Primary control unit will...

Primary control unit will not turn on the igniter and fuel oil blower. I can overide it and heat up.

Contractor's Assistant: Did you double-check the thermostat's settings? And what about the filters?

Thermostat sending signal. Primary control unit will not engage to turn on start . Can be overiden to start and provide heat well.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

If heating the unit up . Then turning thermostat down. Forced air chimney functions properly. Unit air circulation functions properly then shuts off.

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 11 hours by:
11/12/2017
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,400
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your

issue. First I’ll need some more info so I have a more complete picture of your situation.

How do you "overrride" the ignition control?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
I tested the fan control relay. High ohm reading. Ordered 1 to try.
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

You didn't answer my question

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Primary control contacts were burnt. Ordered new one. Fan control relay was bad causing voltage drop to Primary control relay. Primary control relay was damaged from vendor. Was able to repair it and replace fan control relay. All working now.
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

ok

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have an old Williamson temp o matic T167. It isn't firing
I have an old Williamson temp o matic T167. It isn't firing on and the manual sticker does not activate either. … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
We bought a home with a Goodman split system heat pump and a
We bought a home with a Goodman split system heat pump and a Luxaire model OU080MC. The oil burner itself works but the control system does not start it.It used to start it until recently...now that i… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Ive had a heating tech here 5-7 times last year to fix a problem
Ive had a heating tech here 5-7 times last year to fix a problem which seems to stump him. I have a oil hot water furnace for radiator/ baseboard heating. I have Beckett R7148b controller. The furnace… read more
Rick
Rick
HVAC Supervisor
24,400 satisfied customers
I have a burnham oil fired boiler it will fire and run and
I have a burnham oil fired boiler it will fire and run and shut off if you wait a couple of seconds and push the reset button it will start and run for a few mins then shut off again… read more
Appliance Guru
Appliance Guru
18,162 satisfied customers
My Buderus Logano G115/4 burner will not ignite. I bought this
My Buderus Logano G115/4 burner will not ignite. I bought this house which had been vacant for about 12 months and had about 1/8 th heating oil in each connected Roth 250USG tanks in the mechnical roo… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Just replaced a similar blown circuit board after a power hit
Just replaced a similar blown circuit board after a power hit burnt a relay on it. My card is a Honeywell ST9103A 1002 electronic fan timer circuit board and now I have the same issue: blower fan come… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hi, my oil furnace is a 2001 and we have it serviced every
Hi, my oil furnace is a 2001 and we have it serviced every year and we had all the ducks cleaned last summer, but when it is on, it creates an ambient noise that is constant and it is starting to feel… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
I have a lenox furnace that is retrofitted with an EGC1 control
I have a lenox furnace that is retrofitted with an EGC1 control board. The issue that I am having is my Furance will not keep the appropriate temperature. Background information: This is our second wi… read more
hvacexpertjoe
hvacexpertjoe
Electronics Technician
Vocational, Technical or Trade Scho
183 satisfied customers
My air handler runs continuously when emergency heat is on
My air handler runs continuously when emergency heat is on due to temperature drop causing heat pump to shut off. There is a 3 wire thermostat wired at the heat pump that shuts it off forcing the emer… read more
Douglas
Douglas
Vocational, Technical or Trade Scho
3,087 satisfied customers
Ihave a model NLOD105FF01 oil fired furnace. The burner works
Ihave a model NLOD105FF01 oil fired furnace. The burner works but the blower doesn't. I jumpered across the fan terminals to make sure the fan can run and it did. I don't understand the fan limit swit… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I am trying to help a friend get modine working in the gareage
I am trying to help a friend get modine working in the gareage it is a hot water unit. It worked fine when he shut it of in the spring. The boiler is a combination wood and fuel oil. the other 4 zones… read more
Rick
Rick
HVAC Supervisor
24,400 satisfied customers
My Newmac NL2 oil furnace does not ignite. When I set the
My Newmac NL2 oil furnace does not ignite. When I set the thermostat to high temperature, the fan runs, but there is no heat and no flame. Nor is there any smell of fuel oil. I do not think the oil pu… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Beckett AF2-150. 3 yrs old. Problems with outo shut downs(very
Beckett AF2-150. 3 yrs old. Problems with outo shut downs(very hard smokey starts,very shakey running and un called for cycling of motor). Replaced pump last year (leaking). Tech did not use beckett r… read more
Rick
Rick
HVAC Supervisor
24,400 satisfied customers
I have a Williamson Temp O Matic Mod# T167-10-2 oil fired
I have a Williamson Temp O Matic Mod# XXXXX oil fired furnace. The flame starts fine, the blower works fine, the nozzle was changed in October, and at the same time a new oil and air filter. finally t… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a outside wood boiler and a fuel oil boiler in the house.
I have a outside wood boiler and a fuel oil boiler in the house. It is set up for the fuel oil boiler to start when heat is commanded and shut off when boiler is up to operating temps which generally … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have an American Standard 1bj1 boiler that doesnt seem to
I have an American Standard 1bj1 boiler that doesn't seem to be heating up the oil. It lights up but it turns off. It also doesn't seem to be turning on by itself but only by the reset button and then… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Friedrich furnace (OUB-095-AMA) that uses a Honeywell
I have a Friedrich furnace (OUB-095-AMA) that uses a Honeywell fan/limit control L4064B 1592 5. 2 questions: 1. When the cad cell checks as okay, could a faulty limit control cause an apparently prope… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My oil burner sometimes leaks oil all over burner and blower
My oil burner sometimes leaks oil all over burner and blower even bad enough it spills on the flow. What do you thing it is.… read more
hvacmrfixit
hvacmrfixit
disabled
Vocational, Technical or Trade Scho
118 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x