I have a NTI- TRINITY Ti150 boiler that shuts down after…

Customer Question
I have a NTI- TRINITY...
I have a NTI- TRINITY Ti150 boiler that shuts down after starting with an error 1 code? there is no power to circulation pump so boiler shuts down, for reaching max temp in heat exchanger. What do i need to check to find problem?
thanks derek
Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 11 minutes by:
11/12/2017
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,418
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. First I’ll need some more info so I have a more complete picture of your situation.

Are you talking about the system pump that circulates water through the house? If so what do you have for a relay controlling that pump? brand & model please?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
no relays, the boiler runs power to circulation pump when a zone commands the boiler to produce heat. circulation pump is in line 3 feet from boiler. there are no circulation pumps inside of boiler housing. there is a power supply running from boiler controller to circulation pump
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

You should have 2 pumps a boiler pump and a system pump. Manufactuere's install instructions require 2 pumps. Are you saying you only have 1 pump?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
it has 7 pumps total, with all the zones, but whatever that boiler does to command on pump to circulate out of boiler is not sending power out, so since heat is not being removed from boiler chamber it shuts down boiler
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

That's not how it works. The boiler circ is there to moderate (warm up) the cold return water temp before it gets to the boiler which could shock the boiler. The boiler loop pump should run as long as there's a call for heat except if there is a priority call for DHW assuming you don't have a separate indirect fired water heater. If there is no call for hot water and there is no power to the boiler pump then you either have a bad connection or a bad control board.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Have an 11 year old NTI TRINITY 150. ASC code. 12 hrs. I've
yes. Unless it gets over my head. I installed the unit … read more
Rick
Rick
HVAC Supervisor
24,418 satisfied customers
I have a trinity NTI boiler that will not kick on, but
I have a trinity NTI boiler that will not kick on, but showing a flashing error code of "att" and the number of 7 … read more
Rick
Rick
HVAC Supervisor
24,418 satisfied customers
Have a Tekmar 363. Three questions. 1) If Boil Max is 180
Have a Tekmar 363. Three questions. 1) If Boil Max is 180 and Boil Diff is "x" will Boil Supply rise to 180+x, drop to 180-x, rise to 180+x, etc as boiler cycles? 2) Can Boil Supply go above the boili… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I am trying to determine what a normal setting is for the
I am trying to determine what a normal setting is for the weil mclain Gold gas boiler water temprature limit switch is? … read more
Rick
Rick
HVAC Supervisor
24,418 satisfied customers
I have a Trinity Tft85 boiler that is fouling the flame rod.
I have a Trinity Tft85 boiler that is fouling the flame rod. I had a craigslist guy come over and he told me that the boiler was not installed correctly. It was not installed in a primary/secondary co… read more
Rick
Rick
HVAC Supervisor
24,418 satisfied customers
I have a Trinity Ti150 boiler installed 10 years ago and am
I have a Trinity Ti150 boiler installed 10 years ago and am getting an ER1 message. Boiler hasn't been running most of the night so I know it isn't too hot right now. All circulation pumps appear to b… read more
Rick
Rick
HVAC Supervisor
24,418 satisfied customers
I have a Weil McLain gas-fired boiler controlled by a Tekmar
I have a Weil McLain gas-fired boiler controlled by a Tekmar 371, including a DHW loop. The house gets cold when the outside temp drops and especially when the wind blows - seems like the system can't… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Phil: I have a Weil Mclain boiler and my thermostat is set
Phil: I have a Weil Mclain boiler and my thermostat is set at 75, but unit shuts off at 70 and the circulating pump keep running. The house does not seem to be 70 degrees but my thermostat for my furn… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Buderus GB 142/60 seems to overheat in DHW mode. When activated
Buderus GB 142/60 seems to overheat in DHW mode. When activated boiler temp will quickly increase to OY code before heating stops. It will refire when the reading is in the 140-150 range and keep repe… read more
Rick
Rick
HVAC Supervisor
24,418 satisfied customers
NTI Trinity Ti150. Boilers fires up, heats for a minute, then
NTI Trinity Ti150. Boilers fires up, heats for a minute, then flashes error code of E2.2 and shuts off, even the display goes off. A few minutes pass and display lights up and repeats the same sequenc… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have had a Laars Endurance combi boiler for over 10 years.
I have had a Laars Endurance combi boiler for over 10 years. Recently I have noticed that the boiler continues to run after the call for heat from the thermostat has been satisfied. Under normal opera… read more
Appliance Guru
Appliance Guru
18,166 satisfied customers
I have a G124X II boiler w/HS 2105 controller. During the current
I have a G124X II boiler w/HS 2105 controller. During the current cold wave in the NE, low OA temps in 5-10F range, after the house warms up to thermostat day settings, the manual hi temp reset (STB) … read more
Appliance Guru
Appliance Guru
18,166 satisfied customers
We have a oil boiler/furnace that heats our water and heats
We have a oil boiler/furnace that heats our water and heats the house. It has worked fine this whole season until this morning there was just cold air coming out of the vents. The circulator cartridge… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
i have the trinity t150 boiler. it produces hot water for the
i have the trinity t150 boiler. it produces hot water for the heat but tepid water for my shower why?… read more
Rick
Rick
HVAC Supervisor
24,418 satisfied customers
I just hooked up a Buderus 142-60 with a propane conversion
I just hooked up a Buderus 142-60 with a propane conversion kit. the unit fired up fine and heats the water for my hydro-air system, but when it gets to 130 degrees it shuts down with Y0 code and an F… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
HI there, i have a baxi bahama 100, for both heating and hot
HI there, i have a baxi bahama 100, for both heating and hot water the boiler switches on fine and make hot water, but switches off after approx 15- 30 seconds. if you switch of and reset it will do t… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
Im having an issue with an NTI Ti150 Combi-boiler. The unit
I'm having an issue with an NTI Ti150 Combi-boiler. The unit was working fine until, one day, we lost all hot water. We continue to have flow, but no heat. No error codes displayed on the Sentry contr… read more
Plumbing Pro
Plumbing Pro
Licensed Plumbing Contarctor
Vocational, Technical or Trade Scho
1,279 satisfied customers
I have a boiler hot water base board heating system. Every
I have a boiler hot water base board heating system. Every time the circulating pump shuts off, my pipes bang enough to wake you up at night.… read more
Rick
Rick
HVAC Supervisor
24,418 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x