G9MXE0601714-A1 Blower on at power up, then shuts off, then inducer comes on, ignition starts, then blower comes on 3-4 minutes later flames shut off, then inducer starts ignition up n cycle again. Does this 3 times then I get error code 3. I have checked drainage, vent piping, pressure switch hoses, replaced pressure switch (part #(###) ###-#### Still doing same thing. Faulty circuit board?

Contractor's Assistant: How old is the appliance? Have you gotten error messages before?

Manufactured 2013.

Contractor's Assistant: Do you plan on doing the work yourself?

2013

Contractor's Assistant: Anything else we should know to help you best?

Yes

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 hour by:
11/13/2017
HVAC Technician: airheatman, HVAC Technician replied 8 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,213
Experience: Furnace, A/C and heat pump specialist.
Verified

I recommend getting a manometer and verifying that we are actually getting and keeping proper vacumm on the pressure switch .Must stay within .05 of the wc rating on switch.

Sounds like you have already addressed the most common causes if poor vacuum.

If drains are clear, hose not cracked or blocked, or vent not obstructed the only other causes are more serious like a defective inducer motor or wheel not moving fast enough or broken blade or a defective heat exchanger.

If you can verify vacuum is indeed within parameters. then replace board.

If you have further questions, please let me know.

Thanks for letting me work with you.If my answer has been polite, professional,and thorough, please click one of the ratings before you go. If you still need help let me know!.Expert is not paid for assisting you until you rate answer.Feel free to follow up for 30 days at no additional cost. Bonus always appreciated if you feel justified.

To rate answer, please select one of the stars on the page.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,213
9,213 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
My ducane furnace,inducer comes on, it lights, blower comes
my ducane furnace,inducer comes on, it lights, blower comes on. then shuts off after a few minutes. then inducer comes on after a bit but it doesn't stay on long enough to light. seems if I shut off t… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
I have a furnace that will blow air but not heat it. There
I have a furnace that will blow air but not heat it. There is an E2 code flashing on my unit (Amana - about 5 years old). I changed the filter (old one was not plugged with dirt) and still get the E2 … read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
My furnace fan kicks on after reset (or if I force heat on
My furnace fan kicks on after reset (or if I force heat on from thermostat) but heat never kicks in… read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
Trane xv90 Replaced inducer and control board with kit
Trane xv90 Replaced inducer and control board with kit #16582 on Dec 31st 2015. Unit stopped running on 1-20-16. Inducer blower would not switch on. Internal error code. Just replaced with another boa… read more
heatncoolrepair
heatncoolrepair
Former HVAC Service Technician
Vocational, Technical or Trade Scho
75 satisfied customers
My gas furnace is blowing cold air, the burner unit isn't lighting.
My gas furnace is blowing cold air, the burner unit isn't lighting. Checked thermostat settings, everything is OK. All breakers are on and power is getting to the package unit. I've tried resetting th… read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
We have had snow freezing temps in colorado the past 2 days
We have had snow freezing temps in colorado the past 2 days (-1 this am) woke to thermostat reading 44. Checked furnace and black circle thing was rotating very slowly. I went through process of dropp… read more
Joe Chappell
Joe Chappell
Building Engineer
7 satisfied customers
Make : UPG/YORK Model : g8c/fg8 control panel status light
Make : UPG/YORK Model : g8c/fg8 control panel status light blinking 3 times. pressure switch not closing. Whats next step?… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
I have a luxaire furnace that wont light. If remove the 2""
I have a luxaire furnace that won't light. If remove the 2"" pvc pipe just above the powervent it will light. When I reinstall the pipe it will not light. I checked the entire run of the 2'' pvc pipe … read more
airheatman
airheatman
HVAC Technician
6 years college
9,213 satisfied customers
I have a Thermal Zone forced air furnace. It runs perfectly
I have a "Thermal Zone" forced air furnace. It runs perfectly for 5-10 minutes on an initial cold start( I shut it off for an hour or longer) then after that it occasionaly will make it through a whol… read more
MRANSWER
MRANSWER
TECHNICIAN
Bachelor\u0027s Degree
6,158 satisfied customers
we have a Carrier 58mya080 furnace serial #0398a003a get codes
we have a Carrier 58mya080 furnace serial #0398a003a get codes 12 and 13. At call for heat, pre blower comes on for 90 seconds, no gas, no ignition, especially on damp days after heat not used for day… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Bryant furnace is not putting out warm air. I just went
My Bryant furnace is not putting out warm air. I just went and looked at the RED LED status light and it was blinking. After removing both panels and then replacing the top panel, the light remained o… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Payne PG8UAA060135ABJA furnace where the big blower
I have a Payne PG8UAA060135ABJA furnace where the big blower fan comes on instead of the litter exhaust fan that generally comes on just before ignition. What should I do to trouble shoot?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a carrier model 58PAV135-20 furnace. It wont start
I have a carrier model 58PAV135-20 furnace. It won't start and the LED appears to be flashing a code (2 short flashes followed by 4 long flashes). Is there a place online that describes these codes?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
MY RHEEM FURNACE COMES ON BUT WILLNOT IGNITE. I TURN IT ON
MY RHEEM FURNACE COMES ON BUT WILLNOT IGNITE. I TURN IT ON THE SMALL FAN RUNS ,THEN AFTER ABOUT A MINUITE SHUTS OFF AND GREEN LIGHT FLASHES TWICE STOPES THEN FLASHES TWICE (KEEPS ON FLASHING TWICE).… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Having a problem with a XV90. There is a call for heat the
Having a problem with a XV90. There is a call for heat the inducer motor starts then the system fires up but then shuts down in 10-15 seconds. There are no alert lights flashing only the steady red fl… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Im getting a three red LED flashing error signal and the furnace
I'm getting a three red LED flashing error signal and the furnace revs up to start, then stops and starts over again. I have a Trane xv90… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,349 satisfied customers
I have a carrrier furnace model vcl024 with code 34.. please
I have a carrrier furnace model vcl024 with code 34.. please advise on a possible fix b4 calling a pro. Its 30 degrees outside 64 inside..ederly mom is cold... please help… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
Hi there, I have a Carrier Weathermaker 8000. From 1994.
Hi there, I have a Carrier Weathermaker 8000. From 1994. My LED diagnostic light is blinking but I do not have an error code legend on my furnace, so I do not know what the flashes mean. Help!… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.