Have central air heat pump trane unit. Have central air

Customer Question
have central air heat pump...
have central air heat pump trane unit
JA: Did you double-check the thermostat's settings? And what about the filters?
Customer: have central air trane unit heat pump. in either the heat mode --compressor running or in the emergency heat mode , the heat circuit breaker trips after about 5 minutes. in the cool mode there is no problem . . a technician checked the system this past .summer when i had this problem sporadicallyin the cool mode . he did not find a problem. suggested that that circuit breaker was bad. The circuit breaker was changed . --it did NOT solve the problem . I removed the cover from the thermostat. --found the 3 batteries badly corroded . cleaned the terminals --replaced the batteries . system worked fine in cool mode . now it appears the problem has shifted to the heat mode - Can it be that the Trane touch thermostat is defective and is causing the heat breaker to trip ????..or there is another possible problem ??? ..I.hate to call the tech folks and spent more dollars if not needed
JA: Do you plan on doing the work yourself?
Customer: yes if it is the thermostat ..wondering if therei is a way to sub in a cheap temp thermostat and use it as the test ..
JA: Anything else we should know to help you best?
Customer: no I think i covered all the bases ..The tech guy was very through this past summer .. Since he could not duplicate the problem -and found no other issues -his best thought was the circuit breaker. It was only after I replace the breaker that i thought to look at the thermostat. .. -subsequently finding the corroded batteries......did note at that time ( last summer ) the thermostat lost power ( light went out )when the breaker was tripped
Submitted: 1 month ago.Category: HVAC
Show More
Show Less
Ask Your Own HVAC Question
Answered in 2 minutes by:
11/10/2017
HVAC Technician: gotoman for ac, HVAC Technician replied 1 month ago
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,257
Experience: 51 years of experience install design and repair of all makes and models of AC
Verified

Russ here. No the thermostat will not cause you to trip breaker. Can you tell me if it the breaker going to air handler inside or breaker to outside unit. Russ

Ask Your Own HVAC Question
HVAC Technician: gotoman for ac, HVAC Technician replied 1 month ago

Sounds like it may be breaker to emergency heat tripping breaker. Russ

Ask Your Own HVAC Question
Customer reply replied 1 month ago
outside unit ...perplexing since replacing the batteries on the thermostat fixed the problem this past summer in the cool mode ..never thought to check the heat mode ... the tech said there are times when the heat pump get a signal from the cool and heat via the thermostat, albeit rare, ..this could cause the breaker to trip ???? could it be that the new circuit breaker is defective ...but in the emergency heat mode --the compressor is out of the system --so the amp draw should be different.. i h ave about exhausted my 1980ts knowledge of AC system. Assume you are saying that is is the breaker on the inside air h andler part ...the tech did look at them but did not have the right tool to check the tightness of terminal --and we were up in attic and let it go as a look see ..never thought any more of it ...we are getting past my old sgt pay grade
HVAC Technician: gotoman for ac, HVAC Technician replied 1 month ago

I am old Sgt also. Looks like it is the breaker going to emergency heat. Most likely loose connection or bad breaker. Not the same breaker as the compressor. I would call them back and have them check breaker, Thats is all could be. Russ

Ask Your Own HVAC Question
HVAC Technician: gotoman for ac, HVAC Technician replied 1 month ago

The unit will run till it goes into aux heat and breaker will get hot and trip

Ask Your Own HVAC Question
Customer reply replied 1 month ago
thanks for your service ..i spent 20 plus years wondering around .. not sure of how the breaker trips in both the heat mode --( compressor runs ) and in the emergency heat mode -- compressor not running --- and why it does not trip in the cool mode ??? having said all that --i will go up in attic and check those breakers --thought there were two ... for any defects
HVAC Technician: gotoman for ac, HVAC Technician replied 1 month ago

Air Force Vet here. The compressor and electric heat are two separate breaker. If the heat breaker trips it shuts down the system. If you could pull front of thermostat off sub base and remove the white wire going to W2/Aux tape off and retry system. This will eliminate the aux heat and let us know if it bad or weak breaker. Russ

Ask Your Own HVAC Question
Customer reply replied 1 month ago
AF also mostly aircraft maint --some field training instructor on SAC planes --in hind sight was great ..--had the good and bad times like most ...Will remove the wire wire and see what happens....he white wire is just above W2 --4th connection up ..but it is in line with aux 2 .. after removal --assume I will start the system in the heat mode and see if the breaker still trips ?
HVAC Technician: gotoman for ac, HVAC Technician replied 1 month ago

Yes sir. Remove and tape wire and start heat. Air Force was great. No regrets. Need to start the draft again and give some of these young folks some structure in the military. Worked Civil Engineering mostly except for two years in a mobility squadron. Let me know what happens . Let system run. Russ

Ask Your Own HVAC Question
Customer reply replied 1 month ago
removed and taped white wire --system in heat mode -- compressor ran for about 7 minutes and then the heat circuit breaker tripped ..will reinstall the white wire ...
HVAC Technician: gotoman for ac, HVAC Technician replied 1 month ago

Ok about as far as we can go without test equipment. Need to call tech and check amps on compressor. The compressor pulls same amount of amp in cool as it does in heat so there is another problem. Russ

Ask Your Own HVAC Question
Customer reply replied 1 month ago
thanks for help .....agree that compressor does not appear to be problem ..the tech that was here this summer checked amp draw and said it was fine.... additionally ,,the breaker trips in the Emergency mode --which kind of eliminates the compressor ..... i think I will take another hard look in the attic at the breaker up there .. wish I had a wiring diagram to ponder over. -trouble shooting hard when one does not understand how it all works......A puzzle why it does not trip in the cool mode ??/ which keeps leading me back to the thermostat ...I guess I have just enough knowledge to be dangerous
HVAC Technician: gotoman for ac, HVAC Technician replied 1 month ago

You should have small envelope on unit with service facts wiring diagram. Russ

Ask Your Own HVAC Question
HVAC Technician: gotoman for ac, HVAC Technician replied 1 month ago

If you have no more questions I will open rate box for you. If you need a schematic give me model number of air handler and I will get one for you. Russ

Ask Your Own HVAC Question
Customer reply replied 1 month ago
here is the model number 2TWR4D42A1000AAadded info that might help find cause ?? there are 3 circuit breakers on the circuit breaker panel .. TWO of the breakers are marked heat --ONE breaker is marked AC... Only one heat breaker trips every six or seven minutes -- the tripping is the same -- regardless of whether the thermostat is in normal heat mode or if it is in the emergency heat mode ...
yesterday when I put the thermostat in the cool mode --the circuit breaker did not trip ??/ which added to the puzzle ...The question is what is common to the TWO heat modes -- and what is different when thermostat is in the cool mode.. The FAN ..the circuit breaker--and the thermostat are common in all THREE modes... what else is there .that is common or differentnote again that last summer when I had this circuit breaker tripping in the Cool mode - ( but only once in a while --weekly-- or once a day ) The tech guy said nothing I can see bad in the system -so assume it is breaker.
I changed breaker - problem returned.. Changed badly corroded batteries -- Problem did not recur for rest of summer -- Problem returned only after I set thermostat to the heat mode .. adding to puzzle ...something is drawing too much current.. So what are the possibilities .
HVAC Technician: gotoman for ac, HVAC Technician replied 1 month ago

The one thats tripping is a bad breaker. The fact that it only trips in heat. Russ

Ask Your Own HVAC Question
Ask gotoman for ac Your Own Question
gotoman for ac
gotoman for ac
gotoman for ac, HVAC Technician
Category: HVAC
Satisfied Customers: 5,257
5,257 Satisfied Customers
Experience: 51 years of experience install design and repair of all makes and models of AC

gotoman for ac is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

6,877 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

953 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
Turned off circuit breaker while furnace running ... turned
turned off circuit breaker while furnace running ... turned on circuit breaker ... furnace did not come back on ... got message system malfunction outside sensor error on carrier infinity 96. read you… read more
Daniel Plourde
Daniel Plourde
plumbing, hvac technichian
Vocational, Technical or Trade School
355 satisfied customers
Have central air heat pump trane unit. Have central air
have central air trane unit heat pump. in either the heat mode --compressor running or in the emergency heat mode , the heat circuit breaker trips after about 5 minutes. in the cool mode there is no problem . . a technician checked the system this past .summer when i had this problem sporadicallyin the cool mode . he did not find a problem. suggested that that circuit breaker was bad. The circuit breaker was changed . --it did NOT solve the problem . I removed the cover from the thermostat. --found the 3 batteries badly corroded . cleaned the terminals --replaced the batteries . system worked fine in cool mode . now it appears the problem has shifted to the heat mode - Can it be that the Trane touch thermostat is defective and is causing the heat breaker to trip ????..or there is another possible problem ??? ..I.hate to call the tech folks and spent more dollars if not needed … read more
gotoman for ac
gotoman for ac
HVAC Technician
5,257 satisfied customers
MY STOVE HAS C01 DISPLAYED I TURNED OFF CIRCUIT BREAKER AND
MY STOVE HAS C01 DISPLAYED I TURNED OFF CIRCUIT BREAKER AND IT RESET FOR A TIME THEN DISPLAY CAME BACK UP … read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I have a Heil CA5536VKD2, circuit breaker trips when it
i have a Heil CA5536VKD2, circuit breaker trips when it turns on compressor runs for like a second then trips bad compressor? … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I turned the circuit breaker off to my AC to replace a
I turned the circuit breaker off to my AC to replace a thermostat with a NEST thermostat. When finished, I turned the CB back on. No power. I put the old thermostat back on and still no power at therm… read more
Regan Land
Regan Land
General Manager
Vocational, Technical or Trade Scho
508 satisfied customers
Will a weak capacitor trip the circuit breaker. Today only
well I can tell you I took off a fan motor that had 3 wires and replaced it with one with 4 wires… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,877 satisfied customers
I woke up this morning to a tripped furnace circuit breaker,
I woke up this morning to a tripped furnace circuit breaker, I reset it and went up to the furnace and also noticed a burning smell and a humming noise.… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My HVAC is not working. The AC circuit breaker trips as soon
my HVAC is not working. The AC circuit breaker trips as soon as the, I guess, the outside unit try to start … read more
WCohn
WCohn
Journeyman Plumber
Journeyman License
1,229 satisfied customers
The circuit breaker keeps shutting off when the Rheem
The circuit breaker keeps shutting off when the Rheem furnance/air conditioner tries to come on. What is our problem? We just had a new capacitor put in about two weeks ago. … read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
What size amp circuit breakers needed for lennox heat pump
what size amp circuit breakers needed for lennox heat pump 14hpx-036-230-21 and Lennox air handler cby25uh-036-230-10? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,802 satisfied customers
On my Model 213C A/C, I have: Reset the circuit breaker,
On my Bryant Model 213C A/C, I have: Reset the circuit breaker, Replaced the fuses, Replaced thermostat batteries, Replaced the capacitor, Replaced the circuit board. Our A/C unit is less than five ye… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,877 satisfied customers
The circuit breaker that I plugged my window unit into
The circuit breaker that I plugged my window unit into wasn't labeled so it got too much voltage when I plugged it in and it seems to have blown an internal fuse. I'm trying to figure out which compon… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
6,877 satisfied customers
Circuit breaker cutting off no ac or ac will not run,
circuit breaker cutting off no ac or ac will not run … read more
HvacmanSean
HvacmanSean
Owner
HVAC
219 satisfied customers
I turned off circuit breaker to cleanup a water problem in
Greetings, I turned off circuit breaker to cleanup a water problem in my house. As I went to turn on the heat it would start up but then turned back off. Please can you send me some pictures or a link… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
My thermastat is blank I have reset my circuit breakers
My thermastat is blank I have reset my circuit breakers although they were not tripped , taken it off wall and replaced , still no reading … read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
Lennox furnace model SLP98UH090XV36C-04 > circuit breaker
Lennox furnace model SLP98UH090XV36C-04 > circuit breaker relay (CB8) keeps tripping off when interlock switch (panel cover switch) is engaged… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
I turned off power from circuit breaker and outside
i turned off power from circuit breaker and outside switch,still buzzing where all wires are connected,… read more
D.E. Anderson
D.E. Anderson
Industrial Refrigeration Service Manager
200 satisfied customers
Indoor fan won't shut off unless I use the circuit breaker.
Indoor fan won't shut off unless I use the circuit breaker. I have a Carrier split system gas/electric. The indoor unit is a model 58EJA100 and the outdoor unit is 4 ton model AC1AN048. Starting this … read more
Gaztech
Gaztech
Technician
Vocational, Technical or Trade School
1,142 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x