Customer Question
I need to replace...

I need to replace the Zone 3 relay in my Taco SR504, but there are five 28 volt relays and they are not numbered on the board -- or in Taco's documentation.

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

A couple of days. I diagnosed the blown relay, so there is not a problem with the pump or power feed.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes, I have a replacement relay.

Contractor's Assistant: Anything else we should know to help you best?

No -- I just need to know which relay matches Zone 3. There are six relays on the Taco SR504. The first on the left is a 120V relay. The second to sixth appear to be 28 volt relays, with no numbers.

Submitted: 10 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
11/10/2017
HVAC Technician: Rick, HVAC Supervisor replied 10 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,829
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your issue. If my initial response doesn’t answer your question then let me know and we can continue our conversation.

It's the ice cube between the thermostat and pump leads on the relay board for that zone.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Dear Rick: I wish it was that simple. I have the Taco wiring diagram for the SR504 and the wiring posts under the six relays are labeled -- but they do not correspond to the relays above, which are not labeled -- except for the 120V relay on the left side. This leaves five 24 volt relays to the right, for four zones. One of them is probably the 'priority' switch, if you enable that feature. So do you know how the five relays are numbered?
HVAC Technician: Rick, HVAC Supervisor replied 10 months ago

I've installed and serviced this product since it was introduced. Yes it is that simple. The relays to the left away from the zone wiring are not zone control relays.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Dear Rick: The relays for the original Taco SR504 are in the middle of the PCB board, with wiring connectors above and below. So the relays are not "to the left". I attached a PDF of the original SR504 install guide for your review.
Thanks, ***** *****
HVAC Technician: Rick, HVAC Supervisor replied 10 months ago

I'll say this one more time. The 2 relays on the left are not zone control. Granted the zone control relays don't fall exactly between stat and circ wiring but the order right to left is the same.

Ask Your Own HVAC Question
Customer reply replied 10 months ago
Dear Rick: Thanks for your quick reply. I wish Taco documented this basic fact about their controllers -- the documentation for the newer version still doesn't label the relays. So based on your knowledge, Relay 1 = 120v, Relay 2 = Priority, and Relays 3, 4, 5 and 6 = Zones 1, 2, 3 and 4. Attached is a JPG image of the controller layout. If this is correct, please let me know -- and I hope it will be helpful if another customer asks the same question.
Thanks, *****
HVAC Technician: Rick, HVAC Supervisor replied 10 months ago

You have the zone relays labeled correctly

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,829
24,829 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,634 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I had a taco sr504 that one zone was not working. I switched
I had a taco sr504 that one zone was not working. I switched thermostats from other zones , jumped out that zone, switched contactor relays etc. I called taco and they said it was probably a bad board… read more
Rick
Rick
HVAC Supervisor
24,829 satisfied customers
Wiring 2 ganged SR504's to a tekmar 260. The tekmar 260 is
the tekmar 260 is new the sr504's are 20 years installed with 7 zones and dhw priority … read more
Rick
Rick
HVAC Supervisor
24,829 satisfied customers
How much does it cost to chat with an HVAC rep, Can you give
I have a hot water boiler for heat and it has 3 different zones. 2 seem to work but one zone does not… read more
Rick
Rick
HVAC Supervisor
24,829 satisfied customers
I have a (slightly older style) Taco SR503, wired with a
Hi, I have a (slightly older style) Taco SR503, wired with a newer SR503 and an SR504, as shown on p.10 of the 100-9.0 Taco zone controls wiring guide (10 zones total). When a zone calls, the the appr… read more
Rick
Rick
HVAC Supervisor
24,829 satisfied customers
I've got a NTI boiler with Sentry controller. Boiler fires
I've got a NTI boiler with Sentry controller. Boiler fires fine when DHW calls but Thermostat Demand light won't light on the Sentry even though there all calls for heat from all 3 zones. I've just re… read more
Rick
Rick
HVAC Supervisor
24,829 satisfied customers
TACO SR504 I have 4 zones with circ pumps...1 is water. The
TACO SR504 I have 4 zones with circ pumps...1 is for hot water. The boiler cycles but does not fire now. If I call for heat the boiler works fine and the zonegets hot (circ pump runs) During this the … read more
Rick
Rick
HVAC Supervisor
24,829 satisfied customers
I currently have 4 Furnas two pole relays to energize 4 zone
I currently have 4 Furnas two pole relays to energize 4 zone valves and 4 Taco circulating pumps being fed from my Weil Mclain boiler. The boiler has an indirect tank and a on board Taco circ. pump to… read more
Rick
Rick
HVAC Supervisor
24,829 satisfied customers
The Weather Dependent Control AM10 unit for my heating system
The Weather Dependent Control AM10 unit for my heating system seems to have no power coming to it. There's no display of the outside temperature. As the homeowner, is there anything I can do from here… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have Viessmann Vitodens 100-W Boiler and Taco SR504-4 Switching
I have Viessmann Vitodens 100-W Boiler and Taco SR504-4 Switching Relay. It is not obvious to me how to connect them. I have 3 thermostat zones (radiant heating circuits) and one priority zone for DHW… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
How to wire a thermostat through a circulating pump and an aquastat?
How do I wire a thermostat through a circulating pump and aquastat that's on a central HVAC system?… read more
V12Tech
V12Tech
252 satisfied customers
I have a Peerless WV-DV boiler with a Honeywell triple aquastat
I have a Peerless WV-DV boiler with a Honeywell triple aquastat type LB124/C I am also using a Taco SR504 switching relay to operate three pumps. I'm trying to add a Honeyweel CT87N thermastat and a T… read more
Rick
Rick
HVAC Supervisor
24,829 satisfied customers
I have a Taco SR504 wired as a to an SR506. All has worked
I have a Taco SR504 wired as a slave to an SR506. All has worked well for 4.5 years, but this year one zone powered by the 504 does not come on. The monitor light for that zone doesn't light. Swapping… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Wiring Weil-Mclain Ultra 155 Boiler with 4 pumps? Manual wiring
Wiring Weil-Mclain Ultra 155 Boiler with 4 pumps? Manual wiring diagram allows only for 3 pumps 1 Boiler pump 1 DHW pump 1 baseboard radiation pump 1 in-floor radiation pump… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a peerless boiler model # WBU-03-WPCTC Serial # 557872-200609 with
I have a peerless boiler model # XXXXX Serial # XXXXX with a taco sr-503 3 zone switching relay, The system has a primary circulator and 2 24volt zone valves theses are taco 571 I believe, they have 1… read more
Rick
Rick
HVAC Supervisor
24,829 satisfied customers
I am contemplating using Taco Zone Control for 18 zone valves,
I am contemplating using Taco Zone Control for 18 zone valves, 15 stats, 4 circulators, and one fan. I would anticipate using the priority feature for the DHW, defeating all of the heating valves. The… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I am going to list the items used in this application 1.
I am going to list the items used in this application: 1. Weil-McLain Ultra 155 with PHD technology (Gas fired) 2. Weil-Mclain Plus-Line 80 Indirect fired water heater 3. 8-Taco 007 circulators for zo… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
Hello, Ive just installed a RSA85 burnham boiler . It is
Hello, I've just installed a RSA85 burnham boiler . It is set up with a Taco rs504 relay panel. When I try to power up to bleed the oil line, the burner dooesn't start.. I get a 06 error code. It says… read more
Rick
Rick
HVAC Supervisor
24,829 satisfied customers
I have a new honeywell L7224 aquastat and a new cold start
I have a new honeywell L7224 aquastat and a new cold start boiler with 4 zones. What electronic zone control relay panel should I get to connect aquastat for the 4 circulator zones… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x