I have a intertherm gas furnace mgha-056abfc-01 that is

Customer Question
I have a intertherm...

I have a intertherm gas furnace mgha-056abfc-01 that is short cycling. Runs for about 45 secs and blower shuts off with burner still on. Blower was replaced about 6 years ago along with fan switch and limit switch.

Contractor's Assistant: Did you double-check the thermostat? And what about the pilot light?

I swapped the thermostat last night. The pilot light is fine, The burners are working.

Contractor's Assistant: Do you plan on doing the work yourself?

I usualy do if I can find the problem. Checked continuity on flame roll over limit switch and its good.

Contractor's Assistant: Anything else we should know to help you best?

Not that I know of Its a mobile home if that matters

Submitted: 5 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 10 minutes by:
11/11/2017
HVAC Technician: Phil, Mechanical Engineer replied 5 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, try setting the fan and limit switch 20 degrees higher, as a brief test only. If that changes the short cycling situation, tell me what the settings are.

We can go from there.

.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
There isnt an adjustment on the switches. It is a 25 year old mobile home furnace in my rental home.
Customer reply replied 5 months ago
I do not get good phone reception here.
Customer reply replied 5 months ago
hello
Customer reply replied 5 months ago
Are you working on my answer or am I waiting here for nothing? Thanks Brian
Customer reply replied 5 months ago
I am asking for a refund this was a joke and waste of time and money!!!!!
HVAC Technician: Phil, Mechanical Engineer replied 5 months ago

Hello, I can put in for a refund if you wish.

However we handle many questions at a time and there is usually a delay while we do research and type up answers... both take time... there are no pat answers without that research, pulling the manuals and etc.

Ask Your Own HVAC Question
Customer reply replied 5 months ago
I want a refund
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6,938
6,938 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,938 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I need a pilot assembly for my boiler and the number of the
I need a pilot assembly for my boiler and the number of the part is 511-330-116 … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I want to power a single speed circulator pump from a 120ac
I want to power a single speed circulator pump from a 120ac gfi outlet through a honeywell r8285a control center and a honeywell ct33a thermo- … read more
Dales-Electronic
Dales-Electronic
1,033 satisfied customers
I have a Plus 90i gas furnace and was told there was no
I have a Bryant Plus 90i gas furnace and was told there was no filter installed. When I opened the door to find where to put a filter, I see no where to install one. Can you help?… read more
David Bowden
David Bowden
Owner
764 satisfied customers
Is there way to calculate furnace efficiency from the
Hello Richard- Is there way to calculate furnace efficiency from the information from my gas bill? I recently upgraded my 93% efficient( 70k btu) furnace to 96+% efficiency furnace (60k btu). The issu… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Honeywell thermostat pro series. It doesn't say
I have a Honeywell thermostat pro series. It doesn't say which one. it has 4 little buttons on the outside and neither says any directions the two outside buttons on the left is - on the right is + ca… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I am attempting to identify a two valves on a Burderus
I am attempting to identify a two valves on a Burderus Logano G215 US oil-fired boiler. Reference is on page 58 Fig 72, 73 of the User Manual. The symbols are located to the right of three baseboard h… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We have a Trane tcont824as52daa thermostat. We had power
we have a Trane tcont824as52daa thermostat. We had power fluctuations yesterday and I noticed that the screen was white with nothing on it. I unplugged the heater and turned it back in and it was the … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
We have a Rheem Model RTGH-95DVLN, it has been in use for 13
We have a Rheem Model RTGH-95DVLN, it has been in use for 13 months with no issues,. the P1 error code was flashing and the burner not firing up. I flushed the system with vinegar and cleaned the smal… read more
canuck the pro
canuck the pro
253 satisfied customers
Heil-McLain Cg 25 thru 8 Valve P/N VR8300C-4100, Tonight.
Tonight. The “controller circuits” are making a call because I have 24 VAC at the Honeywell valve. The pilot light stays on and when I disconnect 1 of the VAC drive connections to the valve I hear an audible “click.” The valve body is warm, but not excessively. The main burners do not light. … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I bought a blower motor for my heat pump and it didnt have
i bought a blower motor for my heat pump and it didnt have any wires for the blower relay which means the blower stays on all the time … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Bought condo in FL. Would like to employ a Samsung
Bought condo in FL. Would like to employ a Samsung Smartthing to monitor temp while not at the condo. What basic, inexpensive thermostat from Honeywell would you recommend? … read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Lennox XC-21-060 Trip Light On On start up the condenser fan
Lennox XC-21-060 Trip Light On On start up the condenser fan spins slowly once the second stage tries to start the fan stops and the trip light on. I changed the capacitor and the contactor. Did not c… read more
Brian HVAC Guy
Brian HVAC Guy
HVAC Technician
High School
953 satisfied customers
I have a garland strarfire series 48" wide stove. i am
i have a garland strarfire series 48" wide stove. i am looking for new dials … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,700 satisfied customers
Changed the therm coupling and the gas pilot in the
changed the therm coupling and the gas pilot in the installation kit from amazon cleaned the bottom and inside the tank has new air filter the problem it will get luke warm but won't get hot … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Ran out of propane. filled the tanks now furnace is flashing
ran out of propane. filled the tanks now furnace is flashing four red. limit switch is open I presume. every time we run out of propane this happens and I got to call in a tech. three times this year.… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
I have an A.O. 50 gallon natural gas promax hot water
I have an A.O. Smith 50 gallon natural gas promax hot water heater. After running 15 or 20 minutes the gas valve iidicats excessive exhaust back pressure and shut the burner off. I checked the intake … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Your answer to my pilot light problem was that my flame
Your answer to my pilot light problem was that my flame sensor rod was dirty. Do I need to remove the burner assembly to clean this rod?… read more
Phil
Phil
Mechanical Engineer
6,938 satisfied customers
Is this a refrigerant leak on my outdoor a/c unit? When I
Is this a refrigerant leak on my outdoor a/c unit? When I click the thermostat to Cool /Auto the outdoor unit clicks one time and then does nothing (no humming sound or anything)and warm/room temp air… read more
Bill
Bill
Service Mgr
83 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x