I have a Vitodens 100 boiler with a recurring F5 fault code…

I have a Vitodens 100...
I have a Vitodens 100 boiler with a recurring F5 fault code when it turns off or goes into rest mode. Internet search revealed it was the air or pressure-switch problem, "the infamous flap," which is a particular problem for this model (manufactured 2007). A technician was called, he opened the unit, the air chamber, lifted the flap, closed the unit and reset. He said if it continued to call him back for a replacement part. Well, I watched everything he did (turning off power, gas, opening the unit - was very easy) and did it again myself successfully, but on the 2nd try (I had read that the rubber seal gets sticky) on trying to clean the seal I broke the flap clean off. My question is - did I need this flap? I had read that it was possibly an extraneous feature that isn't quite necessary for the operation of the unit, and had caused lots of problems - do I really need it and show call the technician again?
Show More
Show Less
Ask Your Own HVAC Question
Answered in 4 hours by:
11/9/2017
Elliott Oxton
Elliott Oxton, HVAC Mechanic
Category: HVAC
Satisfied Customers: 65
Experience: Lead engineer at eoxtongasservice
Verified
Hi my name is ***** ***** I have worked in the plumbing and heating industry for over 18 years. I am confident I can assist you today and looking forward to helping you. Please give me a moment to review your request.
Ask Your Own HVAC Question
Customer reply replied 8 months ago
I have read that more current models of this type have done away with the flap. Can I go flapless, so to speak?
you are right that the new model 100s do not have this flap. But viessmann may have installed another device further down the line to replace this flap. I have not been able to find official documentation to say that this can be removed on this model.
Generally by law you should not alter the boiler as doing so could potentially cause problems and you would be the one to blame. That being said it does not seem to have caused a problem on others who have removed it.The replacement part that your technician is talking about is probably a new flap but with a different type of washer that does not become 'sticky'.So to answer your question simply:1. If you don't want to call the technician back then the boiler should continue to work with out problems. But we can't say for sure it won't cause long term issues such as causing the boiler to burn inefficiently and damage the burner itself.
2. If you are happy to call the technician I would ask him to replace the part. He may tell you off for touching the part but you will know for sure that the boiler is safe and working as the manufacturer designed. This is the option I would recommend as it is the safest option.Please let me know what you think and if you have any further questions.I have left an option for you to rate my response to you. You can do this by clicking on the star rating above. It is totally free to rate me so I am grateful for you taking a moment to do so. We can continue to talk after you have rated me so I am ready to answer any follow up questions.Thank you in advance for your feedback.Warm regards
Elliot
Ask Your Own HVAC Question
Customer reply replied 8 months ago
I called the technician, waiting for a call back. I guess it is safer to switch the part, although more expensive of course. You reckon I could just put it back together and turn it on until the technician comes? It's cold here and we have wee ones, so heat would be nice (the unit has been shut off since noon)
I apologize but I only just got your message on my device although I see you wrote earlier.The safest option is to wait but I understand with youngsters this is not always an option.
If your technician cannot come out immediately then you could put it back together and see how it works. Make sure the case is completely shut to ensure no dangerous gases escape from the unit.If you have any other thoughts then please let me know.
Warm regards
Elliott
Ask Your Own HVAC Question
Good day,
I see that you have left me a negative rating. I really hope that I can do something to change your rating to above a 3 star.
I'm sorry if the news that I have you was not positive in that you have had to get the technician out again. But I felt that it is the safest thing for you to do considering that you have young children. I'm very sorry that it had worked out that way.
Please can you tell me what I can do to change your rating into a 3star + rating? I definitely don't want to leave you without feeling you have received a good service from us.
Looking forward to hearing from you and doing anything else I can to help you further.
Warm regards
Elliott
Ask Your Own HVAC Question
Customer reply replied 8 months ago
Hi Elliott - regarding option 1 that you gave me - the technician said that if I had put the unit back together, it could have caused an explosion as the flap regulates the fuel / air mixture, and if I had run the unit without the flap it could have been a disaster of epic proportions. While you did say I should call the technician, the inclusion of not calling the technician could have opened the door to calamity. Hence the two star.
Good day,
Thank you for your response. I appreciate you explaining the reasons for your rating.I believe your technician maybe trying to scare you a little by saying those things. In many lands in is illegal to even touch the inside of a boiler if you do not have a license. However the boiler would not have blown up had this part been removed. The manufacture has actually removed that part from the new models and increased the run time of the fan.However the technician did see the condition of your boiler and the damage that has been caused so he may have had another reason to tell you those things.I appreciate you explaining those things to me. It's really better to err on the side of caution which is what I will do with other requests like this.At this time I will not get any compensation for the help I have tried to give you with a 2 star rating. All your deposit will only go to the website. If there is anything I can do to change that please let me know. If not I will try and have this closed for you today.Warm regards
Elliott
Elliott Oxton
Elliott Oxton, HVAC Mechanic
Category: HVAC
Satisfied Customers: 65
Experience: Lead engineer at eoxtongasservice
Verified
Elliott Oxton and 87 other HVAC Specialists are ready to help you
Ask your own question now
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with a hvac technicianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Elliott Oxton Your Own Question
Elliott Oxton
Elliott Oxton
Elliott Oxton, HVAC Mechanic
Category: HVAC
Satisfied Customers: 65
65 Satisfied Customers
Experience: Lead engineer at eoxtongasservice

Elliott Oxton is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Phil

Phil

Mechanical Engineer

7,426 satisfied customers

Retired HVAC/ Electrical & Boiler contractor. Industrial

Rick Mather

Rick Mather

HVAC Technician

3,133 satisfied customers

35 years experience, HVAC

Matthew

Matthew

HVAC Technician

2,014 satisfied customers

14 years experience in the HVAC field of service, installation, Manual J & D calculations

Brian HVAC Guy

Brian HVAC Guy

HVAC Technician

1,019 satisfied customers

I have been an HVAC/R mechanic/technician for 30+ years.

Kenton Guidry

Kenton Guidry

HVAC Technician

963 satisfied customers

12 years install/service experience.

Rick Ridley

Rick Ridley

UK Heating Engineer

871 satisfied customers

Retired But have had 30 years on the tools, Ex CORGI

Tom

Tom

HVAC Technician

770 satisfied customers

16+yrs HVAC/R service. Residential Commerical Industrial

< Previous | Next >

Related HVAC Questions
We have two Vitdedens 200's that were installed in our
We have two Vitdedens 200's that were installed in our Vermont home in 2005 by John Hull, Locust Creek, Bethel, VT. They have operated well for years but have been faulting continuously for 3 months and Hull refuses to service our home (we suspect it is due to his homophobia). So we are constantly without heat or service. … read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
I have a Heil 90% gas furnace that constantly short cycles.
I have a Heil 90% gas furnace that constantly short cycles. I have been told that my 2nd heat exchanger "may" be stopped up and that I am in need of a new furnace. He recently replaced the control boa… read more
hvacguy17
hvacguy17
Mentor Service Technician
Associate Degree
12 satisfied customers
Hi. I have a 2007 Rheem 13 SEER R 22 Heat pump / AC unit.
Hi. I have a 2007 Rheem 13 SEER R 22 Heat pump / AC unit. Last year (2001) it wasn't keeping up with cooling when we turned on in the spring. We called a contractor who came out and re-charged the sys… read more
Airheatman
Airheatman
Heating & Air Conditioning Contractor
6 years college
1,836 satisfied customers
i have a XL 1200 and it is running fine , but the air is not
i have a XL 1200 and it is running fine , but the air is not cold. i had a Trane technician do a check and cleaning last week and it was cooling ok. He said we needed to replace the unit and offered t… read more
Wvfan79
Wvfan79
Mecanical Designer & Estimator
High School or GED
775 satisfied customers
I have a first generation vitodens 100-W boiler that goes into
I have a first generation vitodens 100-W boiler that goes into "reset" once in a while and now quite frequently. the fault code is F9. I will have the boiler serviced anyway but is there anything I ca… read more
HVAC Guru
HVAC Guru
Service Technician
Associate Degree
682 satisfied customers
My gas-fired HVAC unit is only firing intermittently. Sometimes
My gas-fired HVAC unit is only firing intermittently. Sometimes it does not kick on for extended periods of time, despite the thermostat settings being set properly to heat/auto. The igniter glows, an… read more
Matthew
Matthew
HVAC Technician
Bachelor's Degree
2,014 satisfied customers
We have just tried to start our gas boiler [Viessmann Vitodens
We have just tried to start our gas boiler [Viessmann Vitodens 100] as we have been away for several weeks but it won't light. The fan starts but the gas doesn't ignite and after 30 seconds or so it s… read more
Jerry M.
Jerry M.
Senior HVAC Technician
High School or GED
133 satisfied customers
I replace a 4 year old Airease with a Ducane 3 ton 13 seer
I replace a 4 year old Airease with a Ducane 3 ton 13 seer R-22 13HPD. When it was charged and turned on the technician said a 'vaccumm' developed in the lines either on the high or low side that caus… read more
Richard
Richard
District Technical Manager
Vocational, Technical or Trade Scho
1,416 satisfied customers
My new Trane system (Model #TAYWARS082) was just installed
My new Trane system (Model #TAYWARS082) was just installed on May 12, 2011. About a week ago we noticed that the system was shutting down periodically for long periods of time and the temprature upsta… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
The outside unit will power up for a couple of minutes then
The outside unit will power up for a couple of minutes then shut off and a get a red light on the thermostat. I have clean the coils with the recommended foam hydorchoric cleaner but it has not helped… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I have a Lennox G61MP series furnace that is on its second
I have a Lennox G61MP series furnace that is on its second winter. It seems to work fine for several cycles and then fails to respond to a call for heat. Turning the power on and off resets it and it … read more
KenCan
KenCan
Vocational, Technical or Trade Scho
111 satisfied customers
Good afternoon, Ive worked on furnaces and hot water heaters
Good afternoon, I've worked on furnaces and hot water heaters in the past. My son has a gas hot water heater with a White Rodgers gas valve. The pilot was going out and he would relight it. I replaced… read more
Rick the plumber
Rick the plumber
Owner
9,857 satisfied customers
have a ducane ac model Ac12b24 thats not blowing cold air.
have a ducane ac model Ac12b24 thats not blowing cold air. The compressor and is ok its been pressure checked and charged up but still not cold. Condensor coils have been cleaned. don't know where eva… read more
Tim H
Tim H
Lead building engineer
Vocational, Technical or Trade Scho
1,922 satisfied customers
Hello. I have a 6-year-old Trane. Just had my 2nd service call
Hello. I have a 6-year-old Trane. Just had my 2nd service call on it yesterday,in as many days. The tech came out 2 days ago & found that it was low on freon. Everything else was fine. He put the freo… read more
gotoman for ac
gotoman for ac
HVAC Service manager and owner
Associate Degree
4,135 satisfied customers
I have had a vitodens 100 in my new home for a year it has
I have had a vitodens 100 in my new home for a year it has given me constant problems, it gives an F5 error code usually at about 5 oclock on a friday, I had a tech replace the sticky flapper but it s… read more
Phil
Phil
Mechanical Engineer
Degree, Mech Engr Technology
7,426 satisfied customers
I am looking for a service bulletin for Arco Aire gas Furnace.
I am looking for a service bulletin for Arco Aire gas Furnace. I have sludge in my condensation chamber and drain tube, causing a pressure switch to act open, when it should be closed. (Diagnostic cod… read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I have a 4 ton Carrier centralized split system a/c unit .
I have a 4 ton Carrier centralized split system a/c unit . The out side fan seems to be running fine, but it is not blowing cool air. I called a technician and he said to replace the unit. He seem to … read more
Billy
Billy
Journeyman Service Technician
State Licensed Mechanical Contractor
9,330 satisfied customers
I turned on my central air last night, it started blowing cold
I turned on my central air last night, it started blowing cold air and within a few minutes it was blowing hot air. I did use the air back in April and it worked just fine. What could cause this...cou… read more
Mark Henley
Mark Henley
HVAC Controls DDC
3,209 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x