Lennox g40uh open limit switch? Causes? 6hrs. I can get it…

Customer Question
Lennox g40uh open limit...

Lennox g40uh open limit switch? Causes?

Contractor's Assistant: I'll do all I can to help. How long have you been dealing with this?

6hrs

Contractor's Assistant: Do you plan on doing the work yourself?

Yep

Contractor's Assistant: Anything else we should know to help you best?

I can get it to run eventually after 30-40 minutes. Then shuts off with open limit switch code

Submitted: 8 months ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 1 minute by:
11/10/2017
HVAC Technician: airheatman, HVAC Technician replied 8 months ago
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,199
Experience: Furnace, A/C and heat pump specialist.
Verified

To determine if limit is defective or if unit is actually getting to hot, allow unit to shut down on high limit and give us the error code. immediately remove the limit and stick a probe thermometer into the plenum to read actual temperature in chamber.

The limit will have a rating like 175-20 marked on it.(This means it opens at 175 and re closes at 155 degrees.

If limit is opening at a lower temperature than rated for the limit is defective.If chamber is indeed getting hotter than rating, limit is doing its job and you must determine why it is overheating

iI unit is getting too hot below are some things to check and probable causes:

1.Dirty filter

2. Dirty ecaporator coil

3.Blower not running fast enough moving enough air across heat chamber

4.Retricion in ductwork

5.Blocked return air

Ask Your Own HVAC Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask airheatman Your Own Question
airheatman
airheatman
airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 9,199
9,199 Satisfied Customers
Experience: Furnace, A/C and heat pump specialist.

airheatman is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
I was asked to look at a Lennox g40uh-36b-090. The call for
I was asked to look at a Lennox g40uh-36b-090. The call for heat starts the inducer, igniter glows, gas valve opens, fires for almost 15 seconds, blower doesn't come on, gas valve shuts off, blower co… read more
Appliance Guru
Appliance Guru
18,162 satisfied customers
I have a Lennox G40uH-48B-090-05 furnace that is give me
Hi, I have a Lennox G40uH-48B-090-05 furnace that is give me some problems. I'm get a code that say that limit switch is open. Leds read left flash's while the right stays on. It says that it could be… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have problems w/ a Coleman DGAA 70 gas furnace. Runs fine
I have problems w/ a Coleman DGAA 70 gas furnace. Runs fine for about 3~4 cycles then I get a green flashing light. Reset switch and runs fine for another 3~4 cycles. Help… read more
Appliance Guru
Appliance Guru
18,162 satisfied customers
I have a lennox furnace model G40UH-60D and the blower fan
I have a lennox furnace model G40UH-60D and the blower fan runs continuously starting around 5:30 pm till in the morning. Is there a setting that is programmed into the furnace? I have changed the the… read more
Appliance Guru
Appliance Guru
18,162 satisfied customers
Hi, The fan on my Lennox G23Q3/4-100-2 Gas heater is not working
Hi, The fan on my Lennox G23Q3/4-100-2 Gas heater is not working properly. It runs manually (on vs. Auto), but when in Auto, it does not turn on automatically after the burners heat up the unit. So I … read more
Appliance Guru
Appliance Guru
18,162 satisfied customers
I have a Lennox ch33 and woke up to the fan running but no
I have a Lennox ch33 and woke up to the fan running but no heat. Went up in the attic and opened it up. When it gets a signal from the thermostat to run, both flashing lights change to flashing red co… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox G40uh series gas furnace. The furnace will
I have a Lennox G40uh series gas furnace. The furnace will not light. The symptoms are: With heat demand the air inducer turns, the ignitor glows for several seconds and then you hear a relay click an… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
what should the fan limit switch tempature settings be for
what should the fan limit switch tempature settings be for each set switch on a lennox oil furnace.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox G40UH-48C-110-03 furnace. It will only heat
I have a Lennox G40UH-48C-110-03 furnace. It will only heat for a couple of minutes, then it will stop without reaching the set point on the thermostat. The LED error code after the fault is LED1=Slow… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennov G40UH Furnace. The temperature in the house
I have a Lennov G40UH Furnace. The temperature in the house will not exceed 19 deg celcius with the thermostat set to 22 deg or even higher All the cycles run properly except for a point after about 4… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My BRYANT 310AAV/JAV Is not giving out heat fan is continuously
My BRYANT 310AAV/JAV Is not giving out heat fan is continuously running just changed filters code changed from 13 to 33 after i took panel off now what can I do to get the heat back.… read more
airheatman
airheatman
HVAC Technician
6 years college
9,199 satisfied customers
i have a lennox g40uh(x) series furnace led 1 is slowly flashing
i have a lennox g40uh(x) series furnace led 1 is slowly flashing led 2 is on it says in the manual- primary or secondary limit switch open. limit must close within three minutes or unit goes into 1 ho… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a Lennox C33 25A 2F 2 gas furnace. When I turn it on,
I have a Lennox C33 25A 2F 2 gas furnace. When I turn it on, it ignites, the blue flames come on then it shuts off after about 3 seconds. The blower stays on and the lights blink as if it's working pr… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have lennox M/N G23Q 4-100-2 S/N 5896A31221 the heather
I have lennox M/N:G23Q?4-100-2 S/N 5896A31221 the heather start and run fine but it continue run after cool down.and the house it get cool ...… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
5,348 satisfied customers
My combustion air inducer is not starting when I turn the electrical
My combustion air inducer is not starting when I turn the electrical power back on to the unit When I turn on the unit, the g40uh unit comes on but the combustion air unit fan does not turn on. The st… read more
Bill P.
Bill P.
Installer/ Troubleshooter/Technician
338 satisfied customers
I have a Lennox G40UH series furnace. The unit is 2.5 years
I have a Lennox G40UH series furnace. The unit is 2.5 years old. The heating system appears fine though the fan blower does not start. This eventuality will trip the upper limit switch. The fan also d… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a lennox merit c33-36c-2f. On Sunday, woke up and the
I have a lennox merit c33-36c-2f. On Sunday, woke up and the furnace was not running. Shut it off at the breaker, and turned it back on and it ran til this morning--noticed it was off this afternoon w… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
Lennox G40UH(X) series. Installed Honeywell humidifier to
Lennox G40UH(X) series. Installed Honeywell humidifier to 120V HUM-H and HUM-N terminals on board 2 weeks ago. Displaced a wire harness in process. Just found it tonight after furnace will not light. … read more
Bill
Bill
High School or GED
318 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x