I Have an old Peerless oil burner with a Aquastat-Protecto Relay Unit Type R8182D.

Contractor's Assistant: Did you double-check the thermostat? And what about the unit's filters?

I replaced the burner with a Beckett AFG Model that has a Honeywell R7184 P control on it. How do I wire that up to my aquastat

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

Do I keep the R8182 or bypass it and hookup directly to the honeywll

Show More
Show Less
Ask Your Own HVAC Question
Answered in 6 minutes by:
11/11/2017
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,408
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can

continue our conversation.

You connect B1 to LIMIT, B2 to L2 and you need to run a 120 volt hot lead to L1

Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,408
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified
Rick and 87 other HVAC Specialists are ready to help you
Ask your own question now
Customer reply replied 8 months ago
The aquastat had 2 wires from the Cad terminals. Where do those connect on the R7184.
Phone call session started
Customer reply replied 8 months ago
B1 and B2 are connected to the L1 and L2 wires on the R7184. The unit does not turn on.

That's not where I said to connect those leads. Having a little trouble with the phone call.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,408
24,408 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have a 68 series Weil McLain boiler with a Beckett oil
I have a 68 series Weil McLain boiler with a Beckett oil burner model afg . Cleaned boiler today and when i turned it back on i bled the line as you should right when there was a steady stream of oil … read more
Rick
Rick
HVAC Supervisor
24,408 satisfied customers
I have a carrier model 58bma075-12 oil furnace. I replaced
I have a carrier model 58bma075-12 oil furnace. I replaced the beckett model afg oil burner with a new afg burner. When I connect the wiring to the Honeywell st9103a control board the only way I can g… read more
Rick
Rick
HVAC Supervisor
24,408 satisfied customers
I have a Burnham LE2 with a VERY strange problem. The boiler
I have a Burnham LE2 with a VERY strange problem. The boiler quits and has to be "manually" started by pressing the red button on the primary controller Honeywell R7184 A. The green light on the contr… read more
Rick
Rick
HVAC Supervisor
24,408 satisfied customers
I have a Peerless Oil fired boiler that is leaking. I'm
I have a Peerless Oil fired boiler that is leaking. I'm looking to replace parts of it with a unit I found on craigslist. My question is my unit is a WBV-04-150-WPCT. The unit found on craigslist is a… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Honeywell R8182D that is tripping the red safety
Customer: Hello Doug, My name is***** have a Honeywell R8182D that is tripping the red safety button. What is interesting is that it does not trip when the boiler is running. It only trips after the b… read more
Rick
Rick
HVAC Supervisor
24,408 satisfied customers
I need a manual or parts list for the boiler referenced
I need a manual or parts list for the boiler referenced above please. In particular, I need to know what type of combustion ring and electrodes does it use. Boiler Model Num: JO-6L-PF-WU Boiler Serial… read more
Rick
Rick
HVAC Supervisor
24,408 satisfied customers
i am installing a beckett afg oil burner in a Armstrong residential
i am installing a beckett afg oil burner in a Armstrong residential furnace there is a relay in between L1 and the red start wire from the fan,i cannot find instructions on how to wire this relay to t… read more
warmneighbor
warmneighbor
owner
Vocational, Technical or Trade Scho
9 satisfied customers
I acquired a Beckett model AFG series oil burner with a Honeywell
I acquired a Beckett model AFG series oil burner with a Honeywell R7184p Interupted Ignition Oil Primary Control mounted on it. I presently have a early 1980"s Beckett burner with a Honeywell R8182 Co… read more
MattR757
MattR757
HVAC Contractor / Owner
Associate Degree
14 satisfied customers
My oil fired Peerless MODEL EC 04 WV CAST IRON boiler is curently
My oil fired Peerless MODEL EC 04 WV CAST IRON boiler is curently fitted with a L4080B1261 Honeywell aquastat (3/4 Short 123870A} that doesnt have an adjustable high low limit, and because the boiler … read more
Rick
Rick
HVAC Supervisor
24,408 satisfied customers
ran out of oil today,reset button does not turn furnace on(this
ran out of oil today,reset button does not turn furnace on(this always works)so im trying to bleed my beckett afg...not sure where the bleeder screw is and how to correctly bleed the beckett afg so we… read more
Rick
Rick
HVAC Supervisor
24,408 satisfied customers
i previously submitted a question, which is currently being
i previously submitted a question, which is currently being reviewed. I mistakenly entered wrong burnham model #. correct: Burnham oil fired boiler Model # XXXXX (had it as #172 model)… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
Hello, Just a quick oil burner question.Model AFG-Weil-Mclain
Hello, Just a quick oil burner question.Model AFG-Weil-Mclain burner with a Honeywell L814A1124 aquastat. My problem is while burner is running the motor-burner relay in the aquastat starts jumping in… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
286 satisfied customers
i just installed a new oil fired furnace (steam heat) in my
i just installed a new oil fired furnace (steam heat) in my home with a Beckett model AFG burner, my question is this ....to me it seems to be not very efficient, i have used approx. 500 gallons of fu… read more
Rick
Rick
HVAC Supervisor
24,408 satisfied customers
I have installed a new beckett burner afg with a R7184B control.
I have installed a new beckett burner afg with a R7184B control. Will this work with an R8182D control… read more
Rick
Rick
HVAC Supervisor
24,408 satisfied customers
Hi there, I do have an older Beckett RWB unit and thinking
Hi there, I do have an older Beckett RWB unit and thinking about replacing it with newer one. Is it interchangeable/compatible with AF,AFG, NX models? And what are the benefits of newer Beckett units?… read more
Rick
Rick
HVAC Supervisor
24,408 satisfied customers
i have a oil furnace broiler system it heats my water water
i have a oil furnace broiler system it heats my water water is scalding hot what can i do to correct this is it expensive fix… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
I just installed a Beckett AF b2503 High Eff. Honeywell unit
I just installed a Beckett AF b2503 High Eff. Honeywell unit will not initialize. Hot and common correctly hooked up and shows energized on Multimeter. Reset pushed and held for 1, 15 and 45 Seconds n… read more
Roger (Mr. Fixit)
Roger (Mr. Fixit)
Service and Sales Manager
Bachelor's Degree
16 satisfied customers
I have Honeywell type R8182D Aguastate-Protecto relay. I have
I have Honeywell type R8182D Aguastate-Protecto relay. I have baseboard heat need to reach 3rd floor bedrooms in old farmhouse. I have 20psi, limits set at 190/170 but do not know what the diff should… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question