I have a 362AAN low boy with a Reillo 40 burner. Very often,

Customer Question
I have a Bryant...

I have a Bryant 362AAN low boy with a Reillo 40 burner. Very often, I need to press the reset switch to get it to run. Any time I press the reset switch, it will start up. Sometimes it will run fine for many cycles. But, especially if the cycles are far apart in time, it will fire and stop after 20 or 30 seconds. Sometimes, it will start and run for 10 or 15 seconds, and then the flame will stop, and then I will hear the spark click, and the flame will start again, but then stop after a few seconds. Once I get it to run for a minute or so, it will run fine until the thermostat tells it to shut down. Then, if the thermostat commands a new cycle and things are fairly warm, it will start and run fine. Sometimes, especially if things are cold, it will require one or two resets. Again, if it runs for a minute or two, it will run reliably until the thermostat turns it off. I've checked the CD cell and it seems to be fine. I have a new tank of oil, so that is fine, too. Again, once it runs for a while, it runs fine. It is just initial starting and running for more than a minute or so. I'm perplexed as to what the problem could be.

Contractor's Assistant: Just to clarify, do you think this is a larger HVAC problem, or something specific to the thermostat?

I do not believe it has anything to do with the thermostat. It has something to do with the burner.

Contractor's Assistant: Do you plan on doing the work yourself?

Yes

Contractor's Assistant: Anything else we should know to help you best?

I thought that maybe the flue was clogged and that was causing a problem. I checked and there was a lot of debris in the bottom of the chimney and the flue pipe. I cleaned all that out yesterday so that is all good. I have primed the pump with fuel and I get a flow. The filter is relatively new, and this problem has been since before the filter was replaced.

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
11/10/2017
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,401
Experience: 40+ yrs. experience as a licensed oil & gas technician.
Verified

Welcome to Just Answer, my name is ***** ***** I will do my best to help you with your

issue. First I’ll need some more info so I have a more complete picture of your situation.

When was the last time it was tuned up?

Ask Your Own HVAC Question
Customer reply replied 8 months ago
Never.
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

Ok burner neeeds a tune up by a qualified Riello tech. This is not a DIY project

Ask Your Own HVAC Question
Customer reply replied 8 months ago
As I said, I tested the CD cell, and it is clean and working. I am an electrical engineer and have all sorts of test equipment, so I can measure just about anything. I am thinking that I need to change either the nozzle or adjust the spark gap, but it seems strange that it runs once it gets past the first minute or so. If it was the pump, it would not continue to work once it gets going. I have also checked for water in the oil, but that, again, cannot be the problem since that would cause it to shut off at random times
HVAC Technician: Rick, HVAC Supervisor replied 8 months ago

You may be an electrical engineer but you're not a trained Riello tech and I doubt you have a flue gas analyzer, a smoke spot reader or a stack temp gauge not to mention the required training and experience to service this unit. Would you try to tune up a Ferrari? You need a trained tech for this.

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Rick Your Own Question
Rick
Rick
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 24,401
24,401 Satisfied Customers
Experience: 40+ yrs. experience as a licensed oil & gas technician.

Rick is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I have the problem of 3 flashes on the Trane XE 80. The problem
I have the problem of 3 flashes on the Trane XE 80. The problem occurs when the furnace cycles off and then restarts soon after. It gets the call for heat after shutting down for a short time. I suspe… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Automatic ignition of the pilot light is not working... top
Automatic ignition of the pilot light is not working... top panel is off gas is in on position, regulator is in on position. Heater has been commanded to on about 5 minutes now with no attempt at igni… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
My boiler oil fired boiler with beckett burner will start
My boiler oil fired boiler with beckett burner will start and run (with flame) for approx 5 seconds and then lock out. Have to hold the reset button to restart and then it does the same thing. Boiler … read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have an amana air command 80SV that short cycles. When I
I have an amana air command 80SV that short cycles. When I call for heat, it operates for about 10 minutes then shuts down. Then starts again after a few minutes then shuts down again resulting in a "… read more
Bart Jay
Bart Jay
Vocational, Technical or Trade Scho
596 satisfied customers
I have a Laars Mini-Therm II, Model JV, installed new 10 1/2
I have a Laars Mini-Therm II, Model JV, installed new 10 1/2 years ago when we built our home. Last September we replaced a 14 month-old electronic ignition -- a refit intended to solve the problem of… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a Ruud Deluxe 80 Plus. It ignites fine, heats well.
I have a Ruud Deluxe 80 Plus. It ignites fine, heats well. No problems all winter. Now towards the end of winter it sometimes makes repeated clicking sounds while running. Sounds like it comes from th… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have a Payne Furnance and it just started to shut done on
I have a Payne Furnance and it just started to shut done on the thermal high temp switch. I have pushed the reset button and it will run but after 5 minutes it trips again? What can be causing it to t… read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
Hello. I have a Trane XB90 propane gas furnace. When the
Hello. I have a Trane XB90 propane gas furnace. When the thermostat calls for heat, the furnace starts up, the burners fire, and the blower begins to cycle the air as you would expect. However, after … read more
HVAC_Doug
HVAC_Doug
Vocational, Technical or Trade Scho
I have a Trane XE80 Gas furnace. The burner is short cycling.
I have a Trane XE80 Gas furnace. The burner is short cycling. When set to heat, the flue exhaust starts and in about 45 seconds the burner ignites. Approximately 1 minute later the blower motor comes … read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
armstrong air furnace blower turns on and off during heat cycle
armstrong air furnace blower turns on and off during heat cycle burners stay on then after thermostat shuts it down it may or may not come back on i heat thermostat click but nothing happens… read more
Mike
Mike
Service Tech/ Installer
High School or GED
149 satisfied customers
My Trane xl90 will start up, heat up, then the gas goes off
My Trane xl90 will start up, heat up, then the gas goes off, the main blower stops but the smaller return air / exhaust motor will keep running till you turn off the furnace. If I reset it, most of th… read more
Dan Linger
Dan Linger
Lead Technician / Energy Consultant
Bachelor\u0027s Degree
62 satisfied customers
I have a Bryant Gas Furnace and is cycling and according to
I have a Bryant Gas Furnace and is cycling and according to the control board it is Limit or Flame rollout switch is open. I checked the blower motor it is fine I checked filter and motor capacitor ev… read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
furnace starts and then gas shuts off. Will try three times
furnace starts and then gas shuts off. Will try three times and then shuts down. Once in a while furnace will keep running. may run til thermostat shuts it off or will run for 5-10 minutes and then sh… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Hello, I just moved into a foreclosed house and have a Payne
Hello, I just moved into a foreclosed house and have a Payne furnace that's about 10 years old. I had gas put in the propane tank outside and the technician ran a check on the furnace and was running … read more
Rick Mather
Rick Mather
HVAC Technician
Vocational, Technical or Trade Scho
3,133 satisfied customers
I have a ruud furnace that will run for a few minutes then
I have a ruud furnace that will run for a few minutes then will kick off, will not start again until i turn it off and off again. can anybody help me?… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
changed oil filter, was trying to bleed air so the oil wil
changed oil filter, was trying to bleed air so the oil wil flow rough theand won't reset. filter. pushed re set button twice and now it keeps blinking… read more
Rick
Rick
HVAC Supervisor
24,401 satisfied customers
I have a R7184B honeywell....i ran out of oil...i filled my
I have a R7184B honeywell.... held the red button in for 45 seconds and the fan turns on for 20 seconds and then turns off and the light blinks back on recycle.… read more
Rick
Rick
HVAC Supervisor
24,401 satisfied customers
I just put in a new boiler yesterday. The burner is a Beckett,
I just put in a new boiler yesterday. The burner is a Beckett, with a Honeywell thermostat. I had hot yesterday , but the burner won't go on today. If I press the reset, the burner goes on for about 3… read more
Roger (Mr. Fixit)
Roger (Mr. Fixit)
Service and Sales Manager
Bachelor's Degree
16 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question