My furnace is about 1 year old the burners kick on a story on about 3 seconds and then they shut off

Contractor's Assistant: Did you check the furnace's filters?

Yes put new filters in new filter in

Contractor's Assistant: Do you plan on doing the work yourself?

Yes if it sounds like something I can do

Contractor's Assistant: Anything else we should know to help you best?

It is a York Furnace if you need the model number I can get it it has two glasses one at the top and one at the bottom and the glass the bottom of light or fire whatever it is down there is flickering when I turn the furnace on right now I have the furnace shut off

Submitted: 5 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Customer reply replied 5 months ago
I took both doors off of the front of the Furnace there is a looks like a red light on at the bottom which was showing through the glass when I kick the furnace on that light glows when it starts to act up that life starts to Flicker and then when the burners shut down at light shuts off
Customer reply replied 5 months ago
Posted by JustAnswer at customer's request) Hello. I would like to request the following Expert Service(s) from you: Live Phone Call.
Customer reply replied 5 months ago
Let me know if you need more information, or send me the service offer(s) so we can proceed.
Answered in 48 minutes by:
11/10/2017
HVAC Technician: Phil, Mechanical Engineer replied 5 months ago
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,313
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Verified

Hello, so far it looks like a dirty or failed flame sensor rod, easily cleaned if its just dirty... 90% chance thats the problem.

OR a 10% chance the printed circuit board is bad IF you have actually seen the flames on the actual burners.

.

Take a close up, exceedingly well focused photo of the wiring diagram glued inside the furnace/air handler door, and I will mark it up with trouble shooting instructions. Use the 'add files' link next to your send button to get the photo(s) to me.

We can go from there with training, coaching and diagnosis.... without a time limit, In depth with as much detail as needed , after you rate this answer:

Select the 'finish and rate your expert link' near the top of your page and click on it.

.

OPENING STATEMENTS

Important note about RATING my work:

I am a retired mechanical engineer and HVAC/electrical/ refrigeration and boiler contractor ... with 56 years in this business. The last 20 of those years consulting for major firms nationally.. and with over 8,000 questions answered here since 2009, with a 98.5% satisfaction rating.

.

All I ask is please respect me and my input by selecting the***RATING LINK***at the top of your page, that is the only way I am credited through the site. Rating does not affect your charges nor ability to refund if not satisfied.

.

If you need to be coached through a full diagnosis/repair,and wiring etc. for up to two days, and wish to be trained to use test instruments...... that goes well beyond' Just a simple Answer' of course, and goes beyond what most other experts here offer.....rate my answer so far positively.. . and I will deliver that training and coaching to you All on the same dime so to speak.

That said, I cannot guarantee that you will not do something unsafe, or cause damages. You take that risk.

.

Lacking a positive rating I can spend days helping a person at my own expense and loose my shirt, shorts and socks on the deal.

.

Phone call offers:

If you wish to accept the companies $25 phone call offer, if indeed they send you one, this will go a *lot faster, but it IS 100% optional... or we can continue here in this dialog box at no additional charge.

.

Tell me a lot about your technical background and instruments on hand so that I can coach you most effectively. We can go from here as you keep asking follow up questions without any limits … those actions are necessary to keep you on my list.

Ask Your Own HVAC Question
Was this answer helpful?
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 9,313
9,313 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

9,313 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Buderus GB142 wall hung boiler with in concrete floor
Buderus GB142 wall hung boiler with in concrete floor radiant heat. Boiler Temp is set at 135, the attached AM10 has the target temp point set at 135 as well and the base temp point at 110. On cold da… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have an old York furnace, we lost power and it would not
I have an old York furnace, we lost power and it would not start back up... I checked the codes and it says “open pressure switch” I blew and sucked on the hose I hear an Audible clicking, tried again… read more
Phil
Phil
Mechanical Engineer
9,313 satisfied customers
I have a cg5 boiler for my home. The boiler ignites and runs
I have a cg5 boiler for my home. The boiler ignites and runs for 10 seconds or so, turns off for 1 or 2 seconds and then reignites, that happens over and over again for 30 minutes or so and then shuts… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
EcoTecplus 428 boiler,after reset boiler not coming on,but
ecoTecplus 428 boiler,after reset boiler not coming on,but pcb has power. … read more
Plumbers_Mate
Plumbers_Mate
General Manager
Vocational, Technical or Trade Scho
2 satisfied customers
Can you refer me to a Weill McLain boiler repairman? Boiler
Can you refer me to a Weill McLain boiler repairman? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
My crown boiler boiler model no. AWR070ENST2PSU runs for a
My crown boiler boiler model no. AWR070ENST2PSU runs for a short time, shuts down, then takes a long time on start running again. We change the control. the pump, and the gas valve, Don't appears to h… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a York Furnace. It will run for a while and then shut
I have a York Furnace. It will run for a while and then shut off, with four red blinking lights. I check the limit switches and they didn't seem to be open. … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
York furnace stopped working and showing 3 red flashes. A
york furnace stopped working and showing 3 red flashes … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a York Furnace Model TG9S060B12MP11A My heater is
I have a York Furnace Model TG9S060B12MP11AMy heater is having problems. It blows hot air for some time, and about 30 minutes or so the air gets cool, it doesn't blow hot air anymore - even if the roo… read more
Phil
Phil
Mechanical Engineer
9,313 satisfied customers
Diamond 80 york furnace. Stuck open pressure switch. 3
Diamond 80 york furnace. Stuck open pressure switch. 3 flashing led. Right before Christam Eve...right? Clasdic. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,684 satisfied customers
I have a York furnace flashing 7 times. Little fan turns on
I have a York furnace flashing 7 times. Little fan turns on but ignitor does not turn red. Over the past several weeks same thing has happened 3-4 times. I have turned off furnace several times and wa… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Im working on a boiler right now and the boiler is running
Hi pearl im working on a boiler right now and the boiler is running but is not heating the downstairs not the upstairs. I can't figure out why. Yesterday I replaced the pressure relief valve and the e… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
We have a York furnace. We have no heat. The fan is working
We have a York furnace. We have no heat. The fan is working but the burners will not fire. … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,684 satisfied customers
I have a York furnace that has been operating erratically
I have a York furnace that has been operating erratically for about a week, although sometimes it operates fine, at other times it will do the following:Calls for heat but the inducer motor will not s… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
We have a rooftop York furnace model D1NH03N05606C. We
We have a rooftop York furnace model D1NH03N05606C. We recently had to turn the gas off to the house and now the heater is not working. We assume this is a pilot light issue but don't know where to fi… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
How can I tell I my York furnace control board is the cause
How can I tell I my York furnace control board is the cause of the furnace not completing the heat cycle. It shuts down and give me the pressure sensor/switch code but two tech's have been out and ver… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a York furnace Model #P3UCD20N09101A. The thermostat
Good morning Pearl, I have a York furnace Model #P3UCD20N09101A. The thermostat calls for heat and the ventor motor comes on and the igniter lights but I get no flame. Any ideas? … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
Just put new control board in a YORK furnace the same issue
Just put new control board in a YORK furnace the same issue occurs. I have no voltage off the 2 eac leads on the board … read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
450 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x