option on
Need assistance with a couple wires and a config option on honeywell HZ322 zone controller… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am replacing a Honeywell LR1620 thermostat with a new RTH6350.
I am replacing a Honeywell LR1620 thermostat with a new RTH6350. The old unit has a yellow wire connected to the K terminal, then on to W2. The new unit has no K terminal. How should I wire the new un… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Ok i have a payne module #pf1mnc061and im takeing off honeywell
Ok i have a payne module #pf1mnc061and im takeing off honeywell pro th3000 . E and aux are jumpered together and white goes to aux. Y=yellow g=green o=orange r=red c=black i dont think black needed to… read more
joeydelia
joeydelia
HVAC-R Tech
High School or GED
81 satisfied customers
We are installing a new thermostat for the furnace. A Honeywell
We are installing a new thermostat for the furnace. A Honeywell Model # ***** We put in a new wire and it is a bit different from the old. The old wires were White, Green, Red, Blue with the blue wire… read more
warmneighbor
warmneighbor
owner
Vocational, Technical or Trade Scho
9 satisfied customers
old thermostat is TA32H01 on a water furnace it is using C
old thermostat is TA32H01 on a water furnace it is using C R L G O W Y1 my new tstat is a nest it has different hookups wondering which one to use? on the nest it has Y1 Y2 G ob Rc W1 W2aux C * Rh… read more
Scott
Scott
Self Employed HVAC Service Technician
Associate Degree
400 satisfied customers
I just bought a ADMH110 Series. I am replacing a totaline energy
I just bought a ADMH110 Series. I am replacing a totaline energy star. For the wiring on the totaline the wire connectings are as follows, R- red, G-green, Y1- blue, W2- no wire, W1- white( also has a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier Performance Series TP-PHP Thermostat wired
I have a Carrier Performance Series TP-PHP Thermostat wired as follows: Wire Color - Terminal Blue - OAT Brown - SRTN Red - Rh White - W/W1 Green - G Yellow - Y/Y2 Black - C Orange - O/W2/B I want to … read more
servtech50
servtech50
HVAC/R service tech
216 satisfied customers
I am replacing a Trane thermostat (XT302B) with a 3M Filtrete
I am replacing a Trane thermostat (XT302B) with a 3M Filtrete (3M-50). The Trane is connected (R-Red) (B-Blue) W1(White) W2(Black) (Y1-Yellow) (G-Green). The new thermostat has: C - B - O - W - W2 - Y… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Im replacing a Trane Weathertron with a new Hunter 44860.
I'm replacing a Trane Weathertron with a new Hunter 44860. The Weathertron is configured as follows: R - Red O - Orange G - Green Y - Yellow X2 - Black B - Blue U - Light Green (U and W are jumped tog… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
RS5110 2T thermostat wiring. I have an OLD thermostat.
RS5110 2T thermostat wiring. I have an OLD thermostat. 1970s? Wiring: Green, white, red & yellow codes. (Green post has a blue wire but I'm sure that's irrelevant. Just the rubber.) The Robt Shaw does… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am converting from a Weathertron thermostat to a Hunter model
I am converting from a Weathertron thermostat to a Hunter model 44860. The Weathertro was wired as follows: X2- Black O - Orange G - Green Y - Yellow W - White R - Red B - Blue the Brown wire was not … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Hello Presently I have a heat pump furnace and Im trying
Hello XXXXX have a heat pump furnace and I'm trying to change a "Water Furnace" thermostat with a Honeywell RTH8500. Presently the Water Furnace has this configuration R Y/Y2 G C W/W1 O/W2 Y1 L The Ho… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I am trying to install a white rodgers 90 series blue 1f95-1277,
I am trying to install a white rodgers 90 series blue 1f95-1277, but I am clueless as to what to do… read more
Heath
Heath
Vocational, Technical or Trade Scho
1,002 satisfied customers
I just bought a hunter 44155c and I am confused with the wiring.
I just bought a hunter 44155c and I am confused with the wiring. I have the following wires comming out of the wall: Green Red Orange Yellow White Black Blue The thermostat has the following connectio… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I just bought a Hunter thermostat model 44360. My old one has
I just bought a Hunter thermostat model 44360. My old one has this for wiring wire color hooked to Orange O/W2 red R yellow Y/Y2 green G gray C white W/W1 The new Hunter has these terminals G, RC, RH … read more
ComfortZone
ComfortZone
Associate Degree
485 satisfied customers
I am having trouble with wiring a Hunter 44668 thermostat to
I am having trouble with wiring a Hunter 44668 thermostat to a Trane Heat Pump. My wire colors are green, white, yellow, blue, brown, red and connections are G,W/B,Y/O,RC,RC1,RH,Y1. Can you please hel… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I have the th4110d1007. I have a master slave. Wires are
I have the th4110d1007. I have a master slave. Wires are RH, W1, Y1, B, O and G. How do I wire?… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x