I have two Trane XE80's (side by side) in a new house I

Customer Question
I have two Trane...

I have two Trane XE80's (side by side) in a new house I moved into this summer. About two weeks ago, I opened them up to check the filters; all burners in both units were on. A couple days later, I changed the filters (after receiving mail order). none of the burners were on, but the house was at the right temp. These past few days are the first below 40 degrees. I noticed this morning that the house was at 60, and it was set at 64 overnight. i checked, and none of the burners are on. i have a nest thermostat that i installed several months ago. i "reset" the burners (turned down thermostat, turned off electricity, turned off gas to the units, waited 15 minutes, turned on the gas, turned on the electricity, turned up the thermostate). the blowers go on, but do not light. i do not see any glow from the hot surface ignitor. at a loss for what to try next!

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

The thermostat seems to be telling the system to go on and off at the right times. the blowers go off when i turn thermostat down, and go on when i turn the thermostat up. it's just that the burners aren't lighting.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes if possible

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
11/12/2017
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,401
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your

issue. First I’ll need some more info so I have a more complete picture of your situation.

What are you getting for a flash sequence on the contrl board LED? You should be able to see it through the viewing port in the blower access panel without removing the panel.

Ask Your Own HVAC Question
Customer reply replied 8 months ago
the red LED light is blinking steadily, about twice per second. per the board, that means no issues.
Customer reply replied 8 months ago
uploading pictures
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

If it's a steady blink not a 2 flash them pause then 2 flash then you have no call for heat being recognized by the unit. This could be a thermostat or thermostat wiring issue

Ask Your Own HVAC Question
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

ok

Ask Your Own HVAC Question
Customer reply replied 8 months ago
the inside of the unit has the codes - it says "flashing slow - normal - no call for heat" and "flashing fast - normal - call for heat"i turned thermostat down, and it was blinking roughly one every .75 seconds. when i tuned it up, it did not change. i'll take a picture of the thermostat wiring. when i installed the nest, there was a little hesitance because i have a heat pump system (also have two XE1000 units ouside). but as i said, everything seemed to be working fine. going to shut things down so i can open up the thermostat now.
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

Could be an open short in the thermostat wiring. You can confirm this immediately by jumping the R & W terminals on the furnace thermostat terminal strip. Be sure the blower door switch is pushed in. When it powers back up does the furnace respond?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
ok. i don't have a jumper wire handy, but can run out and get. here's some add'l info; i'm still getting familiar with the house. the XE1000 units i have are heat pumps. they were not running this morning, but they just kicked on and the house is heating up. it's mid 40's outside. last night was in the low 30's, so suspect the XE 1000's went off, and there's some kind of issue with the gas furnaces. i'll run out and get jumper.i also re-acquainted with the nest. in addition to normal RGYW, there's an orange. that's currently plugged into the O/B terminal on the nest. the nest compatibility checker says my wires are compatible, but should be installed by an expert since it's a dual fuel system.
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

You can just use a piece of wire for a jumper. First mention of heat pumps which could affect things.

I'm going to open this up to my colleagues so one of them can help. Please don't respond (even to acknowledge this post)until you get a response from us. If you respond first it will only delay your answer.

Ask Your Own HVAC Question
HVAC Technician: airheatman, HVAC Technician replied 8 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,206
Experience: Furnace, A/C and heat pump specialist.
Verified

If you have a dual fuel system this requires special setup when using the Nest.I can guide you in setting up but am out of town until late tonight.My Nest manuals are all on my office computer.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
35 year old gas furnace just stopped running. I can
35 year old Bryant gas furnace just stopped running. I can hear/feel power to it. No fan, no gas valve, no igniter. Thermostat is calling for heat. … read more
airheatman
airheatman
HVAC Technician
9,206 satisfied customers
I have a newer keep rite gas furnace in my home in Cobourg,
Hi.... I have a newer keep rite gas furnace in my home in Cobourg, Ontario where it is currently minus 22 Celsius. In the past 12 hours the furnace keeps on cutting out after a few minutes of operatio… read more
airheatman
airheatman
HVAC Technician
9,206 satisfied customers
I don't know if you can see the screen I am reviewing. It
I don't know if you can see the screen I am reviewing. It concerns the same furnace I have - the Carrier WeatherMaster 8000 TS. I have had trouble with the furnace not lighting in the past and have re… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My Honeywell thermostat seems to be set properly, but the
my Honeywell thermostat seems to be set properly, but the heat will not come on? … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
Have a forced air furnace model# 394GAZ024050, temp wont
Have a Bryant forced air furnace model# ***** temp wont exceed 64 degrees F. no matter where thermostat is set … read more
Rick
Rick
HVAC Supervisor
24,401 satisfied customers
My furnace will run at proper temp for most of the night
my furnace will run at proper temp for most of the night then will slowly cycle down to 55 degrees the red lite is flashing a steady flash and it will light for a few seconds and then shut off ? … read more
Kcrand36
Kcrand36
Technician/Owner
Vocational, Technical or Trade School
72 satisfied customers
I have a carrier 8000TS 58UX furnace that has been off all
hello I have a carrier 8000TS 58UX furnace that has been off all summer. When we tried to turn it on it does the following (all see normal) 1. Blower starts 2. Igniter heats up 3. gas is produced and … read more
airheatman
airheatman
HVAC Technician
9,206 satisfied customers
MY Trane XE80 gas furnace blower continues to run after reaching
MY Trane XE80 gas furnace blower continues to run after reaching thermostat temp and the gas shuts off then it's blowing cold air unless I raise the temp on thermostat… read more
airheatman
airheatman
HVAC Technician
9,206 satisfied customers
i have a goodman gpg10300701A electric/gas unit. starting
i have a goodman gpg10300701A electric/gas unit. starting 3 days ago, the unit works fine in the morning, but at some point in the afternoon the fan shuts off. the blower continues to blow (air is com… read more
Will
Will
President
Vocational, Technical or Trade Scho
131 satisfied customers
I have a system that is controlled by a honeywell thermostat.
I have a system that is controlled by a honeywell thermostat. One day overnight the unit just stop cooling the house to the temperature that the thermostat was programed to. We have it set at 55 degre… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
bryant 90plus does not always start heating. i hear the blower
bryant 90plus does not always start heating. i hear the blower go on but it sometimes just stops. problem seemed to start earlier this week, then it was fine all week and i noticed an hour ago the the… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Goodman GMPN High efficiency (92%) gas furnace and
I have a Goodman GMPN High efficiency (92%) gas furnace and the blower is coming on when the thermostat is not telling it to do so. The burners do not light at this time. It will even come on when I h… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
this question is for oglesby i replaces the ignitor it was
this question is for oglesby i replaces the ignitor it was burned almost off it is srill doing the same thang. i have hat the ignitor for 2 days now it has went off on rollout once yesterday and once … read more
M Oglesby
M Oglesby
Vocational, Technical or Trade Scho
2,010 satisfied customers
Our furnace was working fine when we ran out of propane. After
Our furnace was working fine when we ran out of propane. After our propane tank was filled I relite the pilot light, turn the furnace to on. Everything seamed to be working fine until the temp. in the… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
My home central air conditioning compressor is running but
My home central air conditioning compressor is running but the vents in the house aren't blowing air. I just noticed it today. It has worked fine all summer. I did turn the circuit breaker off and bac… read more
THEFIXER1966
THEFIXER1966
High School or GED
12 satisfied customers
I have a Trane XE80 Gas furnace. The burner is short cycling.
I have a Trane XE80 Gas furnace. The burner is short cycling. When set to heat, the flue exhaust starts and in about 45 seconds the burner ignites. Approximately 1 minute later the blower motor comes … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
96 gmp gas furnace, been away for the weekend, held temp at
96 gmp gas furnace, been away for the weekend, held temp at 64. Came home, can't get the furnace to get back up to 68. Won't ignite. Reset thermostat, everything on the electrical end of the thermosta… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Carrier 58mxa 080-16 gas furnace. Installed 1/30/04.
I have a Carrier 58mxa 080-16 gas furnace. Installed 1/30/04. When heat is called for the hear goes on and the blower motor starts with 60 sec delay. The blower motor goes off after @ 10 min even thou… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x