Rick I still have issue with my boiler BUDERUS G-224 It

Customer Question
continues to make the knocking...
Rick I still have issue with my boiler BUDERUS G-224 It continues to make the knocking noise inside that transfers on the pipes and radiators when the boiler is reaching the cut of temp of about 150F
What do you think maybe happening?
Submitted: 9 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 minutes by:
11/10/2017
HVAC Technician: Rick, HVAC Supervisor replied 9 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,621
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Well with water temp well below boiling point the only other possibilities are air in the system or possibly to high water flow (pump GPM too high) and you get what's essentially water hammer when a zone valve closes.

Ask Your Own HVAC Question
Customer reply replied 9 months ago
Rick I did replace last week the Amtroll expansion tank and it helped little bit. I did eliminate the zone pumps because they switch on before I start to hear the knocking it gets louder as the boiler reaches its cut off set point some of the knocking is low I hear it when I am by the boiler but then are the louder ones that travel through the pipes. .
HVAC Technician: Rick, HVAC Supervisor replied 9 months ago

Do you have a separate temp gauge or are you relying on the boiler temp reading?

Ask Your Own HVAC Question
Customer reply replied 9 months ago
Rick I will call you on a day when I am back at the house and next to the boiler so you can also hear what it is doing, Stan
HVAC Technician: Rick, HVAC Supervisor replied 9 months ago

Ok

Ask Your Own HVAC Question
Customer reply replied 9 months ago
the boiler is controlled by it own Buderus Logomatic control.
HVAC Technician: Rick, HVAC Supervisor replied 9 months ago

That's not what I asked. I asked if there is a separate external temp gauge to verify water temp. If not then the boiler temp sensor could be off and your water could be a lot hotter than you think.

Ask Your Own HVAC Question
Customer reply replied 9 months ago
there is a T/P gauge on the manifold above the boiler that shows the how hot is the water leaving the boiler it is some 5 feet away.
HVAC Technician: Rick, HVAC Supervisor replied 9 months ago

Ok

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7,426
7,426 Satisfied Customers
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,024 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
What may be causing my Buderus G 224 boiler to make
Douglas what may be causing my Buderus G 224 boiler to make hammering noise in the piping throughout the house? … read more
Rick
Rick
HVAC Supervisor
24,621 satisfied customers
I have 2 Burnham Alpine 80s. Installed new, a month ago. Oil-to-gas conversion. Had noi
I have 2 Burnham Alpine 80s. Installed new, a month ago. Oil-to-gas conversion. Had noise issues and both boilers required "tuning" - adjusting CO2 levels and other settings. Now my boiler is quiet an… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a two wire hydronic system. In the past, it worked
I have a two wire hydronic system. In the past, it worked well with the thermostats. lately, I noticed that everything goes out of whack when the outside temperature goes to the single digits. I have … read more
Rick
Rick
HVAC Supervisor
24,621 satisfied customers
I have a Liberty L 50 slant fin boiler - about a week ago while
I have a Liberty L 50 slant fin boiler - about a week ago while in the basement I noticed a sort of knock knock knock sounds coming from it when it kicked on - now this has evolved into a sort of howl… read more
Rick
Rick
HVAC Supervisor
24,621 satisfied customers
Hi, I have an American Standard G-26 Gas Steam Boiler. (1)
Hi, I have an American Standard G-26 Gas Steam Boiler. (1) When it runs it makes loud banging noise from the basement pipes. (2) I kept the therm at 68, it is placed near the boiler room, and set at 5… read more
Rick
Rick
HVAC Supervisor
24,621 satisfied customers
follow-on question for Peerless M1-04 boiler to radiant
Hello, I have a follow-on question to a session I had with Rick a few weeks back: http://tinyurl.com/m2xyftv. I now have the two underfloor staple-up radiant zones and one (existing) cast iron radiato… read more
Rick
Rick
HVAC Supervisor
24,621 satisfied customers
I have a Weil McLain circulating hot water boiler with old
I have a Weil McLain circulating hot water boiler with old style radiators that is about 15 years old. Last winter the boiler started making noise, after heating up, that sounds like expansion noise. … read more
Rick
Rick
HVAC Supervisor
24,621 satisfied customers
I would like to turn the hot water temp down..I have a Buderus
I would like to turn the hot water temp down..I have a Buderus G215 water boiler.. can you tell me how to do it?… read more
Rick
Rick
HVAC Supervisor
24,621 satisfied customers
I have a G124X II boiler w/HS 2105 controller. During the current
I have a G124X II boiler w/HS 2105 controller. During the current cold wave in the NE, low OA temps in 5-10F range, after the house warms up to thermostat day settings, the manual hi temp reset (STB) … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My boiler started giving loud rumbling noise coming from the
My boiler started giving loud rumbling noise coming from the ground and radiators where the boiler is located. Started happening a few days before but now it's occurring after about an hour every time… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Buderus hot water boiler G-224E-21. 3 or 4 minutes
I have a Buderus hot water boiler G-224E-21. 3 or 4 minutes after the furnace turns on , there is a loud noise. sounds like a drum noise. robert herold gebobh @aol.com… read more
Rick
Rick
HVAC Supervisor
24,621 satisfied customers
My PIN4SNI-ME2 boiler system is single pipe gravity feed. It
My PIN4SNI-ME2 boiler system is single pipe gravity feed. It makes a lot of noise when coming on. It's not a pinging or knocking sound, indicating trapped air, but the sound of gurgling/rushing water.… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have Vaillant Thermocompact boiler 282E, boiler fires for
I have Vaillant Thermocompact boiler 282E, boiler fires for less than minute reaching temperature on gauge of 80 degrees, temperature then drops to minimum before boiler refires some minutes later res… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
I think my boiler may have been affected by the cold last night.
I think my boiler may have been affected by the cold last night. Sound of running water in boiler and pipes, pressure turned to 1.5. Outside, the vent is making a gurgling noise and eventually when th… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
we have a baxi 105e combi boiler, it keeps banging , pressure
we have a baxi 105e combi boiler, it keeps banging , pressure jumps all over the place, hot water goes hot and cold ,heating gets up to temp on boiler then switches off not realy hot at rads, have ask… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
I have a Heatline Capriz 25 boiler that is controlled by a
I have a Heatline Capriz 25 boiler that is controlled by a radio-controlled thermostat, placed in the hallway. When the heating is on it will fire up for a while heat the rooms up by 0.5 degrees and t… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
Hi I have a Vaillant Eco Tech + 428 Boiler which was installed
Hi I have a Vaillant Eco Tech + 428 Boiler which was installed in January this year. the problem I have is that it fires up and then cuts out when the temp reads 77 degrees. This goes on for hours unt… read more
Rick Ridley
Rick Ridley
UK Heating Engineer
30 years on the tools
871 satisfied customers
I just installed a L8148 Aquastat relay to replace a 22 year
I just installed a L8148 Aquastat relay to replace a 22 year old relay that had mechanical failure. My furnace supplies forced hot water heat as well as hot water (no separate hot water heater). My he… read more
Rick
Rick
HVAC Supervisor
24,621 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x